  • What is Zs, what is it made up of. We look at the different parts of a circuit, Ze, R1 and R2 to understand what is involved in the testing. How much current can flow, what is a fatal electric shock and how does a correctly wired electrical system prevent this. Understand the difference between an impedance and a resistance, understand why a disconnection time is specified. A short and to the point video that will help you to understand this fundamental test for safety.
    To view all our videos, click on the following link
    / @learnelectrics4402

ความคิดเห็น • 117

  • @learnelectrics4402
    @learnelectrics4402  3 ปีที่แล้ว +4

    SEE ALL - To view a list of all our LearnElectrics videos, click on the link below.
    There are many videos on many electrical topics including Installation, Part P, 18th Edition, Testing, Certification, Lighting, Sockets, Ring Circuits and much more.
    th-cam.com/channels/YaJQnpO4XAp0yCgqzMkmfA.html

  • @rri7534
    @rri7534 3 ปีที่แล้ว +21

    The most understandable explanation of zs I have come across, Thank you for your time & effort in making this available, will help me loads towards passing the 18th Edition exam, God bless you 🙏🏽👍🏻👏🏻👏🏻👏🏻👏🏻

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว +1

      Thank you so much for the great feedback. Lots more to come, including tips on the 18th Edition Exams and using the Regs book. Spread the word, the more that know about our channel, the more videos we can make. Dave.

  • @multirole240
    @multirole240 3 ปีที่แล้ว +5

    Thank you for an excellent straight forward understandable presentation, well spoken at a sensible pace.

  • @lcutz9854
    @lcutz9854 3 ปีที่แล้ว +1

    What an excellent video! Best explanation so far I’ve seen on TH-cam 👍

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      Thank you for the positive comment. We try our best and comments like this make it all worth while.
      Bux

  • @tomb3175
    @tomb3175 2 ปีที่แล้ว

    I agree with others. This is the best straightforward explaination on TH-cam.

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว

      So glad you found it useful, really appreciated. Dave.

  • @rezamaddah2010
    @rezamaddah2010 3 ปีที่แล้ว

    Just I want to say all about electrical describ are complete and clear and I learn to get many information that I didn't know.God bless you.thanks.

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      Thank yo Reza, very kind words. Lots of videos to watch and lots more to come. Dave.

  • @Michael-xk9ft
    @Michael-xk9ft 3 ปีที่แล้ว +2

    Thanks you, a nice useful recap. I hope more like this will be coming. Cheers

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว +2

      Thank you for your comments. We try to use our experiences of all the questions we are asked over the years. Certainly there will be more to follow. Every Monday we upload a new video. Thanks again, Dave.

  • @chrischaralambous286
    @chrischaralambous286 2 ปีที่แล้ว

    Thank you for this crystal clear explanation. This video has been very helpful. I have watched a couple of other videos from Learn Electrics and would just like to thank you for explaining things so clearly and making it so much easier to understand.👍

  • @hussmortada
    @hussmortada ปีที่แล้ว

    Thank you very much, a clear and easy to follow explanation. I always benefit from your videos and enjoy watching them. Thank you again

    • @learnelectrics4402
      @learnelectrics4402  ปีที่แล้ว

      Thanks Hussein, and thanks for supporting the channel.

  • @Andrew-hu9ke
    @Andrew-hu9ke 2 ปีที่แล้ว

    Excellent as always, Thank you 👍😎

  • @rizgar8121
    @rizgar8121 8 หลายเดือนก่อน +1

    Thank you Dear, for all this understandable lessons.

    • @learnelectrics4402
      @learnelectrics4402  8 หลายเดือนก่อน

      Glad it was helpful and thank you for watching. Appreciated. Dave.

  • @alvarob2443
    @alvarob2443 2 ปีที่แล้ว

    Love this videos, specially now that i started doing testing

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว

      That's good, glad you are finding them useful. Lots more to follow. Dave.

  • @alikhalfa4932
    @alikhalfa4932 4 หลายเดือนก่อน

    Thanks a lot for a clear and fully understandable method of teaching , i spent 3 years in college couldn't understand properly the principle of ZS till now .

  • @pinchermartyn3959
    @pinchermartyn3959 2 ปีที่แล้ว

    Just excellent. Thank you.

  • @MobiletentedcampsZa
    @MobiletentedcampsZa 2 ปีที่แล้ว

    Brilliant as usual.

