    Thank you for posting this informative public service video. The heavy-duty industrial grade NEMA 14-50 receptacles (Hubbell, Bryant) are constructed of fire-resistant Bakelite rather than injection-molded plastic, and their 4 contact springs are heavy-duty with heavy plating, specifically designed for thousands of insertion/removal cycles rather than a few dozen. They also feature specially plated clamp-style wiring connections with set screws which must be carefully tightened using a calibrated torque wrench. A side-by-side comparison is compelling, and there are a rapidly-growing number of photos of melted/scorched/burned NEMA 14-50 outlets posted on the Internet. Sadly, many of these dangerous receptacles were installed by licensed electricians.
    Less-expensive, lower-quality NEMA 14-50 receptacles are unsafe for EV charging and should all come with a warning that they are not designed for and must not be used for EV charging applications. Given the risk, home improvement stores (Home Depot, Lowes, ACE Hardware, etc) should completely stop selling them, and online stores should be required to have detailed warnings. The national wiring codes should also be updated appropriately. No one should die or lose their home over this issue.

    • @dancolestock
      @dancolestock 2 ปีที่แล้ว +9

      That said, whenever possible an EVSE should be permanently installed with suitable heavy gauge wiring rather than using NEMA 14-50. The Laws of Physics dictate that I*I*R heating occurs in wires and connections whenever there is electrical current, and today's home EVSEs draw up to 48A@240Vac (11.52kW). THAT'S A LOT OF POWER. When you draw that amount of 240Vac current steadily over several hours, the wires and connections GET HOT. Direct wiring eliminates one set of temporary connections that are likely to degrade over time and overheat with repeated usage.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      Thanks for this important information!

    • @dancolestock
      @dancolestock ปีที่แล้ว +1

      The price of the Industrial Grade Hubbell and Bryant NEMA 14-50 receptacles has dropped significantly (8/2023) - about $75 - now that supply is catching up to demand. Meanwhile, lots more online reports and images of $15 NEMA 14-50 receptacles failing and melting/catching fire.
      Please hire a licensed, experienced electrician and consider a safer hard-wired EVSE installation, especially now that NACS is being adopted for EV charging in 120/240Vac North America, the Tesla (Gen 3) Wall Connector is a good value with a large installed base and excellent safety and reliability record.

  • @mattandlanacarter4137
    @mattandlanacarter4137 ปีที่แล้ว +28

    I’m an electrical contractor and one thing you can do is increase the wire size to 4 as a heat sink … the thicker the wire the less chance you have of a 50 cheap Leviton 14-50 of over heating . . Don’t ever use less than 6 though . Good video to re think that extra prong we never use !

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      Thanks for the info

    • @gheumann
      @gheumann 11 หลายเดือนก่อน +7

      If you're an electrical contractor then you know that the amps rating for a circuit is NOT FOR CONTINUOUS DUTY - it is for max 85% - at least here in California that's the case. Upsizing the wire isn't good enough - you must have at least 60A circuit to pull 50A continuous through it.

    • @brianarant5932
      @brianarant5932 7 หลายเดือนก่อน +4

      @@gheumann Should be 48 amp continuous for a 60A breaker. It is 80% of breaker rating.

    • @weaesq
      @weaesq 6 หลายเดือนก่อน +1

      4 gauge wire is rather difficult to route. Not sure having three cables (assuming 2 phase or split phase) of that size will fit in a 1 inch conduit. But it is an interesting idea.

  • @MTNRanger
    @MTNRanger 2 ปีที่แล้ว +21

    Yes, prices are triple of when I did my NEMA 14-50 installation video back in 2020. I still recommend installing the 14-50 since most EVSE use that plug. The Eaton 5754N is also a good option. The Bryant 9450FR is a good deal - thanks for the suggestion.

  • @joelm077
    @joelm077 2 ปีที่แล้ว +3

    Watched old video and you convinced me to upgrade from the cheap Menards 14-50 to Hubbell. Went to shop for another Hubbell for my brother in laws house and saw the price....then saw Bryant and did a search...found this vid...buying Bryant 14-50. Thanks for the info! (already have the 14-50 mobile plug)

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Haha good story. Glad I came on this journey with you.

  • @simonpaine2347
    @simonpaine2347 ปีที่แล้ว +6

    Thanks for providing the alternatives! It obviously helped to shake up the marketplace. As of August 2023 Amazon has Bryant at $49 and Hubble is down to $88!

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Thanks for the info!

    • @dancolestock
      @dancolestock 9 หลายเดือนก่อน

      It appears that the Hubbell/Bryant manufacturer(s) switched over from 1930's Bakelite to modern injection-molded glass-filled thermoplastic to satisfy the increase in demand brought on by EV adoption. There continues to be significant quality, ruggedness and safety differences between the consumer-grade and more expensive industrial-grade receptacles. Consumer-grade receptacles are designed for relatively infrequent use and intermittent loading.

    • @YourBestFriendforToday
      @YourBestFriendforToday 7 หลายเดือนก่อน +2

      Got a bryant as well.

    • @hank8632
      @hank8632 5 หลายเดือนก่อน

      I got Hubble for 50 on Amazon 🤷🏾‍♂️

  • @patrickbauer5358
    @patrickbauer5358 2 ปีที่แล้ว +4

    Good timing. Telsa just stated that they are no longer supplying UMC with car and they are out of stock on line. I put in Hubbell 14-50 in anticipation of home charging w included UMC. Wish I'd have hard wired instead. Cost of outlet+GFCI breaker+UMC that I have to order now is a push compared to hard wiring charger (I know its not a charger but...)

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      The UMC will come back in stock. Id think they would still include it for orders prior to the announcement.

  • @danmitchell1143
    @danmitchell1143 2 ปีที่แล้ว +4

    For me, the NEMA 6-50 is the way to go. I use the outlet to charge my MY and on occasion my wife uses the outlet to her electric kiln. Thanks for the great videos.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Thanks :)

    • @benjurqunov
      @benjurqunov ปีที่แล้ว

      The 6-50 also allows you three conductors rather than four.
      That alone can save substantial money right there.

  • @carolan066
    @carolan066 2 ปีที่แล้ว +8

    Great video - thanks. I actually wound up just recently buying the Hubbell. Your first video was the reason I bought it :). I wound up purchasing it from a local Electric store here in NJ and I only paid $38. I had to wait about a month for it to get into stock though. One extra cost to consider is that the faceplate for the Hubbell is non-standard. I wound up paying almost $20 just for the faceplate.
    Another point on the GFCI - My Juicebox 40 specifically says not to use it with a GFCI outlet. The Juicebox has GFCI built in. I believe other manufactures have the same recommendation. Also, good to know that the Bryant is similar to the Hubbell. I did not realize this.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      All EVSEs should have built-in GFCI protection because you need to be able to charge outside. And I’ve heard that it’s never good to have multiple GFCIs in line. But the NEC doesn’t list any exclusion for EV charging. So I’m not sure what’s the “best” thing to do.
      Electricians commented on my original 14-50 installation video that the breaker should have been GFCI per code. So I upgraded it in this video th-cam.com/video/BixGQisysDc/w-d-xo.html

    • @wiedapp
      @wiedapp 2 ปีที่แล้ว +1

      @@handydadtv Two GFCI in line won't harm themselves or the person using the outlet. You just can roll the dice which one shuts off when something happens, if the tripping value is identical on both.
      Greetings from a German electrician (just randomly got your video recommended to me, probably because I looked up the type of plug well over a year ago...)

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +3

      @wiedapp Hello Germany! Since EVSEs supposedly have internal GFCIs without a test button, they must do a self test before every charge. Is it possible that’s when a GFCI breaker can pop? People have quoted ChargePoint’s instructions that it should not be installed on a GFCI protected outlet.

