1 ton = 3.5 kw , ye cooling capacity h na ki electricity consumption. 1.5 ton ac 1300 se 1800 watt leta h, toh 16 amp mcb is good. I have 16 amp mcb on 1.5 ton ac and never trips
16 amp mcb is enough for a 1.5 ton of ac all acs hving 1.5 tn capacity consumes about 8-9 amp max which is half of the mcb if the voltage is too low about 150 still the mcb will not trip
This is nonsense!! 1.5 ac is not 5000+ watts, that is the COOLING CAPACITY not WATTAGE. Devide the value of cooling capacity by ISSER value to get an approximate wattage value, But in outdoor unit there is mentioned the total wattage.
1.5 air conditioner Power input : 1790w Running current : 8.2Amp Power supply: 1ph/230V/50hz मुझे कितनी आरएम केबल और कितने एम्पीयर सर्किट ब्रेकर का उपयोग करना चाहिए?
1.5ton inverter AC mein 32amp ka MCB bahut jayada ho jayega jiski current rating 5.5amp hai meri calculation k hisab se 10amp ki MCB sahi hai aur aap batay
Don't use Isolator. Use a MCB. 40A will be on safer side. When shortcircuit or overload happens in your AC, isolator will not trip which will result fire & shock. MCB will trip in that case & it will come costly than isolator.
The MCB, is it B or C type and how many amps 16A, 25A, 32A and what is the wire sq mm, is it 2.5 mm or 4 mm. Also what is the 3 pin socket amperage 16amps? This is for 1.5 ton, 5 star inverter type split ac
Brother mere pass o general ka window AC hai non inverter maine direct socket me lagaya hua hai 16amp ka socket hai but socket maalt ho Raha hai baar baar iska koi solution hai?1.5 ton ka AC hai
नही ये एसी को खराब कर देगा यदि 1.5 टन इन्वर्टर एसी हे तो 10 एंपियर का टाइप बी एमसीबी लगा सकते हे और यदि fix speed ac हे तो 16 एंपीयर की एमसीबी लगाए ।एमसीबी ओवर अधिक एंपियर की लगाने का कोई मतलब नहीं हे वो सिर्फ एक on off switch की तरह काम करेगी वैसे भी 1.5 टन इन्वर्टर अब 8 एम्पियर का लोड फुल स्पीड पर लेता हे है एक अच्छा 4 kva का ऑटोमैटिक स्टेबलाइजर जरूर लगाएं यदि घर के आस पास वोल्टेज में 20 वोल्ट तक उतार चढ़ाव है तो 150 से 290 वोल्ट तक और यदि 40 से 50 वोल्ट का अंतर हे तो 90 से 285 वोल्ट का ऑटोमैटिक स्टेबलाइजर लगाए जो200 दे 240 वोल्ट आउट पुट देगा स्टेबलाइजर हाई लो कट ऑफ थर्मल ओवरलोड प्रोटेक्शन और टाइम डिले 10 सेकंड का हो
Nhi Bhai Trip krega mera kr rha h trip moduler board me lga h 25 A ka MCB har 10 minutes me trip krta h but low pr other mode me nhi krta h iska mtlb 32 A hi lgega
Ek customer ke ghar geyatha me .uska 16amp ka mcb tha usko badalne keliye geyatha unka ac, induction, washing machine, 5 fan, or bahut kuch to mene kaha kiye 16amp load nehin lega 32amp lagadenge unhonne saf saf mana kiya ki 16amp ka mcb hi lagao wo kya thik hai ????
Sare ghar ka load nikaalne pahle kitna hai agar 16 empier se jyada ho raha to MCB badalna padega Jo 16 se upar hai usko lagana padega Nahin to बार-बार typing hoga
3.51kw is heating KW Which is not actual KW of AC. Wrong calculation. Correct calculation is 3.51 KW will be divided by efficiency or star rating of AC. If it is 3 star AC then consider the efficiency as 2.6-2.7 though it will be depend on weather. So divide 3.51 by 2.6 we get 1.3 KW. Divide 1.3 KW by 220 volt we get 6 Amp. Then 1.5 sqmm copper wire is more than enough for 1 ton AC. Or for more safety we can use 2.5 sqmm.
1 ton = 3.5 kw , ye cooling capacity h na ki electricity consumption. 1.5 ton ac 1300 se 1800 watt leta h, toh 16 amp mcb is good. I have 16 amp mcb on 1.5 ton ac and never trips
16amp work nhi karega 1.5 Tn AC me 32 amp hi sahi rehta hai
16 amp mcb is enough for a 1.5 ton of ac all acs hving 1.5 tn capacity consumes about 8-9 amp max which is half of the mcb if the voltage is too low about 150 still the mcb will not trip
😅@@texastiger7139
Absolutely wrong information. He knows nothing. Misleading information.
