    Yes we can use that type of AVR but u have to supply input voltage at L-N to get 240Vac from stator windings output voltage with excitation current of 3amps per 10secs.

  • @EdelSM
    @EdelSM 4 ปีที่แล้ว +2

    for remote voltage adjustment potentiometer ay OK lng kahit more than 1watt, and mas better. but the resistance should be 1k as per the manual.

  • @DieselGeneratortraining
    @DieselGeneratortraining 3 ปีที่แล้ว +1

    Sir did u suggest to install the 6 amps breaker on AVR output or not as u mention there is no Protection on AVR

  • @franciscorabano8025
    @franciscorabano8025 ปีที่แล้ว

    Sir.. mike pwedi nyo po ba magawan ng video yong sa load sharing at paralleling requirements para sa dalawa or more generators.. thanks

  • @aslamsajjad8867
    @aslamsajjad8867 8 หลายเดือนก่อน +1

    Yes it is compatible.

  • @gabornerimar2094
    @gabornerimar2094 4 ปีที่แล้ว

    Tnx you sa video sir good bless and more power

  • @teloexplicaeldiamante2855
    @teloexplicaeldiamante2855 11 หลายเดือนก่อน +1

    MY AVR GAVE AT MAXIMUM RANGE, THE GENERATOR IS 220 V AND GENERATES 355 V.
    IT DOES NOT ADJUST BY THE VOLTAGE POTENTIOMETER. WHAT WAS DAMAGED?

    • @shuttlemarineengineering
      @shuttlemarineengineering  11 หลายเดือนก่อน

      What is the brand and capacity of the alternator?

    • @teloexplicaeldiamante2855
      @teloexplicaeldiamante2855 11 หลายเดือนก่อน

      IT IS A CARD EQUAL TO THE STAMFORD, BUT UNIVERSAL. MY QUESTION IS: WHAT COMPONENT WAS DAMAGED TO THE CARD SO THAT IT DOES NOT REGULATE THE OUTPUT AND IS AT MAXIMUM RANGE

    • @shuttlemarineengineering
      @shuttlemarineengineering  11 หลายเดือนก่อน +1

      @@teloexplicaeldiamante2855 Hard to know which electronic component gave up, but based on your info’s it’s on the regulation circuitry. But if fitted with remote V adjustment is suggest you check if it’s open or if connection from potentiometer to avr if not broken or loose. A loose remote V potentiometer also causes high V output. If no remote then AVR is defective. Thanks

  • @joeopilas52
    @joeopilas52 4 ปีที่แล้ว

    The regulator of my 7.5 KVA generator has corroded and I want to replace it with a new AVR just like this SX460. I understand this is designed for a brushless generator which requires a smaller amount of current considering that the AVR is powering a slave generator which in turn supply a bigger amount of current to the exciter of the main generator.
    The way I look at it is that the voltages are just alright for my generator and the AVR. I just want to know if its 4A continuous current in the output is adequate to power the exciter field of my generator. By the way its exciter resistance is 6.9 ohms. Thank you very much and keep up the good post.

  • @crellyortilla1194
    @crellyortilla1194 2 ปีที่แล้ว

    Thank you sir Mike God bless 🙏🙏🙏. Si undo ito

  • @teloexplicaeldiamante2855
    @teloexplicaeldiamante2855 11 หลายเดือนก่อน

    I HAVE AN AVR SX460 INSTALLED ON A 220V GENERATOR. BUT NOW IT IS GENERATING 360 V AND IT DOES NOT TAKE ADJUSTMENT BY THE VOLTAGE POETENTIOMETER. I ASK YOU: IS IT A PROBLEM WITH THE AVR CARD OR IS IT AN INTERNAL PROBLEM. BECAUSE THE CARD LOOKED GOOD

    • @shuttlemarineengineering
      @shuttlemarineengineering  11 หลายเดือนก่อน

      SX460 max input in 264V only and it’s receiving 360v and since this avr’s does not have fuses then your avr is probably gone. Check excitation V how high is it and from there you can confirm that you have a defective AVR. Damaged rotating diodes or burnt winding wont show a high voltage, instead it produces a very low V. Thanks

  • @goldgolden3004
    @goldgolden3004 2 ปีที่แล้ว

    Thank you so sir . Good bless you

  • @kennethbuenaflor4372
    @kennethbuenaflor4372 5 หลายเดือนก่อน

    Hi ser How do you get over voltage of output 90v to 150v is that ok??