    • @wiedapp
      @wiedapp 2 ปีที่แล้ว

      @@handydadtv Well, that would need to be tested, I think.
      On the other hand: We have mobile GFCI here for some applications (worker protection mandates them sometimes, if it is not determinable if the used outlet is behind a GFCI already) and you can use them in line with a regular one. These have a test button and if you look at the schematics of how that test button is wired inside a (any!) GFCI, the test doesn't affect another one.
      As long as the test mode in the chargers doesn't bridge live to ground, you should be good to go. Usually the bridging via the test button happens between one output contact (for ex. live 1) and one input contact (for ex. neutral) of the GFCI, so the device 'sees' some current missing and then it shuts off.
      Furthermore: If your local code requires that a certain type of outlet has to be behind a GFCI, what do you do:
      a) follow code or
      b) follow manufacturers instructions and not follow code?
      If we here want to operate something without a GFCI, we have to hardwire it by code.
      I mean, we don't have building inspections like is common for you over there (please correct me, if I'm wrong), so if something is not to code no one will see it. But if something happens because of that, your insurance gets a major homerun and you get nothing...
      And, as I said: The only thing that can happen is, that you have to look on both devices, if there is a situation, because you can't be sure witch one trips first. More annoying than dangerous.

    • @xpxdavex
      @xpxdavex 2 ปีที่แล้ว

      I am in NJ as well. What was the electric store? That's a great deal!

  • @NipomoBeach
    @NipomoBeach 2 ปีที่แล้ว +2

    I installed a Wall Connector when I purchased my EV. We installed a 60 amp circuit. Got a little more juice. But had to hard wire it. It was an expensive project but I only have to do it once.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Good choice 👍🏻

  • @jeffdegross
    @jeffdegross 2 ปีที่แล้ว +6

    Thanks again for a great video. I went with NEMA 6-50 based on your second video, still got a Hubbell and it works great. Dont understand why more people just don't go with 6-50 for their level 2 charging install. Ok, 14-50 gives more flexibility in the use of the outlet, sure, but my charging outlet is pretty much dedicated to charging my Tesla, so save money and go with 6-50. Even the 6/2 wire is a bit cheaper than 6/3 which, as you pointed out, isn't even used by the car for charging

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +4

      I have learned a lot since buying my Tesla by making these videos. I’m glad they’ve been helpful for you. 😊

    • @colinpovey2904
      @colinpovey2904 2 ปีที่แล้ว +5

      Most commercial places today are installing the 14-50, instead of the 6-50, so in the long run, it will be usable in more places.

    • @jeffdegross
      @jeffdegross 2 ปีที่แล้ว

      @@colinpovey2904 You are correct, so what i did is I bought a NEMA 6-50 to NEMA 14-50 adapter from Amazon for $20. Now I can plug in just about anywhere

    • @krelllab6366
      @krelllab6366 2 ปีที่แล้ว

      My defense of the Hubble connector was deleted. Interesting.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      @KrellLab - Apologies. TH-cam filters certain comments (like hate or links).

  • @gheumann
    @gheumann ปีที่แล้ว +24

    If you're going to hard wire, then put in a 60A breaker!!! Then you can charge at 11Kw instead of 9KW. Code says you can only draw 80% of the circuit's rating for continuous duty. So with a 50A breaker you have to set your charger down to 40A draw, which is 9KW. But a 60A breaker is enough to let you draw 48A< a full 11.KW> (Not alll level 2 chargers can draw/charge that much but SOME do - and they MUST be hardwired if over 50A.

    • @handydadtv
      @handydadtv  ปีที่แล้ว +5

      Correct.

    • @monty7336
      @monty7336 ปีที่แล้ว

      Thanks for this!

    • @claytonjames4779
      @claytonjames4779 ปีที่แล้ว +1

      Don't try to do that with a Tesla mobile charger

    • @ronlaverdiere
      @ronlaverdiere ปีที่แล้ว

      Why? Most EVSE units max out at 40 amps. Most cars max out at 9.6 kWh as well for AC charging. 99.999% of home owners will never even benefit from a 40 amp EVSE.

    • @richmoreno6479
      @richmoreno6479 ปีที่แล้ว

      There is no car that charges at 50A. The code asks only for 40A for car chargers. 50A is already a really good over head. Tesla home chargers, or most chargers will max out at 48A, but never really get there. 9kw/ hr is typical. Not the rated 11.5kw

  • @bobblum5973
    @bobblum5973 2 ปีที่แล้ว +1

    Decent video, short but to the point. My only comment is a general one; always check what is proper electrical code for your location, you don't want to do it wrong and need to rework it later.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Good advice 👍🏻

  • @GerardPinzone
    @GerardPinzone 2 ปีที่แล้ว +8

    One more tip: Spray Deoxit into the outlet (whichever one you buy) if you need to plug/unplug frequently. Deoxit DN5 can be used on live circuits since the can contains nothing that can ignite if there's a spark.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      Thanks for the tip!

    • @carolan066
      @carolan066 2 ปีที่แล้ว +2

      Deoxit is great and I use it all the time. Every 6 months I’ll clean my contacts with 0000 steel wool followed by deoxit to keep the terminal in good shape

  • @paulg8065
    @paulg8065 ปีที่แล้ว +4

    Thanks. I’ve been hearing horror stories from people who charge their cars on $10 Home Depot receptacles and have them melt. I was about to buy the Hubbell but went with the Bryant instead to replace my two $10 receptacles.

    • @handydadtv
      @handydadtv  ปีที่แล้ว +3

      I also recommend charging as slowly as possible on a daily basis. Just because your charger can do 40 amps doesn’t mean you need to always charge at that rate. My daily rate is only 15 amps which takes around 7 hours. That keeps everything cooler.

    • @jawharris
      @jawharris ปีที่แล้ว

      @@handydadtv I bought a 2021 Nissan Leaf, can I change the rate on that? I read the Leaf is a 30 am charger.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      @jawharris Google that. I don’t know the Leaf.

  • @CubbyTech
    @CubbyTech 2 ปีที่แล้ว +4

    A GFCI breaker is not required if you have an outlet for your EVSE. That segment is a bit confusing because some EVSE's say you should not use a GFCI breaker.
    Amazon isn't a good 'price guide' lately, I'm usually comparing between a brick and mortar's website and Google to get an idea of what something *should* cost.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      I read the code and there is no exception for EV charging:
      th-cam.com/video/BixGQisysDc/w-d-xo.html

    • @brianleeper5737
      @brianleeper5737 2 ปีที่แล้ว +2

      @@handydadtv It depends on what version of the NEC your state or locality is using. The requirement that 240V outlets be on a GFCI is a fairly recent one, and your state or locality may not have adopted that NEC yet. Some states are still using the 2008 NEC and some are still using the 2014 NEC.

    • @jeffwilliams8179
      @jeffwilliams8179 2 ปีที่แล้ว

      @@brianleeper5737 Agreed. Most chargers have built in GFCI and recommend not being on a GFCI circuit. Hopefully NEC will address this issue and rewrite the code.

    • @Wowzersdude-k5c
      @Wowzersdude-k5c 2 ปีที่แล้ว +1

      ​@@jeffwilliams8179 I doubt NEC will revise it because a 240V outlet can be used for things other than an EV car charger. So the NEC wants that outlet GFCI protected when little Johnny comes along and decides to plug something else into it. The best way to avoid this hassle is to simply hardwire the charger so there is no outlet at all. Let the EV charger's built in GFCI provide the shock protection.

  • @rebootninja8036
    @rebootninja8036 ปีที่แล้ว +1

    I bought a Bryant 6-50R from Amazon and it works…. buuuut the ground terminal screw (flat head) stripped when I torqued it to spec of 30 lb-in.
    It’s been too long to return it so I’ll see about a warranty claim, but I’m planning to replace it with a Hubbell 6-50R that has the metal clamps and not just a set screw.
    The interior plastic housing is also white on my Bryant outlet, maybe the 14-50R is generally the same but for some reason the 6-50R has different design between Bryant and Hubbell.
    Honestly at this point I should really just hardwire the EVSE, but I use it at my in-laws house a couple times per month and it’s pretty handy when I do.

