    @lesterwatson8519 11 หลายเดือนก่อน +3

    A fuse is much more reliable than a breaker in my 50 + years as an electrician I have never seen a breaker trip before a fuse blew when the circuit was protected by both a fuse and a breaker. A breaker is just more convenient to reset. I have actually seen circuits protected by a 15 amp breaker and a 20 amp fuse and the fuse blow first.

    • @NorthwestCraftsman
      @NorthwestCraftsman  11 หลายเดือนก่อน +3

      Fascinating, I’d be curious what the lead evidence was to move to breakers instead. I’m assuming there was more than the convenience factor

    • @mandelstamm
      @mandelstamm 6 หลายเดือนก่อน +1

      Fuses are still used in commercial applications. There's different types of fuses that are designed to be fast trip, medium trip, and then time delay. For residential applications in most cases time delay is the way to go. Breakers do a great job for time delay. So, they became the norm. Fuse panels can be dangerous due to the ease of changing out fuses for higher amperages to avoid tripping. That's why breakers became the safe norm. Again, in commercial applications fuses are still used. Also, you'll find fusable disconnects at residential outdoor ac units.

  • @KindCountsDeb3773
    @KindCountsDeb3773 2 ปีที่แล้ว +3

    THIS is why an ignorant person like me would have to call an electrician. Safest for me. Thanks, I needed the name of the larger fuses.

    • @NorthwestCraftsman
      @NorthwestCraftsman  2 ปีที่แล้ว

      Absolutely! For anyone that is not comfortable and familiar with this type of work, I always recommend hiring an electrician

    • @KindCountsDeb3773
      @KindCountsDeb3773 2 ปีที่แล้ว

      @@NorthwestCraftsman Yes, You are right. I'm sure a LOT of people use your explanation/help to do their own.

  • @Progrocker70
    @Progrocker70 2 ปีที่แล้ว +3

    I was going to say you could use the power tap lugs directly under fuses 1 and 2 which comes directly from the main 60 amp fuses. Get a small 30 amp two space subpanel and mount it next to this panel. Connect it to these tap lugs, and install your two pole 20 amp breaker in the sub. If you ever have to cut power to the welder from the fuses, be very careful when you unscrew them, because on the first fuse you unscrew there will be voltage present on the metal screw shell of the fuse as you are removing it.

    • @NorthwestCraftsman
      @NorthwestCraftsman  2 ปีที่แล้ว +1

      I hadn’t thought about that but what a great idea! Thanks for the explanation, and warnings, I’ll check into that!

    • @Progrocker70
      @Progrocker70 2 ปีที่แล้ว +1

      @@NorthwestCraftsman The two space sub and double pole breaker are cheap. This also provides an easy and safe disconnect with the breaker when you need to cut power.
      With fuses on 110 v circuits, unscrewing a fuse is perfectly safe, once you back out the fuse the exposed metal threads on the fuse are dead and you won't get a shock if your fingers were to touch them. However when you're using two fuses to get 220 volt this isn't the case. If you go unscrew one of the fuses, power will be present in that fuse's screw shell, you don't want to touch this shell as you are unscrewing it or you could get a shock. Only safe way to disconnect power is to unscrew both at the same time so you're breaking connection to both fuses. This is the reason 220 v fused circuits use pullouts to remove both fuses simultaneously, or a safety switch with plug fuses that kills power to both fuses at the same time so you can safely remove or install them.

    • @NorthwestCraftsman
      @NorthwestCraftsman  2 ปีที่แล้ว

      Interesting! Again, great info. Thank you!

  • @Sparky-ww5re
    @Sparky-ww5re ปีที่แล้ว +2

    The bus bar taps under fuses 1 and 2 are sometimes referred to as water heater taps. From there you could add a subpanel, but if you're adding a subpanel for the purposes of adding a bunch of new circuits 60 amp service really isn't enough power. In that instance it would be a good idea to begin budgeting for a service upgrade very soon, 200 amps seems to be the standard now, 100 amps is the smallest service allowed on a single family dwelling and may be plenty of power if the range, water heater and furnace are gas rather than electric, and central AC is not included. I personally prefer 200 amp services because the cost difference between 100, 150 and 200 isn't really significant, and it's not very cost effective to cheap out and go with 100, only to find out 10 or 15 years down the road you need at least 200 because you wanted to add a fancy induction range and central AC.