  • @reymartmanablug2965
    @reymartmanablug2965 4 ปีที่แล้ว

    Very informative video sir.

  • @roderickmagpantay6039
    @roderickmagpantay6039 4 ปีที่แล้ว

    Hi Can you discuss also AVR AS480 connection. thank you

  • @kuyaerapshoo1256
    @kuyaerapshoo1256 3 ปีที่แล้ว +1

    Still compatible sx460 same as sx440 avr even 415volt. Am I correct Sir?

  • @rutchelgimeo1306
    @rutchelgimeo1306 4 ปีที่แล้ว

    Sir ask lng ako kasi ung gen set namin I convert nmun sa manual need talaga palit an ang avr kasi digital ung original nya

  • @Musliperanto
    @Musliperanto 2 หลายเดือนก่อน

    What is the notmal output sir of the avr without load connected?

    • @shuttlemarineengineering
      @shuttlemarineengineering  2 หลายเดือนก่อน

      Voltage output of AVR without load has different values based on brand and capacity. Some has only 6vdc & some has 15vdc @no load. Whats important to consider is that the Voltage output is proportional to the loading conditions. I hope this answers your question. Thanks

  • @АлексейЛевченков-д4к
    @АлексейЛевченков-д4к 3 ปีที่แล้ว

    i need an instrution manual for avr taiyo exu-61a .please if you have it send a link.

  • @glennjayranjo5554
    @glennjayranjo5554 3 ปีที่แล้ว

    Sir my dianamo alternator 5kva pano daigram nga pagkabit ng AVR ata anong brand.... Salamat

  • @denboymechanic
    @denboymechanic ปีที่แล้ว

    I have 375kva nta855-g1 genset for poultry use. .the problema low herts low l-l low l-n kw low and shot down engine. .what is the problem sir can u advice me what is the probs of my genset 365kva

    • @shuttlemarineengineering
      @shuttlemarineengineering  ปีที่แล้ว

      It really depends on the engine shutdown protection naka install sa system. But based sa info mo sir, low Hz means mabagal andar ng prime mover kya low L-L and L-N din yan definitely. Check na lang ano issue sa governor, fuel lines or other mechanical parts that is causing the RPM nd ema meet rated. If its 4poles yan 1800rpm Im assuming 4 poles windings. Thanks

  • @rodeldurban4534
    @rodeldurban4534 4 ปีที่แล้ว

    Sir very informative.. May narinig ako voltage droop san po makikita yan? Sa avr din po ba?

    • @shuttlemarineengineering
      @shuttlemarineengineering  3 ปีที่แล้ว +1

      Yes sir droop adjustment is located in AVR. Manufacturer has their own description on droop...you might see it as P/F, derating, AMP, PAR or sometimes even as a simple S. i hope makatulong sa iyo yang infos nyan sir. Thanks

  • @gaminglover9652
    @gaminglover9652 4 ปีที่แล้ว

    Hello po pwede po pa discuss as440, nag under voltage po kasi ang genset tapos bigla namamatay possble po ba na sa avr ang problem..thanks po

  • @JonielBantan-g9h
    @JonielBantan-g9h 15 วันที่ผ่านมา

    Sir good evening.. ask lng Po f pano malaman Ang pin input 220vng generator 12kva 4pins palitan ko Sana Ng AVR sx460 salamat po sana mapansin

    • @shuttlemarineengineering
      @shuttlemarineengineering  15 วันที่ผ่านมา

      @@JonielBantan-g9h good pm sir, terminal 7-8 input terminals. Tnx

  • @becongcabahug7016
    @becongcabahug7016 3 ปีที่แล้ว

    Sir, need to reply to make more participant perhaps.

  • @josec.eleccion9349
    @josec.eleccion9349 3 ปีที่แล้ว

    Good day engr. Anong schematic diagram ng ATS Pag connect sa generator. Salamat.

  • @reynariob.ermino5368
    @reynariob.ermino5368 3 ปีที่แล้ว

    Yng. Training. Nyo. Sír. Ay. Tangap. Ng. Marina. Para. Sa. ETO. Salamat. Sir...

  • @melalbano6351
    @melalbano6351 3 ปีที่แล้ว

    Sir how about Generator control modules?

