  • @easytechbangla1510
    @easytechbangla1510 ปีที่แล้ว +1

    Why you add varistor before fuse?
    Proper way to add varistor after fuse.
    Am i correct?

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว +2

      After fuse

  • @saqibrehman4701
    @saqibrehman4701 หลายเดือนก่อน

    Dear i think max voltage protection should be around 260v max. 270 to 290v tak b appliances mein aygy tu wo already problem ker jygy. What u think about it?

    • @TARIQLAB
      @TARIQLAB  หลายเดือนก่อน

      Ye RMS volts hain Peak volts ziyada hoty hain , 220v ke peak volts 320~330v tak hoty hain,

  • @AchayanIn
    @AchayanIn ปีที่แล้ว +1

    If the surge voltage coming through negative line?? This can happen right?? I would recommend to have fuse need to be installed on both negative and positive lines 😊

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      Fuse will blow in both case, important this is to protect appliances

  • @sumitnarkhede.3105
    @sumitnarkhede.3105 2 ปีที่แล้ว +1

    ACHI JAANKARI DI SIR AAPNE.SIR KYA HUM 471 KI JAGAH 7d 511 NO KA MOV LAGA SAKTE HAI.AUR AAPNE YAH NAHI BATAAYA KI FUSE MITANE AMP KA LAGAAYE HAR EK DIVICE KI POWER ALAG HOTI HAI.CIURRENT CONSUMPTION ALAG HOTA HAI.PLESE BATAAYE.

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว +1

      7d511 850 volt pe short hoga 220 ke liye faida nahi, fuse load se thora ziyda hona chahiye,

    • @sumitnarkhede.3105
      @sumitnarkhede.3105 2 ปีที่แล้ว +1

      @@TARIQLAB DHANYAWAAD SIR.

  • @DiGiTAL_S80
    @DiGiTAL_S80 ปีที่แล้ว +1

    according to the specs of 10d471k it's max ac voltage is 300v, does that mean it will burn at 300v?if yes won't that mean that 299v will go to the electronics and burn it?

    • @amazonquiz6807
      @amazonquiz6807 ปีที่แล้ว

      exactly i want to know , but 10d471k is max 470 voltage

  • @abhisekhrai6706
    @abhisekhrai6706 ปีที่แล้ว

    svc 681-10 mere pc safety purpose ke liye lagaa sakta hu kiya agar ha iskaa rating kitna hain

  • @abdulhusseinabdulhussein8047
    @abdulhusseinabdulhussein8047 8 หลายเดือนก่อน

    An impressive presentation

    • @TARIQLAB
      @TARIQLAB  8 หลายเดือนก่อน

      TQ

  • @chemicalengineer5626
    @chemicalengineer5626 ปีที่แล้ว

    Iam from karachi I have a 12 volt lead acid battery charger which burns over 240volt
    Which mov code should i buy
    How to read code and get as per requirenment.
    Where to get this plug having fuse option

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      3 pin plug available in the market, or u can use inside the device, device input supply?

  • @NandhaKumarrocks
    @NandhaKumarrocks 2 ปีที่แล้ว +1

    i need small help, example i need only 220v output whatever input happens. is that possible? any suggestions

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว +1

      its not a controller or regulator,
      u can use a stabilizer

    • @NandhaKumarrocks
      @NandhaKumarrocks 2 ปีที่แล้ว

      @@TARIQLAB ok got it, it can protect the transformers and other components right?

  • @tonyorchid
    @tonyorchid ปีที่แล้ว

    what about connecting 3 mov s , across N-Erth , L- E and then L-N. any more good?

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      Only L & N

  • @NandhaKumarrocks
    @NandhaKumarrocks 2 ปีที่แล้ว

    can we use it for LED bulbs, FM players, DVD Players because of electrical fluctuations transforms get faulted and replacing. that's why asking

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว

      u can use for any device, appliance

  • @ratnathalur8537
    @ratnathalur8537 2 ปีที่แล้ว +1

    सर धन्यवाद,
    क्या इसे मीटर के पास जहा से सभी जगह सप्लाई जाती है लगा सकते है क्या???सभी चीजों की प्रोटेक्शन हो जायेगी, यदि हां तो क्या यही mov लगेगा, नही तो किस नंबर का लगेगा कृपया बताएं

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว +1

      Jee, laiken iss se pehly fuse zaror lagana. Yehi number 2 ya 3 bhi laga sakty hain, nahi tu pehla number jo 7 ya 10 hai iss ki jaga 20 bhi milta hai

    • @ratnathalur8537
      @ratnathalur8537 2 ปีที่แล้ว

      @@TARIQLAB thanks friend

  • @bradgilbs6013
    @bradgilbs6013 3 ปีที่แล้ว +1

    If 110v whats the good voltage and uf to used for surge power?