    • @NorthwestCraftsman
      @NorthwestCraftsman  ปีที่แล้ว

      Thanks for that added knowledge on the bus bar taps!
      I totally agree with you, ideally this would be its own 200A service. We’re renting currently so I’m not planning to touch it since it works for me as is. However, when we have a place of our own, a 200A panel in the shop will be a must.

  • @gretchenbonk9848
    @gretchenbonk9848 9 หลายเดือนก่อน

    Thank you so much!!! It’s exactly what is in the wall.

    • @NorthwestCraftsman
      @NorthwestCraftsman  9 หลายเดือนก่อน +1

      So glad I could help! I had such a hard time finding my info. Just be sure to know which bus bars run to which fuses. They change per panel design.

  • @dhelton40
    @dhelton40 2 หลายเดือนก่อน +1

    If the weather head and meter use this same cloth covered cable outdoors, chances are they are rotten and because they are not fused until they get to this little 60 amp box they pose a serious fire hazard. In all likelihood it is only twenty coats of paint holding it together. If you value your building, replace it and certainly do not heat it up by trying to run a welding machine.

    • @NorthwestCraftsman
      @NorthwestCraftsman  2 หลายเดือนก่อน +1

      I’d have to go back and check but we don’t live there anymore. I appreciate you pointing this out though.

  • @clydejr6065
    @clydejr6065 ปีที่แล้ว +1

    Hey were can I buy a fuse box like that .

    • @NorthwestCraftsman
      @NorthwestCraftsman  ปีที่แล้ว +2

      Probably can’t anymore, they’re quite outdated and shouldn’t be used. I’d recommend a small breaker panel that matches your needs. They’re cheap and much safer.

  • @maryandtrooper
    @maryandtrooper ปีที่แล้ว +1

    Meant for those with more than a passing knowledge of fuse boxes, and I've gotten that from other videos. Lost me.

    • @NorthwestCraftsman
      @NorthwestCraftsman  ปีที่แล้ว

      Shoot! I'm sorry to hear that! That wasn't my goal. Can I help answer any of the questions you still have?

  • @xrux-xs8ev
    @xrux-xs8ev 8 หลายเดือนก่อน

    Is there any way you can help me with my fuse box i was using a air compressor and the eletricity went off and i pull the squere thatvis in the braker an put it back on and now just half of the house has electricity

    • @NorthwestCraftsman
      @NorthwestCraftsman  8 หลายเดือนก่อน

      Hey! Caveat that I’m not an electrician but I’ll give it my best shot. The black box that you pulled, does it have two, tube like fuses in it? It sounds like one of them popped so one of your busses isn’t getting any power. You should also be able to test this with a voltmeter by removing one of the small fuses on a working circuit and one that isn’t working. Measure both with reference to ground. I suspect the dead bus will read zero. If so, and perhaps even before whipping out your voltmeter, pull the black box and look for signs that one of them popped. You should see some charring inside or an indicator that popped. If you do see that or it reads zero with the voltmeter, you should be able to take it to your local hardware store and get a replacement fuse. Make sure to get the exact same size, dimensions, and current rating. They come in slightly different sizes and shapes but you should be able to find it.
      I would also be remised if I didn’t recommend replacing your fuse box with a breaker box. It’s not that expensive and is miles safer and easier to work on. Case in point here, if you blew a fuse you need to replace it, breakers you’d flip back on.
      Also not to go on and on but you may check what your loading on that bus is and ensure your fuse sizes on your circuits match the wire coming out of the box. If your air compressor tripped the main fuse, it means your bus was overloaded even though the individual circuit was not. That’s what the fuse is for but it’s generally to be avoided or means your fuse is oversized for your circuit which is more dangerous.
      If you’re at all uncomfortable with those descriptions, call an electrician and they’ll be able to quickly sort you out and make sure things are safe (though they will surely recommend or require a panel upgrade).
      Sorry for the long winded response! Hope this helps!

