  • There are really only 3 underlining reasons that your circuit breaker keeps tripping - Overloaded circuits, short circuits, and a ground fault.

ความคิดเห็น • 252

  • @derrickwilliams8716
    @derrickwilliams8716 2 ปีที่แล้ว +2

    Thank God for this man. Fixed a ground fault caused by a dumb ol outlet.

  • @westernman7032
    @westernman7032 2 ปีที่แล้ว +23

    This video is exactly what I needed. You saved me a lot of time and money. Thank you!

  • @icreatemyowngoodluck
    @icreatemyowngoodluck ปีที่แล้ว +2

    This video was very helpful. I replaced a breaker but that wasn't the problem. After watching your video I changed the socket where i had an electric chain saw plugged in and everything was fixed. Just like you said , wires were moved because that's where I plug in my electric weed wackers too. Pulling on that socket over the years and it was and old socket .

  • @Steven-rp8zo
    @Steven-rp8zo 3 ปีที่แล้ว +12

    Great info! Straight to the point, love it!

  • @kennethreynolds1532
    @kennethreynolds1532 ปีที่แล้ว +4

    Thank you for not dragging the video out with a bunch of bull an being very informative and informational. I have had this issue for a week now an was not sure what I needed to look for an now I do.

    • @jamescorfield534
      @jamescorfield534 3 หลายเดือนก่อน

      Right!? Keeping it simple in the video is easier for me too

  • @jeffbrett8160
    @jeffbrett8160 11 หลายเดือนก่อน

    Thanks so much Jack, made it very easy to understand.

  • @ej8688
    @ej8688 2 ปีที่แล้ว +3

    Nice! A 4 min video just saved me . Problem solved. Thanks for doing these

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว +1

      Oh man! Glad to have helped out!

  • @adim4927
    @adim4927 3 ปีที่แล้ว +7

    Thank you for sharing this valuable knowledge!!

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว

      Thanks for watching and commenting!

  • @bookieyadigg
    @bookieyadigg 2 ปีที่แล้ว +4

    2022 video still helping us. Thanks

  • @Peterpiperofthes
    @Peterpiperofthes 2 ปีที่แล้ว +6

    I went and changed out my breaker switch, then it would still not flip on. You saved my butt bc it was a screw, touching the side of on of my boxes, thank you for the great video

  • @markbowles2382
    @markbowles2382 ปีที่แล้ว

    I always wanted to go to Chicago (for the infrastructure and the U505).... thanks for the free info sir....im on the univ of utube working on a dead dishwasher after a lightning strike.... so thanks for the basics, every little bit helps.

  • @MOUSEBOWEN
    @MOUSEBOWEN 3 ปีที่แล้ว +5

    Awesome video. I’m a new handyman on some apartments complex for 2 years. I got a called last night Tennants says smells like burning and only half of the house has power. Many outlets wasn’t working. The breaker was tripped . I put the breaker back to on and tripped right away. I couldn’t find was outlet was tripping the breaker. So I had to called a experienced electrician

    • @MOUSEBOWEN
      @MOUSEBOWEN 3 ปีที่แล้ว +7

      @The Mythology was a burned outlet was making contact hot to neutral . Electrician replaced it and got fixed

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว +2

      Thanks for the positive feedback

  • @G.I.JeffsWorkbench
    @G.I.JeffsWorkbench 6 หลายเดือนก่อน +1

    Very clear explanation. Thank you.

  • @lisanjohnny1
    @lisanjohnny1 11 หลายเดือนก่อน

    Sending you Aloha from Oahu, this helped me tremendously

  • @Komander8236
    @Komander8236 3 ปีที่แล้ว +2

    Thank you. Helped me fix an issue

  • @DaxEmerson2
    @DaxEmerson2 2 ปีที่แล้ว +4

    This video nailed all my question. The one about the outlet you should explain how to fix that problem . Thanks for the video

    • @piotrfolczyk8589
      @piotrfolczyk8589 2 ปีที่แล้ว +3

      Open it, see what is shorting, unshort it.
      Replace outlet if not in perfect condition.