  • @jovsd.i.yprojects
    @jovsd.i.yprojects 3 ปีที่แล้ว

    Sir pwede va yan sa ref

  • @justiceekong6116
    @justiceekong6116 11 หลายเดือนก่อน

    How can I convert maccalte AVR to work with Stamford AVR

    • @shuttlemarineengineering
      @shuttlemarineengineering  11 หลายเดือนก่อน

      What is the alternator output V rating and check nameplate what is the excitation V. From there it can easily be determined what brand and type of AVR can be used. Thanks

  • @ruelbajar8805
    @ruelbajar8805 3 ปีที่แล้ว

    good day sir ask q lng po Sana alarm ng genset perkins 500kva
    BOC L1L3

  • @franciscorabano8025
    @franciscorabano8025 ปีที่แล้ว

    Pwedi po ba yong dalawang generator na hindi pareho ang rated power?

    • @shuttlemarineengineering
      @shuttlemarineengineering  ปีที่แล้ว

      Pwede yan sir aslong as not too huge capacity difference, important to note na they should have the same hz and exactly the same V at whatever loading %. Thanks

  • @borjokworkz6273
    @borjokworkz6273 2 ปีที่แล้ว

    Sir good day may generator po akong kinabitan ng AVR. GB170 po yung avr para po sa STC na mindong dynamo po. Ang problem po hindi po naaadjust yung voltage nya sa avr. Yung connection ko sa UVW ok naman po. Dun sa Dalawang Z po sinunod ko naman yung diagram base dun sa manual. Ano po kaya problem sir.? Thanks po

    • @shuttlemarineengineering
      @shuttlemarineengineering  2 ปีที่แล้ว

      Good day sir, yung mindong genset kasi basically brush type and walang exciter field and exciter rotor. Yung output ng stator na U-V-W dun din kukuha ng voltage input yun GB170 na avr, make sure tama yan, yun naman feed sa main field dadaan lang sa trio bridge diodes pra yung 3phase AC from a separate coil group ng stator papunta na main field maging DC volts, pero yung 1 line from stator daan muna sa avr terminals labels Z - Z pra ma regulate yun DC na feed sa main field. Kung maka download ka ng PDF ng manual then balikan mo itong explanation na ito mas maintindihan mo yan. I hope makatulong sa iyo sir. Stay safe

  • @raghavendragajapathy6476
    @raghavendragajapathy6476 4 ปีที่แล้ว

    Yes we can use.. Your videos are good.. Kindly share me some more videos about AVR .. Also i have seen few transformers inside alternators.. Please explain about that

    • @theoryofeverything9439
      @theoryofeverything9439 4 ปีที่แล้ว

      Only by using a step down transfer because as you see input voltage limit is 264 vAC and Alternator output (input for AVR) is 415 v. All other specifications are satisfactory like Excitation field resistance is above 15 (25 ohm in this case) and AVR output 75 vDC

    • @Adarsh19893
      @Adarsh19893 4 ปีที่แล้ว

      @@theoryofeverything9439 no need transformer.. Input voltage for avr coming from mid taped alternator terminals

    • @aiahamadumbayo1666
      @aiahamadumbayo1666 3 ปีที่แล้ว

      Is this avr 3 face

  • @dharmeshdj5869
    @dharmeshdj5869 4 ปีที่แล้ว

    Make vedio on sensor wiring to interfacing board on Disel generater

  • @renechavez8275
    @renechavez8275 4 ปีที่แล้ว

    Pang 312 kva na AVR, ang model engine NTA 855

  • @addiszemen1637
    @addiszemen1637 7 หลายเดือนก่อน

    Thank you so much

  • @ianmichaelluaton9243
    @ianmichaelluaton9243 3 ปีที่แล้ว

    What if sir there is no residual magnetism so it means the avr will not work? And how to restore the magnetism? Thanks

    • @shuttlemarineengineering
      @shuttlemarineengineering  3 ปีที่แล้ว

      No it wont if the residual voltage is not suitable for the AVR triggering V, restoring by field flushing. thanks

  • @richardparacuelles3612
    @richardparacuelles3612 2 ปีที่แล้ว

    sir magandang araw po,, naka encounter ako sa generator namin ,na sira kasi yung voltage adjuster kasi sinusunog niya yung parang transformer ,,,ngayun wala na akong ibnag paraan oara mag adjust dun lang talaga sa avr mismo ,,,anu pong nang yari jan sir?