    • @xrux-xs8ev
      @xrux-xs8ev 8 หลายเดือนก่อน

      @@NorthwestCraftsman thanks so much i will check tomorrow because i try to replace one of the fuses the 30 green one but didn't work so i needed the light on my bathroom so i conect my light to the kitchen switch but i not sure if that is safe to do i mean works fine im just not gonna connect my compressor again

    • @NorthwestCraftsman
      @NorthwestCraftsman  8 หลายเดือนก่อน +1

      Yea, if you could have an electrician look at your panel, that’d probably be your best bet to both ensure you have the right size of fuse and that everything is wired correctly.

  • @johnolson7430
    @johnolson7430 ปีที่แล้ว

    Just change the panel ! What scares people from doing this? Hire someone who knows what they are doing and get it done. Alot cheaper than losing your home

    • @NorthwestCraftsman
      @NorthwestCraftsman  ปีที่แล้ว

      Hey John! I don’t disagree one bit. I’m renting this place right now and plan to move soon so it’s not worth changing myself. However, in the whole, I agree, it’s not a hard or expensive swap long term.

  • @mernokimuvek
    @mernokimuvek ปีที่แล้ว +1

    Its impossible to install a 220V line in your shop. You can get 120, 208 or 240 Volts, never ever 220. 110 and 220 V doesnt exist since the 1930s, 115 and 230 V was standardized. And later 120 and 240 V.

    • @NorthwestCraftsman
      @NorthwestCraftsman  ปีที่แล้ว +1

      You’re totally right. I can’t remember where I had heard 220 in place of 240 early in my life but it stuck.

  • @richsparkman9980
    @richsparkman9980 2 ปีที่แล้ว

    I think you would have much better off just changing out the fuse box out to a circuit box they are not that expensive and would be better for any future updates

    • @NorthwestCraftsman
      @NorthwestCraftsman  2 ปีที่แล้ว +1

      Totally agree it’s better for any future updates. I didn’t upgrade because I don’t expect to be in this shop for more than a few years and I’m renting the space.

    • @KindCountsDeb3773
      @KindCountsDeb3773 2 ปีที่แล้ว +3

      I've read to HIRE someone to do that, it IS expensive. DIY is a different story.

    • @richsparkman9980
      @richsparkman9980 2 ปีที่แล้ว

      Not that hard to do. If you can turn off the power and can use a screwdriver you can do it.

    • @LH-kz2nf
      @LH-kz2nf 2 ปีที่แล้ว +1

      The breaker box itself isn't that expensive but if the house is wired with two receptacles wouldn't you be required to rewire the house?
      I'm no electrician by any means and this is the situation I'm in. I know the only way I can install a 3 prong outlet now is to replace the two prong receptacle with a 3 prong GFCI receptacle and the lable included has to be place on the outside of the receptacle warning that it's not grounded

  • @chuethao385
    @chuethao385 10 หลายเดือนก่อน

    Keep cheaping out one day you'll regret

    • @NorthwestCraftsman
      @NorthwestCraftsman  10 หลายเดือนก่อน +4

      Out of curiosity, what am I cheaping out on?

    • @nudenoodl3
      @nudenoodl3 6 หลายเดือนก่อน +1

      Fuse boxes do not magically burst into flames, you just have to maintain them a bit more than breakers. In good working order, they are perfectly safe.
      Also, do you forget that a lot of people rent and dont have the option to change things like this entirely? Whats better, living with a fuse box that you have to maintain a little bit or being completely homeless?

    • @Showbyshowclips
      @Showbyshowclips หลายเดือนก่อน

      @@nudenoodl3exactly bro this is my situation right now but i know god has blessed me with a home and i am more then grateful i will ride it out until I physically cannot no more , these comments be giving me some hope yo im not the only one going through this