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว +1

      10D201K , 130v varistor is good for 110 supply

  • @tonyorchid
    @tonyorchid ปีที่แล้ว

    is it a surge protector , spike suppressor ? if so, will it act as a TYPE 3 protector ? i m facing serious switching surge problem at my home. please do reply Tariq thnx in advance

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว +1

      Yes, choose according to to ur main voltage

  • @001irah
    @001irah 5 หลายเดือนก่อน

    Fridze ke liye fuse ki amp kitni lagani hai.

    • @TARIQLAB
      @TARIQLAB  5 หลายเดือนก่อน

      3A

  • @XYZ-qn7bd
    @XYZ-qn7bd 2 ปีที่แล้ว +1

    Kya ay circut high voltage te mere computor off kar de ga?

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว

      Fuse jal jaye ga, computer safe rahe ga

    • @XYZ-qn7bd
      @XYZ-qn7bd 2 ปีที่แล้ว

      @@TARIQLAB OFF aya ON rahe ga o batao mere pas ups nahi he

  • @abhishekparmar3698
    @abhishekparmar3698 3 ปีที่แล้ว

    Fuse kite amp ka lena hai or mov ki kon se vale for double door refrigerator

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว +1

      mov 10 amp fuse 5 to 8 amp , check fridge consumption

  • @avp.69
    @avp.69 4 หลายเดือนก่อน

    I connected a varistor accross L & N.
    Turns out there was 220v in both L & N which got solved after removing the varistor. What could have happened?

    • @TARIQLAB
      @TARIQLAB  4 หลายเดือนก่อน +1

      What was the issue

    • @avp.69
      @avp.69 4 หลายเดือนก่อน

      @@TARIQLAB Same aapke jaise plug mai Maine varistor connect kiya. But appliance on nahi hua.
      Fir maine plug ka cover kholke plug ko socket pe lagaya aur terminals pe tester laga ke dekha to pata chala dono live and neutral mai voltage 220v as rahi thi.
      Varistor hata ke normal hogaya sab. Varistor laga ke neutral mai bhi 220v aane lage

    • @TARIQLAB
      @TARIQLAB  4 หลายเดือนก่อน

      Mery channel description main WhatsApp hai contact karen

  • @Ckk8888
    @Ckk8888 ปีที่แล้ว

    can i do it on my 4 way extention 3 pin plug with grounded wire ? Is it safe ? Cause the video u show doesn't have grounded .
    P/S: Im not professional electrician.

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      Yes only with live & neutral

    • @HunterEddie
      @HunterEddie 6 หลายเดือนก่อน

      @@TARIQLABcan use with earthing wire or no bro?

  • @farukhagwan8577
    @farukhagwan8577 ปีที่แล้ว

    Sir agar 280 volt aaye to ye mov kam karega kiya please sir

  • @omarjaysultan6293
    @omarjaysultan6293 2 ปีที่แล้ว +2

    Nice video, thank you for sharing. Sorry i couldn't understand your language but despite of that i do understand what you are trying to teach, but if you don't mind may i ask, can i use 2 of that mov in one power strip?

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว +1

      u can use more than one in parallel

    • @omarjaysultan6293
      @omarjaysultan6293 2 ปีที่แล้ว

      @@TARIQLAB Thank you so much. God bless!

  • @uv886
    @uv886 ปีที่แล้ว

    Sir 7d471k mene lagaya leken blast ho raha hai. Esla keu ??

  • @ramakantshinde7348
    @ramakantshinde7348 ปีที่แล้ว

    नमस्कार, भाईसाब इसतऱ्हका (पेटेन्ट डिझाईन )थ्री पिन प्लग कहा मिल सकते है |धन्यवाद.

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      इलेक्ट्रिकल शॉप से ​​थ्री पिन प्लग और इलेक्ट्रॉनिक पार्ट्स शॉप से ​​वैरिस्टर

  • @amsiyal
    @amsiyal 2 ปีที่แล้ว

    Little bit confused on varistor connection... 1p would be after fuse.. I mean on Load side....???

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว

      Yes, on load side. Upper side of fuse to load wire down side to wall plug

  • @nelsonudeh4473
    @nelsonudeh4473 3 ปีที่แล้ว

    Can I connect the varistor legs any how or so there a polarity I must follow?

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว +1

      no polarity

    • @nelsonudeh4473
      @nelsonudeh4473 3 ปีที่แล้ว

      @@TARIQLAB please can I use varistor 10471U?