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      That sucks

    • @rebootninja8036
      @rebootninja8036 ปีที่แล้ว +1

      @@handydadtv
      Lol, yup.
      I was using the outlet in a box for the past couple months, but the box was just loose on the floor near my panel so I decided to finally get everything properly mounted and secured to the wall.
      On the bright side, I’ve got conduit shaped & mounted, the box is on the wall, wire is pulled to the panel and pretty much all the hard parts are done.
      I’ve still got the slow charger (L1 EVSE) and my BMW i3 has a gas range extender, so I won’t be totally out of luck even if I’m lazy and don’t get the L2 hooked up again right away.
      BTW I’ve really enjoyed your videos on this, it’s been helpful to get a DIY perspective that includes best practices as you learn more details.
      I’ve watched a bunch of professional electricians videos on this stuff as well - I feel like your videos complement those well and fit right in with expert guidance in a very approachable way.
      So thanks for making these.

  • @DanielinLaTuna
    @DanielinLaTuna ปีที่แล้ว

    Thanks for sharing! I had wondered why the 240-volt outlet had a slot for a neutral wire! You answered my question by saying “it isn’t used.”

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      It’s not used by the EVSE.

  • @cyborgsheep6077
    @cyborgsheep6077 2 ปีที่แล้ว +5

    Keep it in mind though that electrical codes may require you to install a disconnect switch if the charger is hard wired since it is an electronic device that is prone to failure

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +3

      Why is that any different than my hard-wired wall oven? The breaker is the disconnect.
      It could be a requirement outdoors though.

    • @MelvinTheGrate
      @MelvinTheGrate 2 ปีที่แล้ว +1

      @@handydadtv I can't comment about whether a disconnect is required, but if a disconnect is required, the code requires tha it be clearly visible from the equpment and the distance must not exceed 15m (50 ft). Your breaker in the panel almost certainly does not qualify.

    • @JetSettingBotanist
      @JetSettingBotanist 2 ปีที่แล้ว +1

      Don't quote me on this but I believe that's only for loads over 60amps.

  • @ericgold3840
    @ericgold3840 ปีที่แล้ว

    I''m also in the hardwired camp unless there is a good reason to choose 14-50. Another cost savings that come with hardwiring is from skipping the extra conductor for the grounded (AKA 'neutral') conductor. All the EVSE I am familiar with only use two hots and the grounding conductor. If e,g, Romex is used, 6/2 can be purchased instead of the 6/3 that a 14-50 receptacle would require.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Good point. The NEMA 6-50 is a good option without the neutral, but it’s not as common for EVSEs.

  • @douglasbernick5908
    @douglasbernick5908 ปีที่แล้ว

    Watching your video and cracking mistakes you might’ve missed one on the plug outlet where you were showing copper wires were the insulated wire wasn’t covered completely. There was copper exposed, which could cause arcing and eventually a fire all right awesome video keep it up.

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      Thanks for the advice!

  • @frankcoffey
    @frankcoffey ปีที่แล้ว

    I had the Hubbe installed and it was worth it but I paid less than $100 for it. The plug cycles is not really an issue because I use an RV quality extension cord so I don’t have to back in and I only unplug the mobile adapter when I’m going on a trip. We also have the Tesla wall connector for my wife’s car but if I use that the cable is behind her car and see can’t back out without unplugging it. It just works better with each car having it’s own unit.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Thanks for the info

  • @johnreese3762
    @johnreese3762 ปีที่แล้ว

    I just bought a Bryant from Grainger for my new Tesla!! Thanks for the great video!!

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Glad it was helpful 👍🏻

  • @TonyPham-Creations
    @TonyPham-Creations 11 หลายเดือนก่อน

    Thanks for the informative videos! I’m still convinced that hardwired is the best option, in the end. Went from 14-50 but needed the extra ~50% faster charging speeds, so hardwired Gen3 Wall Connector is the way to go

    • @handydadtv
      @handydadtv  11 หลายเดือนก่อน

      Definitely 👍🏻

  • @cube1us
    @cube1us 2 ปีที่แล้ว +6

    Note that in quite a few areas of the country you do not need the GFCI breaker for a Nema 1450 outlet. And since the charger itself has protection if the only thing you’re ever going to plug into that outlet is a charger you are just as safe as you would be as if you installed the GFCI breaker. But it does vary by state depending on which version of the national electrical code they are currently using.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Thanks

    • @dontbanmebrodontbanme5403
      @dontbanmebrodontbanme5403 2 ปีที่แล้ว +2

      Just to add to what you've said, many have reported their charging being interrupted on GFCI breakers. My state doesn't require a GFCI breaker and, as you said, since I'll only be plugging in a charging station anyway, which has the protection, I'm fine. Now, there is indeed a VERY GOOD POINT in simply not using an outlet period. The downside is you can never unplug your device if you want to take it with you, etc.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +3

      In 2.5 years, I’ve taken my UMC on a handful of trips and never touched it. I try to choose hotels with destination chargers or I just Supercharge when needed.
      One time, at a rural AirBNB, I could have used the UMC but left it home. 🤷🏻‍♂️

    • @jolyonwelsh9834
      @jolyonwelsh9834 ปีที่แล้ว

      The 2017 NEC doesn't require GFCI protection for EV chargers. The 2020 NEC does regardless as to whether it is hard wired or not.

  • @Dactylonian
    @Dactylonian ปีที่แล้ว

    Thank you!! This video answered every question I had about what is 6-50 vs 14-50, and why would someone hardwire vs use the 14-50 plug that comes with the EVs I’m looking at.

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      Hardwire is safest.

  • @colinpovey2904
    @colinpovey2904 2 ปีที่แล้ว +2

    Thanks for the video. I too found the Bryant outlet at Grainger.
    Be sure to order the matching face plate as well, as there are similar but slightly different face plates that are incompatible.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Thanks for the advice!

    • @andrewt9204
      @andrewt9204 2 ปีที่แล้ว

      Grainger has sold to individuals for as long as I've been going there. Which has been like 9 years now. Can't say to anything before that of course.

    • @colinpovey2904
      @colinpovey2904 2 ปีที่แล้ว

      @@andrewt9204 Thanks for the update. I'll fix my answer.

  • @FixitFred
    @FixitFred 2 ปีที่แล้ว +1

    One benefit of installed an outlet especially a Nema 6-50 is that welders use that plug. So you can unplug your ev charger and plug in your welding thus serving dual purpose.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Good point

    • @timgraham7851
      @timgraham7851 2 ปีที่แล้ว

      Welder adapters can be found for a reasonable price.

  • @jabroni6199
    @jabroni6199 ปีที่แล้ว

    I have that same emporia charger using the 14-50 plug and had a UEFI breaker. It kept tripping for no apparent reason. Emporia support said their chargers already have UEFI protection built in and I needed to replace my breaker with a standard one. Once I did that no issues. Same deal with the FORD optional EV chargers. It specially says not to use UEFI breakers. The ford mobile charger that comes with their EVs call for a UEFI breaker.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Huh. I never had any issues with the GFCI breaker tripping.

  • @someoneelse6934
    @someoneelse6934 8 หลายเดือนก่อน

    I just got a Hubbell 14-50 for $59 on Amazon. I am happy with that price.

    • @handydadtv
      @handydadtv  8 หลายเดือนก่อน

      That’s a great price.

  • @JeanPierreWhite
    @JeanPierreWhite ปีที่แล้ว

    It's worth checking codes in your area. A GFCI is not required everywhere. It is true the latest electrical code does call for it. There will be a time when we must use GFCI breakers. Some portable units do a ground fault check and will trip GFCI breakers, AFCI maybe better in that case. Plug in EVSE's are probably going to be a thing of the past once everyone adopts the new codes.

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      I recommend hard wiring to avoid the issue.

  • @Condor1970
    @Condor1970 ปีที่แล้ว

    Unless you're frequently running high current welding equipment and car chargers, then regular $10 4-prong outlets from Home Depot for your average residential shop is more than adequate. They can easily accommodate 240v air compressors, table saws, and auto lifts, etc. If you need a car charger, it's actually best to just hard wire the thing.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      I agree. Hard wired is best.