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว +1

      Thank you!

  • @oscarcolindres1051
    @oscarcolindres1051 3 ปีที่แล้ว +2

    Great video.

  • @vivienne192
    @vivienne192 2 ปีที่แล้ว +5

    This is such a informative video. Thank you for making this

  • @speed_rider362
    @speed_rider362 3 ปีที่แล้ว +8

    In our country we no longer use metal mounting brackets to install wall sockets. You can find them in very old installations (about 60 years or more). It is nowadays expressly forbidden. Electricians use in-the-wall-brackets and boxes made from a fire-retardant and heat resistant plastic material. It is for those exact reasons you just mentioned.

    • @crand20033
      @crand20033 2 ปีที่แล้ว +1

      My house in the US is 20 years old. I have plastic socket boxes. I have a bedroom where I have a dorm fridge and a table microwave plugged into different sockets in the room with a 15 amp breaker in the garage. The breaker will just mysteriously trip every 3 or so days and on the last occasion we turned on the microwave and the breaker tripped. Because of the problem, I went and bought a new fridge, microwave and breaker. We still have the problem so we unplugged the microwave and that solved the problem but we shouldn't have to do that because we have three other bedrooms all having fridges and microwaves and we don't have the problem in those other rooms. What should I do so that I can leave the microwave plugged in?

    • @speed_rider362
      @speed_rider362 2 ปีที่แล้ว

      @@crand20033 I am sure an electrician would help you. It might be so that a 15 Amp breaker is just so-so and these two appliances sometimes overload it. You will probably need to add at least one more breaker to supply power for the oven.

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว +1

      @@crand20033 If you haven't solved the issue yet, we do see microwaves that go bad internally from time to time. Recently had a similar issue at a clients home we had just rewired. The client was pissed and thought we messed something up after a year of everything working properly. We were able to determine the microwave was the issue and they were able to get a new one and were happy at the end of the day!

  • @MrCashmerethoughts
    @MrCashmerethoughts 3 ปีที่แล้ว +3

    Thank you, great information

  • @PDTH12
    @PDTH12 ปีที่แล้ว +1

    This was perfect. Thanks.

  • @chefbambu9382
    @chefbambu9382 2 ปีที่แล้ว +1

    Thanks. You solved the isse, it was a new device I had plugged into an outlet causing the circuit to switch off.

  • @RicoDjMigo
    @RicoDjMigo 2 ปีที่แล้ว +3

    Very informative💪🏾💪🏾

  • @yenle5408
    @yenle5408 3 ปีที่แล้ว +4

    Hi Arnold, I live in Canada. Could you tell me the reason why my outlet didn’t have power when I plug into the car to keep it warm ( -20’C). I changed the outlet but the Circuit Breaker keeps tripping. Do I need to change the Circuit Breaker or Fuse? Thank you very much.

  • @dlouis1830
    @dlouis1830 2 ปีที่แล้ว +3

    Thank you this is so good for homeowners who want to be conscious of their Houses inner workings. Would these scenarios change if the breaker only trips when I unplug my microwave? As long as I keep the microwave plugged in it’s fine it’s the darndest thing.

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว

      Hey Louis, sounds like you have a short somewhere. Hope you were able to solve your issue!

  • @KENNETHEMorse
    @KENNETHEMorse 3 ปีที่แล้ว +1

    Very,very helpful

  • @AimGobalWorldBibleSchool
    @AimGobalWorldBibleSchool ปีที่แล้ว +1

    Thanks man...Fantastic! and Outstanding!

  • @groundtenpro
    @groundtenpro 5 หลายเดือนก่อน

    Great info! Thanks!