  • @cobydavies5304
    @cobydavies5304 3 ปีที่แล้ว +4

    This was quality thank you

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว +1

      Thankyou for your comment. Glad you liked it, we try our best.

  • @trebushett2079
    @trebushett2079 2 ปีที่แล้ว

    Excellent and informtive channel.

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว

      Much appreciated Tre. Thanks for watching. Dave.

  • @paulward143
    @paulward143 ปีที่แล้ว

    Brilliant very clear.

    • @learnelectrics4402
      @learnelectrics4402  ปีที่แล้ว

      Thank you Paul, appreciated comments and thanks for watching. Dave.

  • @alig7800
    @alig7800 3 ปีที่แล้ว

    THANK YOU
    MADE IT EASY TO UNDERSTAND

  • @danielteyehuago1633
    @danielteyehuago1633 ปีที่แล้ว

    Wow! This is very informative, thanks for sharing it with us. It worth it and the best tutorial on the topic for me...dl

  • @2207amin
    @2207amin 2 หลายเดือนก่อน

    I like ur simplicity in ur answers. Its v good when u start from basics. Thanks 🎉🎉🎉❤❤❤

    • @learnelectrics4402
      @learnelectrics4402  หลายเดือนก่อน

      Thank you so much, great comments, appreciated.

  • @Ibrehas
    @Ibrehas 10 หลายเดือนก่อน

    simple and precise
    just wanted to know what you would set your multimeter to when measuring the ZE and R1 + R2

    • @learnelectrics4402
      @learnelectrics4402  10 หลายเดือนก่อน

      You can use a multimeter for R1+R2 but you will need a multifunction tester for Ze and Zs. Hope this helps. Dave.

  • @dascarcatumbela4084
    @dascarcatumbela4084 2 ปีที่แล้ว

    thanks for good lesson

  • @slapman7646
    @slapman7646 2 ปีที่แล้ว

    Thank you.

  • @IFICANDOITYOUCANDOIT1979
    @IFICANDOITYOUCANDOIT1979 3 ปีที่แล้ว

    BIG THANK YOU

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      Great feedback and much appreciated. Thank you. Dave.

  • @atifmughal1905
    @atifmughal1905 หลายเดือนก่อน

    Hi Dave,
    Thank you for the great content as always. Amazing work and information provided. I wanted to ask a question, why would the RCD trip when ZS testing and I get no reading.
    Please if you could have an idea of what this could be?
    Thanks

    • @learnelectrics4402
      @learnelectrics4402  หลายเดือนก่อน

      If you have your test meter set to the normal Zs test this will happen. Set your test meter to the NO-TRIP setting and it should clear this. Different meters mark the no trip test differently so check the user instructions with the meter or go online to the manufacturers website.
      Take a look at the video on this link, its an old one of ours, but it will help.
      th-cam.com/video/n1XSSSs5ILo/w-d-xo.html

    • @atifmughal1905
      @atifmughal1905 หลายเดือนก่อน

      @@learnelectrics4402 thank you for your reply and your time. This property is the only one that gives me a problem - testing other properties with the same tester I’ve never had this issue. The setting is always set the same way but it only seems to be happening at this property.
      Just abit baffled as to why this is happening here. The tester is Megger MFT1721
      Thanks

  • @mdmvukengineer4873
    @mdmvukengineer4873 หลายเดือนก่อน

    Excellent 👍

  • @shahzadhameed3741
    @shahzadhameed3741 3 ปีที่แล้ว +1

    Excellent

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      Thank you for the positive comment. Appreciated. Dave

  • @ranat5526
    @ranat5526 3 ปีที่แล้ว

    Thank You.

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      Thanks for the comment, glad you liked it. Lots more to come. Bux

  • @hakeem2006
    @hakeem2006 3 ปีที่แล้ว +1

    Excellent presentation.
    Please can you explain how do we achieve the 100amp fault current to flow to trigger the MCB to trip @ 0.4 second!
    Knowing appliances don’t required that much amperes to start or run on full load.
    Forgive my ignorance if have asked an obvious question!
    Regards

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว +2

      It is the earth fault path having a low resistance that allows a large fault current to flow. The fault path is Line and Earth, not Line and Neutral
      Its all to do with Ohms Law, if the earth fault path is low enough then the current will be high. Some of our other videos will help you to understand this better, especially our video on Ohms law.