    • @nelsonudeh4473
      @nelsonudeh4473 3 ปีที่แล้ว

      @@TARIQLAB thanks

  • @V98000
    @V98000 ปีที่แล้ว

    Value of MOV for mainline/whole house protection?
    14D or 20D ?

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว +2

      20D is better

    • @hartonoaji6574
      @hartonoaji6574 ปีที่แล้ว

      @@TARIQLAB berapa tegangan breakdown 20D mas broo

  • @muhammadfirdaussebeli1263
    @muhammadfirdaussebeli1263 3 ปีที่แล้ว

    Any different put varystor before fuse or after fuse?

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว +4

      After fuse, because when over voltage fuse will cutoff current otherwise varistor will blast

    • @florind.5711
      @florind.5711 2 ปีที่แล้ว

      Bettee the fuse to be filled with sand/ or with ceramic walls instead of clear glass

  • @zubairmalik7062
    @zubairmalik7062 2 ปีที่แล้ว

    How I can use in splite ac unit 1.5 ton
    Plz mentioned fig : of varistor
    Iam waiting ur rply

  • @tehniathali2285
    @tehniathali2285 3 ปีที่แล้ว +1

    Salaam Bhai,
    I am college student (Commerce) and had experienced burning of new Dell Laptop Charger-Adapter. I can't carry the heavy UPS with Laptop! Here are my queries:-
    -
    Q1) Is Spike Buster also called Surge Protector? If not, can't we have both in one Plug?
    -
    Q2) For protecting Laptops, the maximum AC Voltage is 240V because the Charger-Adapters are rated from AC 110-240V. So which MOV should I buy for protecting the Charger-Adapter?
    -
    Q3) I am confused! Should I consider 220V or 230V or 240V for the safety of the Adapter? Accordingly, what would be the MOV designation?
    -
    Q4) Alternatively, why not use step-down transformer to limit the AC Voltage to 150 or 200? Because one has to replace the burnt-out MOV in your idea!
    -
    Q5) Next Alternative is to make auto-Spike Buster with setting of 200 V AC! In the market, this is available for R1400/-. But it is set at 240 V. It auto-disconnects at a 240 V and auto-reconnects after the voltage reduces without the effort of replacing the burnt-out MOV? Can we make it at home with the max Voltage set at 200V?

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว

      MOV can be fixed inside a plug or charger,
      step down transformer is not a good choice, if input 240 out put 200 , if input voltage spike 440 then output around 400, mass of transformer & heat is another issue.14D391k is best. will give protection above 250 v ac

  • @shankarnathmajumder
    @shankarnathmajumder 4 ปีที่แล้ว +1

    Nice Trick...! 🤔
    👍🏻👍🏻👍🏻👍🏻👍🏻

  • @najirulislam3444
    @najirulislam3444 2 ปีที่แล้ว

    Can I use the same MOV for a high end PC (825~w)?

  • @noumaanansari7279
    @noumaanansari7279 ปีที่แล้ว

    Sir Baar Baar Laptop ka charger kharab ho raha hai Konsa Mov aur fuse lagana sahi raheyga
    Charger Input 100-240V hai 1.5A

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      Over voltage aty hain

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      Ups tu nahi laga ghar main

    • @noumaanansari7279
      @noumaanansari7279 ปีที่แล้ว

      @@TARIQLAB Nahi Laga

    • @noumaanansari7279
      @noumaanansari7279 ปีที่แล้ว

      @@TARIQLAB 240v se zada voltage nhi chahiye aur 1.5A supply hai uske liye konsa Varistor aur fuse lagau

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      Fuse 2A, varistor 7d471

  • @kabandajamir9844
    @kabandajamir9844 ปีที่แล้ว

    So nice thanks sir

  • @BittuSingh-ul9dh
    @BittuSingh-ul9dh 9 หลายเดือนก่อน

    kitne voltage anne per ye fuse short hoga

    • @TARIQLAB
      @TARIQLAB  9 หลายเดือนก่อน +1

      270-280v

    • @BittuSingh-ul9dh
      @BittuSingh-ul9dh 9 หลายเดือนก่อน

      @@TARIQLAB but itna per to jo product laga o v kharb ho jaiyega 255 se jada Indian product save nahi hai like tv .charger

  • @tanveeralam10
    @tanveeralam10 3 ปีที่แล้ว

    What value of varister I can use to protect my 1 HP water pump / motor?

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว +1

      if voltage 220 then use that I mentioned in this video

    • @allinonevlogsbym.k1652
      @allinonevlogsbym.k1652 2 ปีที่แล้ว

      Mujhe 270volt se upar nhi chahie

  • @muhammadarsalankarim1191
    @muhammadarsalankarim1191 3 ปีที่แล้ว

    Whats the difference between fuse and varistors? Both control surges.