  • @Rivanni1
    @Rivanni1 ปีที่แล้ว

    thanks for the info very helpful

  • @kathyr5278
    @kathyr5278 2 ปีที่แล้ว +2

    Awesome thank you so much for the info. 👍🏻

  • @bennylynn6211
    @bennylynn6211 ปีที่แล้ว

    Thank you for the info

  • @heroknaderi
    @heroknaderi ปีที่แล้ว +1

    Thamk you for your time.

  • @gregbeaudion7781
    @gregbeaudion7781 2 ปีที่แล้ว +2

    thank you from New Orleans

  • @reginagrimes3873
    @reginagrimes3873 2 ปีที่แล้ว +2

    Thank you for explaining this in English.

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว

      Thank you for the feed back!

  • @monaxiinc.6542
    @monaxiinc.6542 ปีที่แล้ว

    Thanks for this video. I was able to fix the simple issue where an electrician would have charged fortune.

  • @josephgrierjgrier11
    @josephgrierjgrier11 2 ปีที่แล้ว +1

    This was very helpful.

  • @maureenreeder
    @maureenreeder ปีที่แล้ว

    Can an overload or other issue you mentioned trip a circuit breaker other than the one causing the problem? My kitchen remodel is happening and electrical work done, but the garage door circuit breaker keeps tripping. It doesn't look tripped because the position shows on but when I flip it, it works.. for one use, maybe 2.

  • @prorescuer1
    @prorescuer1 3 ปีที่แล้ว +2

    Great info

  • @mantaship
    @mantaship ปีที่แล้ว

    At 2:48 I new I had the winner. Thanks for saving me $200 or so bucks...

  • @losmoore3358
    @losmoore3358 2 ปีที่แล้ว +2

    Thank u for the video.

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว

      Thank you for watching and commenting!

  • @JB-rt1ig
    @JB-rt1ig 10 หลายเดือนก่อน

    Nice video. My breaker has recently tripped when I plug the fridge or a saw but there is only a Dyson charger on the circuit. Until now the fridge was plugged in the outlet and I never had any problem. Without the fridge Or the saw plugged in the outline the circuit works fine. any idea where it can come from ?

  • @johnmcdonald5998
    @johnmcdonald5998 3 ปีที่แล้ว +1

    Thanks for sharing your knowledge!

  • @doveboyz857
    @doveboyz857 2 ปีที่แล้ว +1

    Thanks so much 👍

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว

      Thanks for watching the video!

  • @evelynlebron6824
    @evelynlebron6824 ปีที่แล้ว

    I am in Arizona so calling you would be out of the scope of work but I do have a question I hope you can answer for me. I changed all of the wall sockets in my master bedroom about 2 months ago and the breaker will trip sometimes but I can reset it and I am good to go for days and/or even weeks. Any idea on what would cause this issue? I changed the sockets because I plugged a vacuum into a wall and lost power to the room so I figured maybe the wall sockets were old and should be replaced. The house was built in 2002.

  • @cthao559
    @cthao559 3 ปีที่แล้ว +1

    Nice video

  • @wahinenuiloa
    @wahinenuiloa 7 หลายเดือนก่อน

    Thank you!

  • @robertfaldetta6560
    @robertfaldetta6560 2 ปีที่แล้ว +1

    Hi, loved the video. I have a breaker that I cannot reset, it arcs when I try. There are several outlets but nothing is plugged in. A visual inspection does not reveal anything, but maybe I am not thorough enough. I was looking for some kind of tester, but are there any testers which can test the outlets with no power from the panel? Thanks

    • @arnoldelectricservices8235
      @arnoldelectricservices8235  2 ปีที่แล้ว

      Hi, Thank you! There are outlet testers you can buy, but they won't tell you where the issues is.

  • @zapataalonzo9177
    @zapataalonzo9177 ปีที่แล้ว

    I have a question sir,I have an outside outlet being powered by an inside outlet . I have the boxes secure to wall, I put silicon on the outline of the boxes to protect it from water and and all I don’t have wires crossing, I made sure the outlet does not touch the metal box, I taped all possible loos cables, inside the house , I don’t have an overload, I made sure the box is not energized by a loose cables, I even used the Klein tool that gets connected to the outlet and lets you know what’s wrong and the breaker still trips every other week or every two weeks. What could it be?