  • @daviddmf
    @daviddmf 6 หลายเดือนก่อน

    Thank you for this. What causes the faulty circuits mcbs to trip rather than the other mcbs in the CU? The incoming supplys Line and Neutral are two incoming supply conductors. If there is a fault a surge of current will loop round from the consumer to the transformer and back round to the consumers CU. How does a single MCB know when to trigger when all the MCBs in the CU are also exposed to the fault current surge coming in from the Supply?

    • @learnelectrics4402
      @learnelectrics4402  6 หลายเดือนก่อน

      Because the fault current has to pass through the mcb of the faulty circuit. It doesn't matter what is happening on just one side of the fuse or breaker.
      Watch this video, it will tell all.
      th-cam.com/video/FZ6-okbgXKo/w-d-xo.html

  • @user-in6lf9jk3d
    @user-in6lf9jk3d 11 หลายเดือนก่อน

    tank you for the nalelge that you give as.

    • @learnelectrics4402
      @learnelectrics4402  11 หลายเดือนก่อน

      Glad that you find it useful. Lots more to come. Dave.

  • @crazyivan52
    @crazyivan52 2 ปีที่แล้ว +1

    I have a question. In a phase - neutral short circuit fault with no grounding what is the fault loop? From the neutral to the trasformer or to the electrical meter?

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว

      It's the whole loop through the transformer and back. Have another look at the video. Thanks for watching. Dave.

  • @ciaranhughes8705
    @ciaranhughes8705 2 ปีที่แล้ว +1

    Great video. Just a quick question. My fluke requires me to have all 3 testing cables connected to undertake a Zs test. If it's only testing through line and earth why is the neutral required to complete the test.
    Sorry if this sounds daft but just interested after watching your explanation.

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว +2

      Not daft at all. The meter tests between phase and Earth but it also needs a neutral connection to make the meter work, for example, just like a kettle needs the neutral connected. Some modern two lead meters actually make an internal link between N and E and on some you can hear the relay pull in if the room is quiet. Hope this helps.

  • @faisalahmad4232
    @faisalahmad4232 ปีที่แล้ว

    Will the reading be effective if i use a temporary generator connected to the earth rods during testing and commissioning instead of the transformer ?

    • @learnelectrics4402
      @learnelectrics4402  ปีที่แล้ว

      If the installation is to run on the national grid, you really need to test it when connected to the grid. Your generator will give different readings. You can test R1+R2 as a dead test and add to an assumed ZE (0.35 ohms for TNCS). When the DNO connects up, the Ze will usually be less than 0.35 so your Zs figures will be acceptable.
      Hope this helps. Dave.

  • @jmphotography205
    @jmphotography205 3 ปีที่แล้ว

    as dyslexic , can i ask you to add subtitles to your videos ,will make me understand you better thanks .love you work cheers

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      Joanna, that is something that could be considered in the future. Thanks for getting in touch and good luck with the learning. Dave.

  • @matthewdaniel1715
    @matthewdaniel1715 ปีที่แล้ว

    A masterpiece

  • @westwonic
    @westwonic 2 ปีที่แล้ว

    Great explanation, but I have one question;
    If the lowest resistance possible is required for the earth conductor ( to achieve higher fault current), why is the cross sectional area of the earth conductor in 2c+e cable smaller than the line or neutral conductors?

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว

      Good question Nick. It's all to do with the Adiabatic Equation and the time for the fuse or breaker to trip. We can put any bigger size earth in we want but if its not going to overheat before the fuse blows then why waste copper (and money).
      Have a look at this video, it explains it all. Dave.
      18th EDITION - SESSION 4 - ADIABATIC EQUATIONS, click on the link below
      th-cam.com/video/173C7yE-xbU/w-d-xo.html

  • @yanalnaghawai1872
    @yanalnaghawai1872 9 หลายเดือนก่อน

    Hello Dave, please be patient with me, A 20A breaker needs 100 amps to flow .. etc, i can't understand from where the 100 amps will come, can you please explain to me or tell me which video i must see to understand this

    • @learnelectrics4402
      @learnelectrics4402  9 หลายเดือนก่อน

      Have a look at the two videos on the links below, they will hopefully answer your questions and help you become expert. Remember that we are interested in two different currents in a 20A fuse or breaker. The 20 amps working current, day in day out; and the 100 amps fault current that causes almost instant tripping to keep people safe, Enjoy and keep learning. Dave
      More magic numbers
      th-cam.com/video/l0y8gtfUj_k/w-d-xo.html
      Why my fuse blows
      th-cam.com/video/FZ6-okbgXKo/w-d-xo.html

  • @user-fx8dy2fw5y
    @user-fx8dy2fw5y 2 ปีที่แล้ว

    Great content. Why is the loop impedance value not the same in Table B6 the onsite guide to BS 7671 table 41.3. B type mcb 20 amp. I know in BS 7671 there is a factor of 0.8 and in your video you mention the value must be below 1.75 ohm. the value in BS7671 says 2.19 ohms. I hope this makes Sense.