  • @modestovillocillo4844
    @modestovillocillo4844 3 ปีที่แล้ว

    May board sa avr ba na para sa delta connection para sa 75kva na avr?

  • @willymerlan4548
    @willymerlan4548 3 ปีที่แล้ว

    Sir meron po ako nyan baka po bibili kayo ..?

  • @theoryofeverything9439
    @theoryofeverything9439 4 ปีที่แล้ว

    Yes we can use but Only by using a step down transfer because as you see input voltage limit is 264 vAC and Alternator output (input for AVR) is 415 v. All other specifications are satisfactory like Excitation field resistance is above 15 (25 ohm in this case) and AVR output 75 vDC.

  • @Fakir-ck4nh
    @Fakir-ck4nh 4 ปีที่แล้ว

    CATERPILLAR AVR PRICE PLEASE?

  • @maribelmendoza5523
    @maribelmendoza5523 3 ปีที่แล้ว

    sir pwede ba gamitin ung avr sa generator pra sa submersible water pump.tnx

    • @shuttlemarineengineering
      @shuttlemarineengineering  3 ปีที่แล้ว

      As long as mag match yun input at excitation voltage/current ng avr and alternator

    • @maribelmendoza5523
      @maribelmendoza5523 3 ปีที่แล้ว

      @@shuttlemarineengineering mga ilang watts kelangan na avr sir

    • @maribelmendoza5523
      @maribelmendoza5523 3 ปีที่แล้ว

      irerekta na sa generator ung sir ok lng ba

  • @andreyaparecidosilva1374
    @andreyaparecidosilva1374 4 ปีที่แล้ว +1

    Presiso de legenda português excelente video

    • @andreyaparecidosilva1374
      @andreyaparecidosilva1374 ปีที่แล้ว

      Hoje eu consigo entender inglês ,💪💪💪💪💪quem diria ,,🫡🫡🫡🫡

  • @louiegalpo5413
    @louiegalpo5413 3 ปีที่แล้ว

    boss pa order nman po need ko sa 3kva generator k0

  • @theoryofeverything9439
    @theoryofeverything9439 4 ปีที่แล้ว

    Without transformer its impossible to use the AVR on this alternator

  • @becongcabahug7016
    @becongcabahug7016 3 ปีที่แล้ว

    Boss paano e connect ang AVR sa three phase 220v generator? salamat

    • @shuttlemarineengineering
      @shuttlemarineengineering  3 ปีที่แล้ว +1

      Ano brand and model ng AVR mo sir, if 220V rated Voltage ng genset mo then madali lang kasi most of AVR naman has 180-260V input kya directly connected na sa any of the 2 lines.

    • @becongcabahug7016
      @becongcabahug7016 3 ปีที่แล้ว

      @@shuttlemarineengineering i have a GAVR20A po.

    • @shuttlemarineengineering
      @shuttlemarineengineering  3 ปีที่แล้ว

      Ok yan, madami na tyo nakabit na GAVR pero 15 nde 20, magandang AVR yan, pra nga syang universal kasi mataas excitation current kya pde yan sa ibat ibang brands.

    • @becongcabahug7016
      @becongcabahug7016 3 ปีที่แล้ว

      @@shuttlemarineengineering OK po sir, maraming salamat

  • @protaciojrescarilla6199
    @protaciojrescarilla6199 ปีที่แล้ว

    sir pwd ba makahingi ng contact no. mo, nag hahanap kz kmi ng mag bgay samin ng training

    • @shuttlemarineengineering
      @shuttlemarineengineering  ปีที่แล้ว

      Kindly email us at perl.shuttlemarine@gmail.com and we’ll coordinate with you accordingly. thanks

  • @dawitarega7677
    @dawitarega7677 9 วันที่ผ่านมา

    Yes comateble

  • @becongcabahug7016
    @becongcabahug7016 3 ปีที่แล้ว

    incompatible po Sir

    • @shuttlemarineengineering
      @shuttlemarineengineering  3 ปีที่แล้ว +1

      Compatible yan sir, youll be guided sa mga ibang parts ng vlogs natin for proper connection. Thanks

    • @becongcabahug7016
      @becongcabahug7016 3 ปีที่แล้ว

      Salamat po sir.