  • @nhattuygiaithiensaunguyen9885
    @nhattuygiaithiensaunguyen9885 3 ปีที่แล้ว +3

    thank you so much

  • @javiloc
    @javiloc 3 ปีที่แล้ว +1

    Can the breaker trip just 'cause or is there always an underlying issue?

  • @stevenalexander5367
    @stevenalexander5367 2 ปีที่แล้ว

    What about the breaker tripping when you add a load to the ckt...any load like turning on a light, plugging something into the receptacle, etc? that's my issue. i have several light switches, smoke detectors, and two receptacles on that ckt. they all worked for years until the weather caused a neighborhood blackout. when the blackout was over the ckt started tripping. it doesn't matter which switch or receptacle in that ckt. i disconnected the smoke detectors, unplugged everything, and tuned off all the lights. the breaker stays energized until i either turn on a light, plug something in, or connect a smoke detector, then the ckt trips.

  • @raymondgarafano8604
    @raymondgarafano8604 3 ปีที่แล้ว

    If a neutral screw touches a grounded box, would that trip a gfi brkr? the idea that the neutral must carry exactly same as ungrounded wire?

  • @shananarocks
    @shananarocks 2 ปีที่แล้ว +1

    Great wise advice. Can i check if my aunt's office MCB that keep tripping. According to her staff, it is the old UPS that is causing the problem and asking her to replace those with new UPS. Appreciate your advice.

    • @arnoldelectricservices8235
      @arnoldelectricservices8235  2 ปีที่แล้ว

      Might be best to hire an electrical to test the load of the UPS and also do a load calculation for you to determine if your system is sized properly. Thank you for the kind words!

    • @shananarocks
      @shananarocks 2 ปีที่แล้ว

      @@arnoldelectricservices8235 Thanks Arnold.

  • @guysawka818
    @guysawka818 2 ปีที่แล้ว +2

    My problem is all of a sudden it started tripping out of nowhere?? 4 lights are on the circuit and all others work n stay on; but only the garage lights trip it. I changed both switches (the one in garage n the one in the house) , but it still trips. I unplugged the 3 fluorescent lights in the ceiling that the tripping switches go to, but it still trips. Ugh
    Any suggestions?

  • @EscoPicoTrane
    @EscoPicoTrane 2 ปีที่แล้ว +2

    Excellent video brother, I have a 50a that I'm using for my EV, It won't trip while in use but I'll leave drive around all day and come back and the circuit has tripped. It's dedicated with nothing else on it. It's a 6 gauge. Any idea why it trips when not in use? Thanks.

    • @arnoldelectricservices8235
      @arnoldelectricservices8235  2 ปีที่แล้ว +1

      No idea! There could be a loose connection by one of the breakers that's causing heat to build up. If its not a loose connection an electrician can put a recording electrical tester on your panel overnight to read any spikes in voltage or amperage. Thank you!

  • @beebob1279
    @beebob1279 3 ปีที่แล้ว +11

    Here’s my situation. I built an addition. Everything including the electric was inspected and passed.
    I have four outlets on the circuit. If I use the first outlet I’m fine. But when I use the vacuum cleaner on any circuit gouging away from the breaker it trips.
    I’m going to be pulling the outlets this week and then try the vacuum. If it doesn’t trip then I know I’m touching something in the box. It only goes when a load on put on.
    I was told it could be a bad breaker in the panel or a screw is touching it.
    But when it’s left alone the breaker doesn’t trip.
    Suggestions?

    • @NickieSzontagh
      @NickieSzontagh 3 ปีที่แล้ว +11

      Most inspectors wouldn't catch bad splices,loose screws, or missed wired devices. Assuming it is not an arc-fault or gfci breaker. #1 Get your Electrician back that did the work. #2 Start by checking for proper voltages (120v) at each outlet #2 remove panel cover to check circuit connections. #3 pull out receptacles affected an look for any discoloring or burn marks ,loose screws,or bad splices.