  • @jasonanderson951
    @jasonanderson951 2 ปีที่แล้ว

    Wow! Awesome! Thank you for another great cost savings informative video Chris. Are you planning on posting any lawn care videos? I’m itching for them!

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      LOL you know I live in a managed community now. People look at me funny when I do any lawn work here. 😂

    • @jasonanderson951
      @jasonanderson951 2 ปีที่แล้ว

      @@handydadtv LOL yeah I understand. I’m sure you could still do some good ones just one a smaller scale. You could also do them at your daughter’s house.

  • @MrJeffoff
    @MrJeffoff 9 หลายเดือนก่อน

    For those with a Long Range Tesla, some can charge up to 48 amps when matched with a charger rated that high. For example a Tesla wall charger, or a Jukebox 48 amp charger. So consider THHN #6 gauge wire matched with a 60 amp breaker, and hard wire it.

    • @handydadtv
      @handydadtv  9 หลายเดือนก่อน

      Totally agree 👍🏻

  • @SwimFlySwim
    @SwimFlySwim 4 หลายเดือนก่อน

    We have to upgrade. The Prius Prime charges fine (and slow) on 120v, but two of them on one line was...dangerous. We're planning to upgrade, but don't need 50A for the Primes (and don't plan to replace them anytime soon). What about running 220v to 20A circuit and going with a 6-20 plug and one of the Level 2 chargers that work with that? Smaller breaker. Smaller plug. The Prius Prime max charge rate is 8A, so 2 Primes on one circuit still brings us to only 16A on a 20A circuit running two plugs. Or would you just go hardwire instead?

    • @handydadtv
      @handydadtv  4 หลายเดือนก่อน

      If hardwiring is an option, that’s always what I’d choose. Also, the Prime won’t be your last EV. If you’re running a new circuit, use 6AWG minimum and do it once.

  • @smashoklw
    @smashoklw 2 ปีที่แล้ว

    EV owner since 2014 and I firmly agree with you. Most people will never have a need to unplug their EVSE so why pay extra for the socket you'll never need.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Thanks. What car and charger do you have?

    • @smashoklw
      @smashoklw 2 ปีที่แล้ว +1

      @@handydadtv I have a 32 amp Bosch Powermax. In 2014, when we purchased our SparkEV, Chevy was offering a $500 rebate on the purchase of one so I got it for something like 50 bucks. Bosch actually OEM'd the unit from Delta but it hasn't skipped a beat in all these years and takes care of the 2020 Bolt with ease.

  • @ronmaynard7424
    @ronmaynard7424 ปีที่แล้ว

    You can get Hubbell for 80 bucks still, but hard wire is way to go, safer, more power and less conductors and no plugs, thhn wire and emt conduit are about the same price as buying the Hubbell and 4 wire. Great video

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      I agree. Thanks 😊

  • @herbertsax7169
    @herbertsax7169 2 ปีที่แล้ว

    Your suggestion is the right one. A hard wired charger is always my favored approach.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Thanks

    • @ronb6182
      @ronb6182 2 ปีที่แล้ว +1

      If you don't need an outlet why bother. Hard wire is the best connection possible. Plugs corrode and wear out. Even if the plug stays plugged in most of the time. If you use the outlet for other uses move the outlet and still hard wire the charger. It's the best alternative. 73

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Agree ☝🏻

    • @cube1us
      @cube1us 2 ปีที่แล้ว

      Until your charger device fails.

  • @theflew
    @theflew ปีที่แล้ว

    Something not mentioned here is that you should be pushing at most 40A through the 14-50 outlet regardless of make. I wonder if many of those melted sockets were people trying to charge at 48A. Not saying an industrial outlet shouldn't be used, but if the outlet is rarely unplugged and you're not trying to push more than 40A through it, and it is properly installed (torqued), then many outlets, industrial or not, should work.
    I've had a 32A charger plugged into an Eaton 6-50 surface mount outlet for 7 years and no problems. The plug was only removed once when a surge knocked out the charger, and I replaced it with a new one plugged into the same outlet.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      It’s all about risk. Hard-wired is the best, but if you don’t want to hard-wire then an industrial outlet is better than a standard one.

  • @bubbavox
    @bubbavox 11 หลายเดือนก่อน

    In technical terms, a hardwired charger would still be an 'outlet'. But it wouldn't be a receptacle. At least in the States. Sorry, couldn't help myself. Helpful video, thanks.

    • @handydadtv
      @handydadtv  11 หลายเดือนก่อน

      Yes you are absolutely correct. I knew someone would point that out. You win!

  • @BoatyMcBoatface669
    @BoatyMcBoatface669 ปีที่แล้ว

    Thanks for this informative video. It's almost Sept '23 and the Hubble is down to about $80 on the Zon. The Bryant was about $10 cheaper there.
    Hardwiring has advantages, but you can't take your charger on vacation or when you sell your home... still on the fence but you gave me something to ponder for sure.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      FWIW, I just upgraded from a 2020 to 2023 Model Y (th-cam.com/video/ZfhLjeuqheU/w-d-xo.html) and I’m still using my 2020 UMC and Hubbell 14-50.

  • @chargermopar
    @chargermopar ปีที่แล้ว

    I know they are no longer used, but all my 50 amp outlets in my shop are nema 10-50 and I have never had one fail, even when running a 5 HP compressor! Most are Eagle brand but the plugs are all Leviton. Being old they seem to be a higher quality.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Plus your tools don’t draw 40 amps continuously for hours.

    • @chargermopar
      @chargermopar ปีที่แล้ว

      @@handydadtv The compressor is on and off, I never measured how much current the lathe or mill use. I just dug out an old Leviton welder outlet 6-50 and it's a lot better built that the new range outlet i have in my parts box!

  • @baylinkdashyt
    @baylinkdashyt ปีที่แล้ว

    Hey, look! When plugged in, that cord cap at 1:20 has its ground pin... on top.
    I guess this settles the "Where should the ground pin on a mounted edison receptacle be?" question...

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      It doesn’t matter.

  • @nasrsayed9362
    @nasrsayed9362 2 ปีที่แล้ว +3

    I had the Leviton 14-50 outlet from homedepot, 50a dual pole fuse, on a 1989 150a panel, with a Gen 3 Tesla wall charger. The setup created a scary humming at the panel at 48a. I figured it was my old panel causing the humming so I lowered the charge amp's to 40a on my Tesla app. Which is when there was little to no humming heard at the panel. After watching your video I replaced the Leviton with a Bryant for safety and even ordered a new 200a panel with all new fuses which is arriving this weekend (11/19/22). To my surprise the Bryant 14-50 outlet with my old panel and 50a fuse didnt hum at 40a, or at 42a, 46a, and not even at 48amps! I am still going to replace my old panel, and loving the 42mil/hr new faster charge rate.
    Fyi: I touched my Bryant outlet and the box it is in after 2 hours of charging and it is cool to the touch. The fuse in the panel though was pretty warm like my Gen3 charger wire going to the car.
    Leviton 14-50 outlet diffiantly should not be used for car charging. Though it cost me about $14 and the Bryant cost me $50 I have to say the Bryant 14-50 outlet was money well spent.

    • @cube1us
      @cube1us 2 ปีที่แล้ว +3

      If you have a 50 amp circuit breaker, you should not charge at more than 40 A. Code requires a 25% headroom on any circuit. So for a 50 amp breaker you should not charge at more than 40 A. Your breaker was humming because it was very near the trip point.

    • @nasrsayed9362
      @nasrsayed9362 2 ปีที่แล้ว

      @@cube1us Thankfully it is not humming now, however, I will reduce the charge rate of 48 amps.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +4

      Use the lowest charge rate necessary to recharge your daily commute. No point in stressing everything to charge in 2 hours when your car sits idle for 10.
      I charge at 15 amps now and it’s still typically done by midnight.