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว +2

      Good question. That is the 80% rule. take a look at our video ZS and the 80% Rule on this link.
      th-cam.com/video/ihD-NO-7G5Y/w-d-xo.html
      Thanks for watching. Dave.

  • @kaybhee6
    @kaybhee6 ปีที่แล้ว

    keen

  • @TheNathan696969
    @TheNathan696969 8 หลายเดือนก่อน

    As a Mechanical engineer that has just progressed into commissioning and consultancy, your video has been very informative and totally understandable! however, I have a question, could an on site guide values deviate from a standard Zs table and if so why?

    • @learnelectrics4402
      @learnelectrics4402  8 หลายเดือนก่อน +1

      Have a look at these 3 videos, less than an hour in total. They will really boost your understanding. The OSG uses 80% values based on the 100% values in the tables in the Regulations book. An, there are some typos in the OSG tables, highlighted in the videos. Thanks for watching. Dave.
      th-cam.com/video/QWr-ilqW67A/w-d-xo.html
      th-cam.com/video/fkSUrz0HaPE/w-d-xo.html
      th-cam.com/video/nVZeIFeEwl0/w-d-xo.html

    • @TheNathan696969
      @TheNathan696969 8 หลายเดือนก่อน

      @@learnelectrics4402 ohh great, thanks a lot :)

  • @zulfakarali6274
    @zulfakarali6274 3 ปีที่แล้ว +1

    Thanks

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      You are very welcome. Glad we can help.

    • @amriabssamad4695
      @amriabssamad4695 3 ปีที่แล้ว

      Thank you for been much clearer in your explanation

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      Happy to help and thank you for the positive comments. lots more to come. Dave

  • @anelectrician
    @anelectrician 2 ปีที่แล้ว

    06:48
    Dave here you're demonstrating a fault at the kettle. Therefore the fuse on the kettle should be the focus and not at the consumer unit.

  • @markpalm672
    @markpalm672 ปีที่แล้ว

    Dear sir, thanks for your great presentations. But in another video , if am not mistaken it was said that for type B we need Zs to be not more than 3.5 Ω and not 1.75 Ω. What is correct?

    • @learnelectrics4402
      @learnelectrics4402  ปีที่แล้ว +1

      Both are correct Mark. A 10A Type B has a max Zs of 3.5 ohms whilst a 20A type B is 1.75 ohms. Hope this helps and thanks for watching. Dave.

    • @markpalm672
      @markpalm672 ปีที่แล้ว

      @@learnelectrics4402 Great Dave! Thanks for your prompt reply.

  • @gd-bq7em
    @gd-bq7em 9 หลายเดือนก่อน

    If the zs on a b32 mcb is 1.10 max on a tn system and the reading was coming back higher, would this circuit require rcd protected to provide fault protection, would it then be acceptable or not,

    • @learnelectrics4402
      @learnelectrics4402  9 หลายเดือนก่อน

      The Regs do permit that under certain circumstances but first look at the options available to bring Zs in line. Have a look at this video on the attached link.
      th-cam.com/video/fUlCDhlcDf4/w-d-xo.html

  • @tommylau7457
    @tommylau7457 2 ปีที่แล้ว

    I want to know how to calculate the time to burn a fuse given the material, temperature, thickness of the fuse, and the current passing through it.
    I tried finding fuses online and very few places have graphs that show the curves (for example generators often have discharge graph with curves)

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว +2

      Tommy, not really something we worry too much about as electricians. We work from a set of approved fuses and breakers and all the calculating of burn time, material etc is done by the manufacturer. You may find the data that you want on a fuse manufacturers website, but then again, they may keep the information secret. Thanks for watching. Dave.