  • @MzzzKLA83
    @MzzzKLA83 2 ปีที่แล้ว +1

    I have a 1984 condo in Louisiana. With high ceilings. I have a ceiling fan that trips my breaker. Company disconnected the light switch. $500. To much to fix a ceiling fan. Hangs 14ft high ceiling 28ft. And my furnace trips my main breaker. Thx for a few ideas and tips to try.

  • @markHolmes81274
    @markHolmes81274 หลายเดือนก่อน

    I have a breaker that trips every day at the same time span. In the evening, around 2 to 7 when the sun is hitting the west side of my house.

  • @jramirez8057able
    @jramirez8057able 2 ปีที่แล้ว

    Thank you.

  • @gillart99
    @gillart99 2 ปีที่แล้ว +3

    Good stuff. I’m living in a 1937 home with this exact problem and no idea how to attack it.

  • @dsmith5832
    @dsmith5832 3 ปีที่แล้ว +1

    Great video! Thanks for sharing.

  • @AT-yo3ik
    @AT-yo3ik 18 วันที่ผ่านมา

    Good info

  • @roheezy25
    @roheezy25 3 ปีที่แล้ว +2

    Thank you

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว

      Thank you for watching and commenting!

  • @lisamcglothin5424
    @lisamcglothin5424 2 ปีที่แล้ว +1

    What if it's a water heater, 240 . We noticed no hot water,tried resetting breaker but it immediately trips. There is only water tank running off that breaker,no outlets. Does that matter?

  • @tatersacs85
    @tatersacs85 2 ปีที่แล้ว +1

    Great video... I have a welder that keeps popping the breaker. Is it ridiculous to change out the breaker?

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว +1

      Hey Harry. Thanks for the feedback! Changing out the breaker may not be a bad idea, but it depends on the conditions of your system. The wire needs to be rated to handle the current of the larger breaker. Your welder should have a "name plate" on the device telling you what the FLC or Full Load Current of the unit is. Check that out. Hit me back up if you have more questions and that does not solve your issue!

  • @selvestre
    @selvestre 3 ปีที่แล้ว +3

    Got an estimate last week. They also said they wanted to re-wire from 14 to 12 Gauge into three separate rooms. He didn’t even look at the wiring. He just gave me an estimate of around 2400. Not including the possibility of opening up the wall.
    I started questioning him, cause he told me my laptop can trip it as well?
    My parents been living in the house since the 60s. This always happened over the last 30 years cause of a hairdryer and heater on at the same time or a combination of toe high wattage items. This only happens on one side of the house.

  • @GmGarlo
    @GmGarlo ปีที่แล้ว

    my tester read my hot and neutral was reversed, so to fix this do you just switch them over or is it more complicated than that?

  • @dimviesel
    @dimviesel 2 ปีที่แล้ว +2

    My Circuits iz Trippin’ Yo!😎
    Whadup wit dat?

  • @odiswilliams3391
    @odiswilliams3391 2 ปีที่แล้ว +1

    Thank God for your expertise....fixed my problem!!

  • @majormagics5571
    @majormagics5571 ปีที่แล้ว

    How about when the GFCI in the bathroom (also wired to the lights) goes out after a couple hours (trips). then We can reset it and we might be good for 10 minutes or a day..? Do you think the 15 amp breaker could be going bad!?

  • @gamingtrading7119
    @gamingtrading7119 2 ปีที่แล้ว

    One ? So i turn the fan in the kitchen on it will still work it will turn on but it will flip a separate breaker on panel? And its on a separate braker?