  • @568843daw
    @568843daw ปีที่แล้ว

    So this particular Hubble receptacle is actually made and rated for 240volts & 50 amps. The available neutral is to run miscellaneous lights and carry the unbalance load back to the panel. It is a current carrying conductor just like the two other hot circuits. The ground is like an emergency pressure relief valve and is used infrequently during a short or arch and sends that back to the panel and to the earth to prevent the melt down of the wires and helps the breaker to turn off. All of these features are what you want. So the Hubble is a great receptacle (Plug) and professionals use them all the time… even in their own homes. Hubble makes durable, long lasting products. Of course, you should buy the appropriate plug of your choice and certainly use the configuration that the manufacturer wants you to use. To get an even more durable Hubble receptacle, get the Hospital grade which has a green dot stamped on its face. Your EV plug will get a lot of electrical excercise on a daily basis. Don’t bet your life on a receptacle that is cheaply made. How much is your life and the lives of your family worth to you? I’m just ask’n?😊

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Thanks for your input

  • @lakorai2
    @lakorai2 หลายเดือนก่อน

    Leviton, Eaton etc make EV rated NEMA 14-50 outlets now. This is now required by the NEC for EV outlets to have an EV logo on the outlet.
    In addition you have to get WR rated outlets if this will be installed outdoors.

    • @handydadtv
      @handydadtv  หลายเดือนก่อน

      Yes thanks.

  • @dpc316
    @dpc316 ปีที่แล้ว

    Thank you returning my outlet and hardwiring :)

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Too bad you bought it in the first place.

  • @MrChevyguy28
    @MrChevyguy28 2 ปีที่แล้ว +1

    Great video! I never knew about the bryant option tuvm!

  • @athuddriver
    @athuddriver ปีที่แล้ว

    Too late...already got it based on the previous video. LOL Only $98 back then. I had a 50A outlet installed as part of the build for our new home but I see from this and other sources they made a mistake. The breaker is NOT GFI. I ordered a Chevy Bolt (I'll not see it for at least 6 months) and thought I would take the $500 charge card. I think that I will change that to the installation offer to get a second opinion on the set up. Ya, I bought the outlet already but I've learned a lot more since and will probably remove it and go hard wired now. Good video and the price of a GFI breaker "shocked" me. LOL

  • @miteeman
    @miteeman 9 หลายเดือนก่อน

    Love the video. After 5 years of 32A charging with a Home Depot Leviton my Tesla is starting to have High Temperature warnings. Amazon is currently selling the Hubbel for $70 and Bryant for $49. I was going to go with Bryant but I decided the $20 isn't a big enough savings. Neat idea about the 6-50 since I don't have a neutral wire anyways but Hubbell 6-50 is $33 + Tesla 6-50 adapter is $45. Is it a code violation to not have the neutral wire to that outlet? Next I have to buy a torque screwdriver!

    • @handydadtv
      @handydadtv  9 หลายเดือนก่อน

      I’m pretty sure it’s a code violation to have an open neutral, but who’s checking?

  • @mernokimuvek
    @mernokimuvek 4 หลายเดือนก่อน

    These videos make me even happier that in Europe we have 230/400 V 3 phase services. 3x16A instead of single phase 50 A.

    • @handydadtv
      @handydadtv  4 หลายเดือนก่อน

      Thanks for sharing

  • @elbergalarga2562
    @elbergalarga2562 ปีที่แล้ว +1

    Question for hard wired installation and avoid outlet, is it ok to just just use a 60 A dual breaker from Lowes or Home Depot? Or do I still need the $150 dollar breaker? Sorry I'm just a little slow. I did buy the Emporia Charger. Thanks for your video and alternative.

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      You don’t need the expensive GFCI breaker if you’re hard wiring your charger.

  • @1942nn
    @1942nn ปีที่แล้ว

    It's absolutely true that using a hardwired charger cost about the same as using expensive GFCI breaker and high quality outlet. I was lucky that I installed the Wall Connector for my Tesla. It does not need GFCI breaker, look good and can run upto 40A at home.

  • @thabte
    @thabte 2 ปีที่แล้ว

    Great video! Thank you for sharing. I ended up going with Tesla home charger hard wired.

  • @Sparky-ww5re
    @Sparky-ww5re 2 ปีที่แล้ว +1

    Good advice. Not sure why most tesla level 2 chargers include a 14-50P when no neutral is used. Why not just simplify and make a 6-50 as standard. The only time you really need a nema 14 wiring device, whether it be a 14-20R, 14-30R, 14-50R or 14-60R, is when you have a piece of equipment that is a combo line to neutral and line to line load, such as an electric dryer or range, amount certain other equipment. A nema 6 wiring device is cost effective for line to line loads. You can then run less costly XX/2 w/G NM cable and of course wrap a piece of black tape around the white conductor to re identify it as being a hot conductor.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +2

      I asked that question and someone commented that the 14-50 is a standard in RV parks everywhere. So I guess that’s why they are more popular for EVs.

    • @Sparky-ww5re
      @Sparky-ww5re 2 ปีที่แล้ว +1

      @@handydadtv well that's logical. I enjoy camping and of course you cannot visit and RV park and not see a TT-30R and a 14-50R simultaneously. And larger RV is obviously a line to neutral and line to line load like your house. Thanks for your kind words I enjoyed your videos.

  • @Appalachiannative
    @Appalachiannative 2 ปีที่แล้ว

    Off topic but need you to do a video on what’s going on with Insteon or what if anything you are doing or plan on doing as a work around. Sorry like I said I know it’s off topic but you’re the first person I thought of when my Insteon light went red last week

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      In the works. 😉

  • @rkgsd
    @rkgsd ปีที่แล้ว

    What RV weatherproof enclosure with fit the larger 2.4" diameter of the commercial grade 14-50? The faceplate on most housings is for the smaller off the shelf receptacles.

  • @lakorai2
    @lakorai2 หลายเดือนก่อน

    Might as well go with a NEMA 14-60 as it is now allowed by the NEC 2023 code.
    The advantage of an outlet is you can use portable level 2 chargers. Otherwise I guess you could hard wire a charger and also buy a portable charger.

    • @handydadtv
      @handydadtv  หลายเดือนก่อน

      Hardwire is the best way to go.

  • @ericklein5097
    @ericklein5097 5 หลายเดือนก่อน

    Does the Bryant NEMA 14-50 have brass contacts inside the outlet? Thats pretty much the core of the resistance issues with the el cheapos

    • @handydadtv
      @handydadtv  5 หลายเดือนก่อน

      I can’t say for sure but they look just like the Hubbell.

  • @jdd91401
    @jdd91401 10 หลายเดือนก่อน

    Important to note that hardwired charger will max out charging and give a 20% boost to charge power and speed vs plug in. Which is why 60A breaker is required. Another tip if you smile a receptacle - buy a (properly rated) extension cord and plug and unplug from that - most have a handle with grips to make it safer and this will save wear and tear on your receptacle.

    • @handydadtv
      @handydadtv  10 หลายเดือนก่อน

      In reality, people rarely unplug their chargers. But every junction has the potential of generating heat which wastes energy and increases the risk of failure. I would never recommend using an extension cord because it adds another junction. Hard wired is always best.

  • @tirec8039
    @tirec8039 2 ปีที่แล้ว

    You made excellent points for hard wire option 😀😀.

  • @drenalin_junkie
    @drenalin_junkie 24 วันที่ผ่านมา

    Wow great advice. Thanks for the video!

    • @handydadtv
      @handydadtv  24 วันที่ผ่านมา

      Glad it was helpful 👍🏻

  • @myreviews4905
    @myreviews4905 ปีที่แล้ว +1

    I am installing a Tesla wall charger. I would like to have a Nema 14-50R as back up. I don't want to spend the $130 on a GFCI breaker 50A. What will happen if I just use a regular breaker?

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      If you’re getting the wall charger inspected, don’t install the outlet until after the inspection.
      Worst case scenario (other than potential electrocution) is a home inspector might flag it when you go to sell the house.