    • @tommylau7457
      @tommylau7457 2 ปีที่แล้ว

      @@learnelectrics4402 i see, so is so many product manufacturers, even for cars, most of the time they base on the previous products rather than doing a whole new set of calculations, probably 95% empirical.

    • @tommylau7457
      @tommylau7457 2 ปีที่แล้ว

      @@learnelectrics4402 or idk if the deviation is too high, the rate of failure is too high, like long HDMI cables, that could also be a reason

  • @ja_adam_
    @ja_adam_ 11 หลายเดือนก่อน

    Hi,
    Need help with this please
    Max Ze for TNCS is 0.35.... What happens when you then have large protective devices for outgoing ways. For example perhaps the consumer unit is more than 3 meters away so you have to use a 100A bs88 fuse.. same for blocks of flats.. this has a max ZS of 0.34.. if the Ze is close to maximum, how on earth are you supposed to get round it?

    • @learnelectrics4402
      @learnelectrics4402  11 หลายเดือนก่อน

      If Ze is close to the maximum, then that is still ok. Also consider what the Zs readings are, they are the important ones.

    • @ja_adam_
      @ja_adam_ 11 หลายเดือนก่อน

      @@learnelectrics4402 that’s what I mean …if I have a 160A BS88 max ZS is 0.34 ….. what if my ZE is 0.34?!

  • @michaelcostello6991
    @michaelcostello6991 2 ปีที่แล้ว

    Why do we not calculate the impedance of the Live/Neutral circuit also ? to ensure breaker trips in time allowed in event of a short etc etc

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว +1

      We do measure it, but its not recorded the same as R1+R2.
      PSCC is your test for shorts.
      Hope this helps.

  • @Wanderers-Bulgaria
    @Wanderers-Bulgaria ปีที่แล้ว

    A question: - if the resistance of a human touching the energized kettle is greater than the Zs, will it receive an electric shock? Perhaps the Zs is more about protecting electric installation and less about human protection 🤔. RCD is the device that is more about direct human electric shock.
    Great video though 👌

    • @learnelectrics4402
      @learnelectrics4402  ปีที่แล้ว

      The human body would form part of a parallel path with the kettle. Thanks for watching. Dave.

    • @Wanderers-Bulgaria
      @Wanderers-Bulgaria ปีที่แล้ว

      @@learnelectrics4402 I am not sure, because the metal frame would have lower resistance than human body, and thus the current would flow through the frame and not the human body. Do you agree?

  • @PhuongLe-bf8ym
    @PhuongLe-bf8ym 2 ปีที่แล้ว

    how did you do it can you share with me , thank you

    • @learnelectrics4402
      @learnelectrics4402  2 ปีที่แล้ว

      It's just repetition and practice. The more you install and test circuits, the more you learn. Good luck. Dave.

  • @jonw2570
    @jonw2570 ปีที่แล้ว

    What happens in a short circuit? If in an earth fault the current flows through the earth and back through the mcb. In a short circuit if it flows through the neutral to neutral bar, how does it go back through the mcb to trip it?
    If it goes back to transformer and then back through to mcb, how come we don’t do a “neutral fault loop” test

    • @learnelectrics4402
      @learnelectrics4402  ปีที่แล้ว +1

      Earth and neutral are effectively the same point back at the transformer. Earth fault is L+E and short circuit is L+N so neutral is covered. Thanks for asking, thanks for watching.

    • @jonw2570
      @jonw2570 ปีที่แล้ว

      @@learnelectrics4402 thanks for the reply! Does that mean in a short circuit the fault current flows down neutral to transformer and back through the L through the MCB causing it to trip… or …. Does the fault current through the L conductor increase due to the fault causing mcb to trip.

  • @dennisfowler7873
    @dennisfowler7873 3 ปีที่แล้ว

    Hi sir... im searching for an answer regarding ZS...wat would cause my measured ZS to be lower than my calculated ZS ... zs = ze + (R1+R2)

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      Measured and calculated are never the same. For a start Ze is a live AC measurement, and R1+R2 are DC dead tests. Different switch settings on your meter and so slight differences. How good are the batteries, how hard are you pressing the probes, what is the temperature in the room. Are there parallel earth paths, is it TT or TN. Lots of things. If they are close don't worry about it.

    • @dennisfowler7873
      @dennisfowler7873 3 ปีที่แล้ว

      @@learnelectrics4402 thanks sir

    • @learnelectrics4402
      @learnelectrics4402  3 ปีที่แล้ว

      Happy to help.