  • @Tecalitlan1943
    @Tecalitlan1943 2 ปีที่แล้ว +1

    I have an older Sears Craftsman 30 gallon air compressor, runs on 110 (15 amp circuit) in my garage. My compressor works fine, but than after a few minutes it pops the breaker. I re-set the breaker and then it pops again. Been doing it for years, but now it has gotten worse. Before I could fill it all up, now it fills just a little. Do you think it’s the capacitors (run or start capacitors) on the compressor and if so which ones? Or do I need to increase it to 20 amp?

    • @user-ds9fg8ru4z
      @user-ds9fg8ru4z ปีที่แล้ว

      If you pull more than 80% on a 15 amp breaker it will heat up and eventually trip! Check your nameplate rating. You may have to dedicate a 20 amp circuit for your air compressor!

  • @2JobsStillPoorUSA
    @2JobsStillPoorUSA 3 ปีที่แล้ว +1

    My older mh i had issues with my hot water heater. The breaker would trip. Turn it on get maybe tepid washer. Had stuff replaced in water heater but still had breakers trip. Turns out the breaker switch was damaged and burnt and brittle. Replaced that and bam hot water and no more trips.

  • @MendezVictor3
    @MendezVictor3 3 ปีที่แล้ว +1

    Hi Arnold, I'm having an electrical issue at home, I was wondering if you could guide me.
    I have a cable that runs from the oven directly to the main breaker, passing through a socket purposely fitted for the oven.
    When I turn the socket on the breaker switches off, but when I turn the socket off then I can turn the breaker on and it will work.
    However I tried changing the socket with a socket that I know for sure it works, but the same thing happens. The oven is not yet connected.
    What could it be??

    • @studiotutorial
      @studiotutorial ปีที่แล้ว

      Weird. Could it be a short-circuit? And by "then I can turn the breaker on and it will work.", what did you mean by "it"? The breaker?

  • @okioki1131
    @okioki1131 ปีที่แล้ว

    I wish you were in Denver!!! Dangit!

  • @mig3872
    @mig3872 3 ปีที่แล้ว +3

    Thank you. Electrician coming this week. But my breaker is now tripping without anything plugged in. My outlets for main tv, cable box, surround sound. The outlets seem to be culprit and maybe it’s the ground fault you said. But breaker stays on for like a min now then trips. Not instantly. Any thoughts?

    • @cristinar5535
      @cristinar5535 3 ปีที่แล้ว

      Hey what was it ? Same problem

    • @mig3872
      @mig3872 3 ปีที่แล้ว +2

      @@cristinar5535 Electrician said it was breaker and replaced breaker. When took panel off, it was also discolored a little.

    • @ariellebloomfield1871
      @ariellebloomfield1871 2 ปีที่แล้ว +1

      Did that fix it

  • @raymondgarafano8604
    @raymondgarafano8604 3 ปีที่แล้ว +1

    used to be 2 20 amp kitchen circuits. Thanks!

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว

      2 - 20amp Small Appliance Circuits as a minimum just for the countertop outlets. You should also have an individual circuit for: Fridge, Dishwasher, Microwave, Disposal, Stove and Exhaust Hood. Sometimes you can combine the stove if it's gas or propane with the exhaust hood.

  • @LRon-ef7ni
    @LRon-ef7ni ปีที่แล้ว

    I have a breaker that won’t reset. It’s a breaker in my Solar panels’ subunit. There’s a buzzing and it trips. The electrician for the solar company couldn’t figure it out and now I’m waiting for another electrician to come check. Any thoughts on what the issue is?

  • @jonathandiaz1701
    @jonathandiaz1701 20 วันที่ผ่านมา

    How helpful can a surge protector be with this issue ?

  • @carth4876
    @carth4876 ปีที่แล้ว

    Question, When my A/C is running and I'm taking a shower my power cuts off to the house, FYI, I have a tankless water heater.

  • @donnag4786
    @donnag4786 3 ปีที่แล้ว +1

    What about if you put the wires to the wrong side of the bolts even if grounded don’t you have to match brass to brass and silver to silver? I think mine may be backwards causing a short now after a year it was fine all of a sudden keeps tripping.. I’m going to try replacing it.. thank you

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว

      The hot wire should be on the brass screw and the neutral wire should be on the silver screw. However if you wired it backwards it would not cause a short.