    • @DanielinLaTuna
      @DanielinLaTuna ปีที่แล้ว

      Second worst case scenario: you have an electrical fire and the insurance company doesn’t pay out because of code violation. They WILL investigate before settling, rest assured; it’s standard operating procedure.

    • @myreviews4905
      @myreviews4905 ปีที่แล้ว

      @@DanielinLaTuna I learned that when you deal w car accidents, or insurance companies, you need to get a lawyer. They get you to buy insurance by promising you a bunch of stuff. And when the claim comes, they don't want to pay. You need to get the right lawyer.

  • @KevinCoop1
    @KevinCoop1 ปีที่แล้ว +1

    You must be careful using the Bryant! It is only rated for 60C. The Hubble is rated 75C. You must use 60C column for conductor ampacity. The GFCI requirement is required if your AHJ has adopted the 2020 NEC. That is the first it is required to be GFCI. I totally agree, it is best to hardwire the charger. I have no idea where people came up with thinking they need a 14-50r. BTW that is the receptacle used for larger RV power connection.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Thanks for the info!

    • @stevenqi2338
      @stevenqi2338 ปีที่แล้ว

      @@handydadtv thanks a lot for both the videos. My electrician said he will just use a Leviton from HD but I now concerned. I am not a professional but #1 the link of the Bryant shows 14-30R; and #2 is that 60C vs 75C an issue for my Tesla M Y charging? Would appreciate if you can respond. Thx.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      My preference, in order:
      1. Hard wire a wall charger
      2. Hubbell 6-50
      3. Hubbell 14-50
      4. Bryant 14-50

    • @KevinCoop1
      @KevinCoop1 ปีที่แล้ว

      @@handydadtv I totally agree with your choices!

    • @802Garage
      @802Garage ปีที่แล้ว

      Both have an environmental rating in the spec PDF of 75C. However, neither device is actually marked 75C and therefore must be used as a 60C device. Both also come with instruction sheets which say to use conductors rated according to the 60C column. They are functionally and specs wise identical, and are very likely identical in manufacturing other than the stamped name. Both must use 6 gauge copper conductors in order to create a true 50A general use circuit. Neither may be used with aluminum conductors.

  • @ohmygosh6176
    @ohmygosh6176 ปีที่แล้ว

    I agree hard wire is the way to go. My electric stove is hard wired.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      That’s good 👍🏻

  • @ntech722
    @ntech722 2 ปีที่แล้ว +16

    I’ve installed plenty Nema 14-50 from Home Depot and lowes that cost around 20 bucks . Haven’t had any issues so far . Works just fine .

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +22

      Until it doesn’t.

    • @Ozzie4Para
      @Ozzie4Para 2 ปีที่แล้ว +11

      @@handydadtv yeah, I agree. I bought the $150 Hubbell from Amazon a couple weeks ago. I took it to my local Lowes just to compare it to what they're selling. You can definitely see and feel the weight difference between the two. Why would anyone choose to "cheap out" on something like this when you're only going to install this type of outlet once for your EV? People need to remember how much power is flowing through these outlets. Yes, the cheaper ones from Lowes or HD will work. But for how long? Charging a Tesla can easily consume 30A or more on these outlets. Who wants to trust that kind of power going through a cheaper made outlet? No me.

    • @NewPhase-kq1fu
      @NewPhase-kq1fu 2 ปีที่แล้ว +15

      Electrician here. I agree with V Ng. Properly installed standard NEMA 14-50 is fine. It’s rated for 50A, the chargers only pull 40A (80%). The burnt outlets you showed were likely due to poor installation. Why you should hire an electrician. Even when the prongs are melted that’s often the result of loose screw connections. The heat transfers from the back to the front of the outlet.

    • @anthonyking7849
      @anthonyking7849 2 ปีที่แล้ว +8

      @@NewPhase-kq1fu I had one failure early on before Tesla started recommending the industrial outlets. It was properly installed by one of my jouneymen. I now exclusively use the industrial outlets for ev charging. While the cheap outlets are rated at 50 amps it isn't worth the risk of a call back.

    • @KevinCoop1
      @KevinCoop1 2 ปีที่แล้ว

      One must be careful with higher ampacity receptacles. Hubbell was the first company to change their connections from 60 to 75C. There may still be some at the lower ratings. Not always easy to find the info. I agree with newphase.

  • @ne8r
    @ne8r 2 ปีที่แล้ว +1

    Leviton - $12.95. I have used for 4 years with my Level 2 charger, remains cool.

    • @FGOKURULES
      @FGOKURULES 2 ปีที่แล้ว

      Leviton here and just started over heating 🤣

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Why tempt fate

    • @FGOKURULES
      @FGOKURULES 2 ปีที่แล้ว +1

      @@handydadtv just bought a Bryant Receptacle

  • @danilomagcalas9215
    @danilomagcalas9215 2 ปีที่แล้ว

    Hi chris,can i use 2 wire with ground to nema 14-50.What will happen if there is no white wire?thanks

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      You need to make sure your EVSE doesn’t need it.

  • @PJ-ee5mc
    @PJ-ee5mc ปีที่แล้ว

    Thanks, Dad! Great video.

  • @brucetrx
    @brucetrx ปีที่แล้ว

    The link to Bryant is now to their 14-30R. The 14-50R costs $200 on their website

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      That’s an issue on the Grainger website. The model and description are for the 14-50. The picture looks wrong. Call them.

  • @garbo8962
    @garbo8962 2 ปีที่แล้ว

    Wow 68 dollars then over a hundred must have solid gold contacts. Had trouble a few years back with Hubbell hospital grade 20 amp duplex receptacles. Stainless steel s crew would tighten up but needed a least a full turn to secure wall plate. Anyway heads on 6 /32 screws would break uo . They were all made in Korea. Glad that I retired 3 years ago. Last roll of 12/2 Romex that I purchased maybe 20 years ago was probably only $25. Home Depot wants $259 for a 250' coil. wow over a buck a foot.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Yeah it’s crazy

  • @TheMrprez
    @TheMrprez 2 ปีที่แล้ว

    Grainier is back ordered on the Bryant 6-50.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      This video could be to blame. 😳

  • @LuLu_World
    @LuLu_World 7 หลายเดือนก่อน

    Hubbell makes a $10 resi grade too. but only use what the charging station specifies. tesla specifies hubbell hbl industrial grade

    • @handydadtv
      @handydadtv  7 หลายเดือนก่อน

      Thanks

  • @crazaholic1968
    @crazaholic1968 ปีที่แล้ว

    Thank you so much for this video. I just purchased the 14-50 Bryant outlet and the face plate following your link. I was going to get the Hubbell wall plate as recommended until I saw your link. What about the electrical box? Any standard box will work or need bigger one?

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      Wait for the outlet to arrive and bring it to Home Depot to get a box that fits it.

    • @crazaholic1968
      @crazaholic1968 ปีที่แล้ว

      @@handydadtv That works. Thanks!

  • @rkgsd
    @rkgsd ปีที่แล้ว

    I was dead set on a basic 14-50 outlet until I saw this video. I'm feeling lucky I saw it. I'll be looking into a hardwired solution for outdoors (side of house) that's designed to handle the sun and rain...probably Grizzl-E or Emporia.

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      Smart move. 👍🏻

  • @HansKlossJ23
    @HansKlossJ23 ปีที่แล้ว

    I also think that reviews on the TH-cam is one of the reason why prices are rising so much. Bryant 9450FR in Canada cost now $134!

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      I’d like to think I have that much influence but it’s hard to believe.