25 ampere is enough for 1.5 ton ac
3.5kw 3500watt hota h…ye electrical terms me nahi he cooling capacity he..watt me max 950-1200w tak hi hota h
This is nonsense!! 1.5 ac is not 5000+ watts, that is the COOLING CAPACITY not WATTAGE.
Devide the value of cooling capacity by ISSER value to get an approximate wattage value,
But in outdoor unit there is mentioned the total wattage.
Dont waste you time to watch this video.
Info in the video
1 ton keliye 20Amps MCB
1.5 ton keliye 32 Amps MCB
2 ton keliye 40 Amps MCB
Thank me i have saved ur 5 mins 😁
Simply 1 ton =10 ampere
1.5 ton= 16 ampere
2 ton= 20 ampere
This is wrong because you did not power factor use.0.8
1.5 air conditioner
Power input : 1790w
Running current : 8.2Amp
Power supply: 1ph/230V/50hz
मुझे कितनी आरएम केबल और कितने एम्पीयर सर्किट ब्रेकर का उपयोग करना चाहिए?
Bahut khoob
1.5 ton non inverter window a.c par stabilizer laga hua ho tou kitne amp ka mcb lagana chahiye?
1.5ton inverter AC mein 32amp ka MCB bahut jayada ho jayega jiski current rating 5.5amp hai meri calculation k hisab se 10amp ki MCB sahi hai aur aap batay
Can we use 32amp switch for 1 ton ac!!
You can run 8.5 ton 3 phase AC or 2 ton Single phase AC if it is 3 star rating. If it is 5 star rating then tonnage will be higher.
No
Nice video
1 ton ac maximum watt construction is 1000 to 1400
Good information
Super sair aidia
Good
Sir 2tan ka ac pe 40 amp ka isolator laga sakte hi Rply
Yes
Don't use Isolator. Use a MCB. 40A will be on safer side. When shortcircuit or overload happens in your AC, isolator will not trip which will result fire & shock. MCB will trip in that case & it will come costly than isolator.
Agar 1.5 ton ka 2 ac hai Ghar me toh ac ka supply line keliye separate MCB lagana ho toh kitne ka lagaye
Aise hi wire ka bhi video bana dijye wire kitne ka use karte kitna waat me
Yah video aap dekh lo : th-cam.com/video/bE3SwrMlWGk/w-d-xo.html
@@USMANELECTRICAL thnx aapko insta me massage kiya load shadule Or sab symbol ka photo ke liye
@@arshkhan0732 ok
Agar 40 A 1.5 ton ac m lga le to koi dikkat nhi hogi ?
Very good explanation. Keep it up .Thanks
1 ton eqauls to 900 - 1200 watt maximum.
Good 👍
Nice
The MCB, is it B or C type and how many amps 16A, 25A, 32A and what is the wire sq mm, is it 2.5 mm or 4 mm. Also what is the 3 pin socket amperage 16amps? This is for 1.5 ton, 5 star inverter type split ac
Brother mere pass o general ka window AC hai non inverter maine direct socket me lagaya hua hai 16amp ka socket hai but socket maalt ho Raha hai baar baar iska koi solution hai?1.5 ton ka AC hai
2 Star 2 ton window ac me kitne amp ka mcb lagayege
Very nice video🎥
2tonAc me kitna ka dp swich Lagana hai
32Amp. ka Dp
Can I use 32 AMP MCB for 1.5 ton non Inverter AC..
नही ये एसी को खराब कर देगा यदि 1.5 टन इन्वर्टर एसी हे तो 10 एंपियर का टाइप बी एमसीबी लगा सकते हे और यदि fix speed ac हे तो 16 एंपीयर की एमसीबी लगाए ।एमसीबी ओवर अधिक एंपियर की लगाने का कोई मतलब नहीं हे वो सिर्फ एक on off switch की तरह काम करेगी वैसे भी 1.5 टन इन्वर्टर अब 8 एम्पियर का लोड फुल स्पीड पर लेता हे है एक अच्छा 4 kva का ऑटोमैटिक स्टेबलाइजर जरूर लगाएं यदि घर के आस पास वोल्टेज में 20 वोल्ट तक उतार चढ़ाव है तो 150 से 290 वोल्ट तक और यदि 40 से 50 वोल्ट का अंतर हे तो 90 से 285 वोल्ट का ऑटोमैटिक स्टेबलाइजर लगाए जो200 दे 240 वोल्ट आउट पुट देगा स्टेबलाइजर हाई लो कट ऑफ थर्मल ओवरलोड प्रोटेक्शन और टाइम डिले 10 सेकंड का हो
@@manoramasharma928NICE INFORMATION .