  • @jdrs4214
    @jdrs4214 ปีที่แล้ว

    One question: I have a brand new 230V Toshiba window unit. It’s a big one. You pull this baby out through the inside of the house, and wheel it outside to clean it. It’s on a dedicated circuit, or receptacle (nothing else is on this circuit). ….and she keeps tripping the breaker.
    Is there a recommended amp rating for these units, Or a certain household receptacle wiring size for a 230V????
    Oh, and here are some bits of info from this Toshiba unit’s data tag:
    Volts: 230/208V single phase.
    RLA: 5.8/6.25A
    LRA: 40A
    FLA: 0.8A
    Amps: 7.2/7.6
    Please forgive my ignorance. All I know is that wire size, and amp ratings have a lot to do with each other, and very important to get this right, and not burn your house down.

  • @firehorse66elaine
    @firehorse66elaine 2 ปีที่แล้ว +1

    Thank you ;)

  • @ruyaal
    @ruyaal 2 ปีที่แล้ว +4

    What is the solution if your breaker keeps tripping and you cannot use a 20 amp in a 15 amp breaker. Do u need to re-wire?

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว +1

      You should never take out a 15 amp breaker that is tripping and install a higher amperage breaker. You need to fix the issue. The wire that is terminated at each breaker is rated only to carry the current associated with the breaker. The breaker is actually designed to protect the wire and keep it from overheating. So if you have a smaller wire on a larger amperage breaker you will ruin the wire causing a larger and much more costly repair in the long run. It is best to fix the root of the problem.

  • @arungopalan1413
    @arungopalan1413 2 ปีที่แล้ว

    Thanks.

  • @rogerdsilva3889
    @rogerdsilva3889 3 ปีที่แล้ว +1

    Hi sir there is nothing plugged in my sockets but as soon as I turn on the switch my RCD trips. Can u help

  • @user-kg1ff2bj5u
    @user-kg1ff2bj5u 11 หลายเดือนก่อน

    Hi my name is Jackie I have a problem breaker trips immediately I disconnected the outlets where the rooms had no power and hallway I checked they weren't touching so I took them off meaning I disconnected them and I put in a new breaker it tripped again so idk what it could be

  • @juliacross9414
    @juliacross9414 2 ปีที่แล้ว

    Why does my light come on in the off position then the breaker immediately trips when I flip the switch into the on position to shut it off. This switch has been in my home for several years. I took a light out and it started doing this.

  • @josh.kaptur
    @josh.kaptur 2 ปีที่แล้ว +1

    I have an outdoor ceiling fan driving me crazy... I can turn it on and it's fine... at some point in the day, it is guaranteed to trip the breaker... almost never happens right away and could be hours later. Any thoughts?

  • @Sparki883
    @Sparki883 2 ปีที่แล้ว +1

    What about the 4th reason why a breaker trips, it's old and is failing? You can still reset it but it trips under normal load.

  • @Mr.709-
    @Mr.709- 6 วันที่ผ่านมา

    I have no idea what is going on but my breaker keeps tripping in my living room it was working fine for a while and i went out bought a new fan that uses 120w and another that used 50w both on opposite sides of the house i had the 120w in the living room and after being on for about 2-5 mins the breaker trips and the same happens with the 50w when i switched them from rooms

  • @dasledogg64
    @dasledogg64 ปีที่แล้ว

    My washing machine keeps tripping the GFCI outlet during the spin cycle. I reset the outlet and it trips it again. Is this a problem with my washing machine or do I need to replace my GFCI outlet?

  • @topdawg3359
    @topdawg3359 2 ปีที่แล้ว +17

    One trick seems to be turn off lights or other things while you use the thing you are trying to use. Circuit breaking often = fire hazard = get a professional involved before you place burns down.