  • @stargazer2504
    @stargazer2504 ปีที่แล้ว +4

    Don't forget to check out the Federal, State & Local rebates, including the local power company rebates available when you install an EV port.
    The rebates can almost offset the entire cost of the high end wiring/outlets/ports, etc.
    Bottom line: If you are installing one, check the rebates and they will probably cover the high-end receptacles, wire, etc. anyway.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Thanks for the tip

  • @Dupont550
    @Dupont550 2 ปีที่แล้ว

    Thanks for pointing out the need for a GFCI, a lot of videos about the mobile connectors leave that information out.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      Many people debate that it’s not needed. 🤷🏻‍♂️

    • @NewPhase-kq1fu
      @NewPhase-kq1fu 2 ปีที่แล้ว

      GFCI is not necessary. Not required by code. And GFCI protection is built into a EVSEs

    • @andrewt9204
      @andrewt9204 2 ปีที่แล้ว

      @@NewPhase-kq1fu 2020 code removed all exceptions for 125-250V receptacles. Including things like dedicated dryer and oven receptacles. Plug-in EVSE's need to remove GFCI protection because of this, or better yet have it selectable as states on the 2017 code didn't require GFCI on 250V receptacles. Either way, doesn't seem smart to forego some kind of GFCI protection on a high powered circuit like that with a long cord and in a potentially wet environment.

    • @NewPhase-kq1fu
      @NewPhase-kq1fu 2 ปีที่แล้ว +1

      @@andrewt9204 They don’t need to remove GFCI from EVSEs. Nothing wrong with redundancy. Where I am we’re still on 2017 code, so GFCI not required on 220v. But, doesn’t matter because again, EVSEs have GFCI protection built in. Not a safety issue, even in wet environments.

    • @Wowzersdude-k5c
      @Wowzersdude-k5c 2 ปีที่แล้ว +2

      @@NewPhase-kq1fu The reason it is code (in 2020) is because the 240V outlets can be used for things other than EV charging. An outlet is an outlet. In fact, GFCI's have been required outdoors or in garages since 1975 (kitchens were added in 1987). But for decades they exempted 240V outlets because 240V outlets are rare (in America) and were only used for large appliances. But in 2020 this changed - most 240V outlets need GFCI now. In fact, even the washer/dryer are required to be GFCI protected now (this came after a kid was killed when he touched a faulty washer). I am surprised it took them until 2020 to require GFCI on 240V outlets.
      So, while it is true that EV chargers come with built-in GFCI's, it is also true that you can use that outlet for other appliances that don't have GFCI protection. I suspect this is why it is now code. With the proliferation of EV's, we are gonna see people using those outlets for other things. One guy in the comments here said his wife uses his EV outlet for other stuff. So, yes, it happens. And that's why they want them GFCI protected.

  • @overdriver99
    @overdriver99 ปีที่แล้ว

    nice video. I agree that hardwire method is the best. BTW, your Bryant link goes to '14-30R' with 30A rating... I am little confused that description is different from picture...?!?

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      That appears to be a problem at Grainger. My link searches for model 9450FR. The correct model number and photo are shown, but the item name is wrong.

  • @tommckinney1489
    @tommckinney1489 7 หลายเดือนก่อน

    The other reason to hardwire is that most chargers have a built in GFCI. Installing a breaker with a GFCI (most codes require it) means there are two GFCIs in series, which can cause on or the other to trip and your car will stop charging. You may or may not get a notification when this happens. Hardwiring solves this issue and keeps everything to code.

    • @handydadtv
      @handydadtv  7 หลายเดือนก่อน

      My Tesla UMC never had an issue being plugged into a GFCI breaker.

  • @Ozzie4Para
    @Ozzie4Para 2 ปีที่แล้ว +2

    Thanks for the great info. My Model Y performance car should be delivered to me hopefully sometime next month. I recently bought the $150 14-50 outlet from Amazon even though it made me cringe to spend that kind of money on one outlet. Of course supply/demand takes over everything. Plus I've been on Tesla's waiting list to buy a 14-50 plug which has been out of stock. So now I went with your advice and I'm going with the 6-50 alternative instead. Cheaper outlet and cheaper wire for something that will do the same exact thing if you go with the 14-50. Doesn't make sense to go the more expensive route. Why spend the extra money going the 14-50 route if the neutral line isn't needed?

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      I learned so much since buying my Model Y in 2020. You’re absolutely right that the 14-50 is overkill for EV charging and I have no idea why it became so popular.

    • @andrewt9204
      @andrewt9204 2 ปีที่แล้ว +1

      @@handydadtv I'm pretty sure it was because of RV parks. It was a semi-popular way to lvl 2 charge out in the wild in the early EV days. That and maybe because a lot of homes have a 14-50 for their stove as a makeshift way to lvl 2 charge with an extension cord.
      I installed a 6-50 to use the UMC, but decided I wanted a more permanent solution after deciding I was going to keep the tesla for a while. I hard wired a Grizzl-e EVSE and it has been great. Really robust unit that should last forever. I just bought an extra J1772-Tesla adapter to leave on it permanently.
      I wanted J1772 just in case something better than the Tesla came along or I got an electric quad or motorcycle.

    • @VienQuach
      @VienQuach 2 ปีที่แล้ว

      Picking up my MYP this weekend.
      Im probably going to hardwire the charger (wall connector).
      I have a 40A breaker/outlet in the garage.
      Not sure if i need to spend the extra $$ to run a 60A wire to the garage (40ft from main panel).
      I only use maybe 10 miles/day. 😀

    • @jasonhadid7477
      @jasonhadid7477 2 ปีที่แล้ว +2

      ....because if you plan on ever selling your house the buyer will want a NEMA 14-50 since it's the most popular and therefore most likely the one that the buyer's charging equipment is compatible with.

    • @Ozzie4Para
      @Ozzie4Para 2 ปีที่แล้ว +2

      @@jasonhadid7477 if the buyer wants a 14-50 outlet then he can pay someone to install it. Won’t be my problem.

  • @aliaghili1785
    @aliaghili1785 ปีที่แล้ว

    Is there a difference in weight?
    Did u weigh both?

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      I didn’t put them on a scale, but they felt identical.

  • @pear7777
    @pear7777 2 ปีที่แล้ว

    True, although I would install a gfci breaker, even when hardwiring, but still good advice!

    • @GerardPinzone
      @GerardPinzone 2 ปีที่แล้ว

      The EV charger has built in GFCI.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      I’ve yet to see a GFCI test button on an EVSE.

    • @benefactionhindrance
      @benefactionhindrance 2 ปีที่แล้ว

      Code requires gfci protection but code also says follow manufacturer recommendation and the Tesla wall charger says gfci protection not required. Both of you and op are right (:

  • @GR-zd6xl
    @GR-zd6xl 2 ปีที่แล้ว

    Great videos. Do you have any recommendations for 6/2 and 6/3 cables and circuit breakers? Thank you.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      For circuit breakers, you need to stick with the brand and type for your panel.
      No specific recommendation for wire, but some places require conduit instead of Romex like I used. Check local codes.

    • @GR-zd6xl
      @GR-zd6xl 2 ปีที่แล้ว

      @@handydadtv Thank you again.

  • @baylinkdashyt
    @baylinkdashyt ปีที่แล้ว

    Question: are you sure that all EVSE's have on board electronics which are 240V native, and do *not* require the 120V circuit provided by the neutral missing on the 6-50R?

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      I only recommend using a 6-50 for EVSEs that come with 6-50 plugs.

  • @DrRavi-MusicallyYours
    @DrRavi-MusicallyYours ปีที่แล้ว

    Do you happen to know the terminal screw torque settings for Bryant 14-50 outlet? Thanks, HandyDad..

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      They’re in this video: th-cam.com/video/1BnK4a4aVpU/w-d-xo.html

    • @DrRavi-MusicallyYours
      @DrRavi-MusicallyYours ปีที่แล้ว

      @@handydadtv thanks. I thought in this video link it was a Hubble outlet you were working on with the torque setting of 75 lb-in. Is it the same for Bryant outlet terminals too?

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      I never installed the Bryant. I just bought it for the comparison.

  • @Alex-py6rf
    @Alex-py6rf ปีที่แล้ว

    The Bryant link from grainger with the same manufacturer number 9450FR now lists a different product, a 14-30R for 30 amps

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Yeah their website is screwed up.