C25 lgaya h 1.5 ton AC m shi rhega
Single pole ya double pole mcb?
double Pol single Pol donon use kar sakte hain
Amazing video bro
MCB input line hisaab se lagaya .na cooling capacity se?
Bahut khub sir
1 ton= in put line 3.5kw ?
2 ac ma kitni ampear mcb lagana chiya
1.5ton 5star AC mein kitane ampiar ka MCB lagay kuch log 10 amp ki ya13amp ki MCB lagany ko bata rahey hai kya karey
C20 MCB lagega........
Thankyou thankyou sir
electrical symbol par ek video banawo
Electrical symbol mein drawing ka symbol chahie video electrical mein sample bahut Tarah ka Hota Hai aapko kis type ka chahie
electrikal drawing ka aur interview me puchete hai building, home, hospital
@@riyajuddinsolanki847 ok bhai samajh gaya
1fase me kitna ac chal sakta hai
Sir ac me kis types ki mc lagae
B & C
Nice video👍👍👍
1.5 ton me 32 amp chalega ki nehi
Nhi jyada h bhot. 16 ya 20 lagao
25 ampere is enough for 1.5 ton ac
Your calculations is wrong.
Right pls mention
1.5 ton Ka ac oyar Kitna Dena ha
Baat samjhe Nahin aap kya puchna chah rahe hain details mein aap thoda likho
1.5 ton Ka ac pe oyar keya Dena ha 2.5 4. 5.
Bhai power Factor suna hai ki nhi
Yes
0.8 ton tc me kitna ampere ka mcb lgega
10 एम्पियर
Ap let ho gye reply dene m 16 ka lga loya thank u
@@manoramasharma928 sirji 1.5 ton 5 star ac h 25 apmire ki MCB lgai h
Agar 1.5 ton AC main 20 amp MCB la gaya jaye tou kya hoga
Mere ghar pe 20 amp MCB laga h
Jab hum switch on kate h tou mcb drip ho raha h
kuch nhi
1.5 ton ac sufficent 25 amp mcb.
16 ampere lagao 25 jyada h. Max to max 20 tak.
No bro Mera khud hi trip kr rha h 32 A shi h 1.5 ton ke lie mera 25 lga hua h polycab moduler board me
25 trip krra h mere yaha 32amp lgaunga ab tb comment krunga dobara
Mera v ac trip kar raha h 1.5, ton me 25 amp laga hua h technician fault pakad nahi pa raha h...aaj 32 amp laga k dekhta hu
Jab kisi cheez ki knowledge na to Gyan nahi dete@@PlayJewel
1 ton 2ton kya hota hai
AC Mein calling karne ka chamta Hota Hai kam ya jyada calling jaldi karne ka
Voltage. .. Bolte hai... Boltage nhi..
1 ton Ac 7 amp leta he to 10 amp ka mcb lagveo
25 kaafi hai
Wrong video
wrong kese h aap btawo
Aap samjha do ya ase hi
tu gadha hai .... cooling capacity ko electricity consuption bata raha hai .... 25 amp MCB lagegi 1,5 ton ac mai
Nhi Bhai Trip krega mera kr rha h trip moduler board me lga h 25 A ka MCB har 10 minutes me trip krta h but low pr other mode me nhi krta h iska mtlb 32 A hi lgega
🤣🤣🤣🤣🤣
Ek customer ke ghar geyatha me .uska 16amp ka mcb tha usko badalne keliye geyatha unka ac, induction, washing machine, 5 fan, or bahut kuch to mene kaha kiye 16amp load nehin lega 32amp lagadenge unhonne saf saf mana kiya ki 16amp ka mcb hi lagao wo kya thik hai ????
Sare ghar ka load nikaalne pahle kitna hai agar 16 empier se jyada ho raha to MCB badalna padega Jo 16 se upar hai usko lagana padega Nahin to बार-बार typing hoga
3.51kw is heating KW Which is not actual KW of AC. Wrong calculation.
Correct calculation is
3.51 KW will be divided by efficiency or star rating of AC.
If it is 3 star AC then consider the efficiency as 2.6-2.7 though it will be depend on weather.
So divide 3.51 by 2.6 we get 1.3 KW.
Divide 1.3 KW by 220 volt we get 6 Amp.
Then 1.5 sqmm copper wire is more than enough for 1 ton AC. Or for more safety we can use 2.5 sqmm.
Galat information
Sahi aap batao
kya galat hai
1.5 ton AC ne 25AMP ka MCB lagta hai
😂😂😂😂 20a mcb nahi ata hai
20A Aata Hai Bhai
Aata hai
😂😂😂😂20a ka mcb aata hai🤣🤣🤣
Aata hi bhai
बहुत खूब
Nice video
Nice video