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว +3

      Is that a trick or a work around? hahaha. You should not have to turn lights off to use the circuit you are using.

    • @J_WheelerDoll30
      @J_WheelerDoll30 ปีที่แล้ว +3

      @@jackarnold3062 exactly. Our property manager and I have been going back and forth on our breaker and dishwasher going out. I do t have “too many” things using lower at once. I put renters insurance on our policy because every time that dishwasher is cycling after I switch the breaker back to working, it smells like burning plastic or burnt metal. This has been going on for over a year and each maintenance guy replaced something in the breaker and it doesn’t resolve the issue. The dishwasher fills up, and the breaker is tripping.. now my new smart tv is crackling and having issues, also the sockets rarely have power. Can’t even use my electrical sockets most of the time. I’m over it. I hope if the apt burns, that myself, babies and dogs , and hubby aren’t there. It’s a scary feeling :(

    • @jglaboratory
      @jglaboratory 9 หลายเดือนก่อน +1

      I kept smelling burnt fishy smell. Manager said its not the electric. Turns out I had an outlet melting in the wall. Crazy how much we can learn from Google nowdays.told em it was bad

    • @angelicdemise6224
      @angelicdemise6224 8 วันที่ผ่านมา

      I’m late but 9/10 majority of the time electricians wired multiple receptacles and lighting fixtures on the same circuit and the gauge of wire they used isn’t rated for much

  • @hydrainarms3135
    @hydrainarms3135 2 ปีที่แล้ว +2

    Could also be drywqller's pierced a wire if that's the case witch the % is very low but again could happen if that's the case then good luck to locating the pierced wire reason I say that cuz it happened to me licensed electrician for 20 years..
    But like the vid 👍

    • @jackarnold3062
      @jackarnold3062 2 ปีที่แล้ว

      That could happen and that would fall under the short circuit category.

  • @judymcneal8519
    @judymcneal8519 ปีที่แล้ว

    My 20 amp breaker 220 going to my well keeps tripping, I disconnected the wires from the well and turn on the breaker and it still trips, how do I find where the wires in the wall or how do I find the short? Thank you so much Sir

    • @RcPlayer-tt2vw
      @RcPlayer-tt2vw 6 หลายเดือนก่อน

      Same we’re screwed lol

  • @isithotmama
    @isithotmama 2 ปีที่แล้ว +1

    I have a new home (let's than 5 yrs) when i run my space heater it trips everytime i reset and start the heater again after about 15 minutes. I only have my TV on with it which is not going out. Why does this keep happening. I'm getting soooo tired of having to go to the breaker box every 20 minutes

  • @JackieBercier-yt8hm
    @JackieBercier-yt8hm 25 วันที่ผ่านมา

    If it's a ground where the metal is touching the metal, how do I find the problem? Check every outlet??

  • @kellysater3562
    @kellysater3562 2 ปีที่แล้ว

    Question: our pool pump was working fine all summer, today while the vac was hooded up I disconnected the power, opened the basket and cleaned the pool debris then replaced the basket, and plugged in the pump. It immediately trips the (damn) GFCI outlet it’s plugged into. The outlet won’t reset, and the pump seemed to be working fine. Best guess?
    Pump is a Hayward, 115v, 12.0amp on a 15 amp dedicated GFCI circuit. The pump is about 6 years old, outlet is at least 10 years old.
    It’s got me completely stumped. I am a welder, not an electrician. (Or pool guy)

    • @aPheonixRises
      @aPheonixRises ปีที่แล้ว

      Gfci plugs don't last forever. If it wont set either the breaker tripped and there isn't power to the gfci, or it's just worn out and needs to be replaced.

  • @crocsonletsgo9665
    @crocsonletsgo9665 2 ปีที่แล้ว +1

    Also there may be moisture in your conduit. That was my issue.

  • @robertehlers4330
    @robertehlers4330 2 ปีที่แล้ว

    I need your advice