  • @EternalDharma01
    @EternalDharma01 ปีที่แล้ว

    Question - Tesla Gen 3 charger doesn't require GFCI circuit breaker ?

    • @handydadtv
      @handydadtv  ปีที่แล้ว +1

      The charger doesn’t require a GFCI; it has one built-in.
      The outlet itself needs GFCI protection.

  • @mythril4
    @mythril4 ปีที่แล้ว

    If a neutral is needed you use the 14-50, if not the the welder plug is fine. What is most important to me is how the wires mount and the structure of the plastic, seen lots of broken and burnt ones, they were cheaper.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Good point

    • @ScottDLR
      @ScottDLR 11 หลายเดือนก่อน

      The Emporia does not use a neutral and the plug they provide has the pin but no wire to it.

  • @cgamiga
    @cgamiga 2 ปีที่แล้ว

    Thanks so much! relatives shopping now for new EV, and having price shock re the Hubbell!
    I'm not sure all codes require GFI breakers for EVSE plug-in install... The Tesla charge cable doesn't always work well on GFI outlets either, as it has GFI built-in

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      The Tesla UMC has no issue with my GFCI breaker.

    • @geoffmooregm
      @geoffmooregm 2 ปีที่แล้ว

      GFCI is totally un-necessary unless you will charge outdoors and the plug socket in the car gets wet.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      @Geoff Where does it say that in the code?

    • @geoffmooregm
      @geoffmooregm 2 ปีที่แล้ว

      @@handydadtv NEC 2020 Section 625.54, which covers electric vehicle charging systems with regards to GFCI protection for personnel. The protection requirements have been expanded to require all receptacles installed for the connection of electric vehicle charging to have GFCI protection. The previous requirements of single-phase, 150 volts to ground or less, and 50 amperes or less have been removed. These changes were made to clarify the intent of providing GFCI protection for personnel and all cord and plug connected electric vehicle power transfer equipment, regardless of phase, voltage or amperage ratings.
      As I understand it all EV chargers have built in protection. So ADDITIONAL GFCI is totally un-necessary however I would still consider it if the cord could lay in the rain or somehow a connector or adapter could be connected before the GFCI part of the circuit is connected then it may be a hazard. I don't know how every different EV charger is designed so it should really be case by case.

  • @jamesstewart2543
    @jamesstewart2543 ปีที่แล้ว

    I ordered the Bryant NEMA 14-50r for an electric range, but the instructions state copper conductor only and I have aluminum conductor.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Do not use it with aluminum wire.

    • @jamesstewart2543
      @jamesstewart2543 ปีที่แล้ว

      @@handydadtv I am shocked and dismayed that the Bryant NEMA 14-50r is not rated for aluminum conductor.I thought all good quality receptacles would be rated Cu/Al. I am of course gong to return it. Do you know of another better quality 14-50r that is rated for aluminum? I could pigtail the aluminum, but the rated connectors for connecting aluminum to copper are expensive in the size required for 4 AWG aluminum.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      I’m sorry I don’t.

  • @tinujatinpatel
    @tinujatinpatel 2 ปีที่แล้ว

    The 14-50 provides a little more protection with the neutral against lightning strikes. Agree generic just as good as the hubble.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      If nothing is connected to the neutral, it provides no benefit.

  • @arturreef8117
    @arturreef8117 2 ปีที่แล้ว

    Hey just fyi, if I am not mistaking the tesla car you don't need gfci breaker. It can cause issues from my understanding

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      I use a Tesla UMC on a GFCI breaker without issue.

  • @andreberthet1283
    @andreberthet1283 10 หลายเดือนก่อน

    One advantage of using a NEMA 6-50 receptacle is that you don't need to run the unused NEUTRAL 6-AWG wire from your panel to the receptacle, and it makes it easier to tuck the two 6-AWG hot wires and the 12-AWG ground wire in the back of the box.

    • @handydadtv
      @handydadtv  10 หลายเดือนก่อน

      The best is a hardwired charger.

  • @travbz24
    @travbz24 2 ปีที่แล้ว

    Planning to go the hardwired route. The Emporia instructions say to use a 60 amp double pull. Sound accurate?

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      You can use UP TO 60 amps. That’s overkill in most situations. If you have a long run, go with 50-amp because the wire will be thinner. Copper is expensive.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      You can use UP TO 60 amps. That’s overkill in most situations. If you have a long run, go with 50-amp because the wire will be thinner. Copper is expensive.

    • @travbz24
      @travbz24 2 ปีที่แล้ว

      Hardwiring follow up on the Emporia. I was planning 6/3 romex. It appears their install instructions don't call for a neutral. Thoughts? Can 6/2 be used?

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      Correct. Just use 6/2. Level 2 chargers don’t need a neutral wire.

  • @jonesgang
    @jonesgang 2 ปีที่แล้ว

    Eaton and Leviton also make the nema connectors. Hubble is just top of the line, nice to have but overkill.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว

      There are tons of receptacle brands. But you need to stick with industrial grade, and you won’t find those in home centers and hardware stores.

    • @jonesgang
      @jonesgang 2 ปีที่แล้ว

      @@handydadtv Utilitech does make industrial nema 14-50 for just under $11.00
      Now I also do prefer Hubble over the rest of the available brands. Some applications just do not require such heavy grade devices, and an EV charger is one that does not have to be overkill. While it never hurts to try and up-sale something. You need to take every situation into account.
      Yes we would all love to drive a tank down a freeway but not very practice.

  • @atitraval4584
    @atitraval4584 ปีที่แล้ว

    Hi Chris, thank you for these informative videos. I am planning to install my charger ( not yet decided between Nema or hardwired) in my driveway. If I install a Nema plug I will need GFI breaker but what if I install hardwired charger like one you have in my driveway, will I still need a GFI breaker? Thanks for creating these videos.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      You only need a GFCI breaker if you install an outlet.

    • @atitraval4584
      @atitraval4584 ปีที่แล้ว

      @@handydadtv I see. So in this case I might be better off installing a hardwired device since cost of breaker will be more. Thank you for your reply.

    • @handydadtv
      @handydadtv  ปีที่แล้ว

      Hard wiring is cheaper and safer.

  • @REWYRED
    @REWYRED 2 ปีที่แล้ว

    You can get different versions of those outlets by different manufacturers that are just as good.
    You can get here in Canada anyway a NEMA 14-50 that is meant to mount on a 4 11/16" box, a "Stove Receptacle" it's called and are worth about $6 or so at a supplier..
    Could also get a "50A welder receptacle", NEMA 6-50 surface mount receptacle, prolly worth $15, maybe $20.

    • @handydadtv
      @handydadtv  2 ปีที่แล้ว +1

      I’m advocating hard wiring these days.

    • @geoffmooregm
      @geoffmooregm 2 ปีที่แล้ว +2

      I am in Canada too and I don't ever remember having sticker shock at my two 50A 240V plugs. They are high quality and CSA Approved.

    • @LuLu_World
      @LuLu_World ปีที่แล้ว

      Other manufacturers are not just as good LOL. Just weigh the receptacle. Brass contracts vs steel, heavy duty terminals and contacts for lower heat resistance and performance. I will pay and extra $50 vs burning down my garage and $60K EV car

  • @kentma7516
    @kentma7516 2 ปีที่แล้ว

    what is the cover for Bryant receptacle?

  • @boybabyboy29
    @boybabyboy29 9 หลายเดือนก่อน

    I prefer a nema 14-50 outlet rather than a home charging station but What if you don’t live in a house, what about apartment complex?

    • @handydadtv
      @handydadtv  9 หลายเดือนก่อน

      For public parking, the apartment complex should provide secure public charging stations. Even if they let you install a 14-50 from your unit, people would steal your electricity when you weren’t there.

  • @stevephla
    @stevephla 7 หลายเดือนก่อน

    Hubbell 14-50 is down to $58.89 on Amazon as of April, 2024. Pretty wild price swings.

    • @handydadtv
      @handydadtv  7 หลายเดือนก่อน

      Wow!