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว

      No, fuse burns over amp but varristor shorts when over voltage to protect the device

    • @muhammadarsalankarim1191
      @muhammadarsalankarim1191 3 ปีที่แล้ว

      @@TARIQLAB Thank you for the response. Its appreciable that you follow your comment section.

    • @florind.5711
      @florind.5711 2 ปีที่แล้ว

      Varistor take care of surge/spike in voltage
      Fuse/Breaker take care of surge/spike in CURRENT (intensity or Amperage)

  • @farukhagwan8577
    @farukhagwan8577 ปีที่แล้ว

    20D431k le sakte hai kiya

  • @SomnathDas-ej3ve
    @SomnathDas-ej3ve ปีที่แล้ว

    Fuse toh board mein hai aur kya plug mein is varistor ko join kar do

  • @SachinPatil-yg8ep
    @SachinPatil-yg8ep ปีที่แล้ว

    Spd ki jagah mov lagaskate kya hai

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว +1

      Yes, iss se pehly fuse lagana ho ga

  • @shamimrashed1100
    @shamimrashed1100 2 ปีที่แล้ว

    Good concept

  • @gursharansingh2911
    @gursharansingh2911 3 ปีที่แล้ว

    Hello 👋 sir je 471k maximum ketna voltage tak work karta h

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว +1

      Under 300V AC,

    • @tehniathali2285
      @tehniathali2285 3 ปีที่แล้ว +1

      @@TARIQLAB
      For AC 230V, what would be the MOV designation?
      Should I consider 240V for the safety of the Adapter?

    • @florind.5711
      @florind.5711 2 ปีที่แล้ว

      Better use 20n431k = 20mm diameter 275V AC and 6.5KA rating for 230-240V network

  • @QUINIX_YT
    @QUINIX_YT 3 ปีที่แล้ว +1

    The I want to safely keep Diwali lights that need less volt but more volts come in holder

  • @allinonevlogsbym.k1652
    @allinonevlogsbym.k1652 2 ปีที่แล้ว

    Value of Varistor for ceiling fan ?

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว

      Same

    • @allinonevlogsbym.k1652
      @allinonevlogsbym.k1652 2 ปีที่แล้ว

      @@TARIQLAB please write the value so that I can purchase from Market

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว

      7D471k

  • @keepopenminds
    @keepopenminds 2 ปีที่แล้ว

    Bro will it protect form Low voltage

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว

      No, only high

  • @jendrikojonatan4083
    @jendrikojonatan4083 3 ปีที่แล้ว

    Varistor type for 220 volt electronic device protection???

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว +1

      I mentioned that number in this video

    • @jendrikojonatan4083
      @jendrikojonatan4083 3 ปีที่แล้ว

      @@TARIQLAB I use the S20 300 & 20D561K type. in series, then the middle is connected to ground

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว

      20d561k 230v ac
      20d391k 250v ac is better for 220 volts

    • @florind.5711
      @florind.5711 2 ปีที่แล้ว

      @@TARIQLAB
      561k maybe too higher voltage level
      for 230-240V use 431k = 275V AC

  • @jameelgujar3767
    @jameelgujar3767 4 ปีที่แล้ว

    great job 👍

  • @okyaarhm700
    @okyaarhm700 2 ปีที่แล้ว

    Aesi plug pin kaha milengi?

  • @YourTechBhaiOfficial
    @YourTechBhaiOfficial 4 ปีที่แล้ว

    Where did you get that plug?

    • @TARIQLAB
      @TARIQLAB  4 ปีที่แล้ว

      its not a special plug, I added varistor

    • @santoshchetry3835
      @santoshchetry3835 4 ปีที่แล้ว

      @@TARIQLAB varisator ratio

    • @santoshchetry3835
      @santoshchetry3835 4 ปีที่แล้ว

      @@TARIQLAB varisator ratio

  • @roneditz6173
    @roneditz6173 2 ปีที่แล้ว

    How to calculate the rating of the fuse?

    • @TARIQLAB
      @TARIQLAB  2 ปีที่แล้ว

      Fuse according to load, varistors also have amp rating

  • @abhisekhrai6706
    @abhisekhrai6706 ปีที่แล้ว

    500 watt pc ke liye variaster code

  • @umeshmali5737
    @umeshmali5737 2 ปีที่แล้ว

    लाईव। चालू। करके. 230. V input करके। दीखाऑ डेमो.... vDR. ऑर mov

  • @gauravnaikin
    @gauravnaikin ปีที่แล้ว +1

    This plugs are not used in India...

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      I made another video for 2 pin plug, check my channel

  • @anandtidke378
    @anandtidke378 ปีที่แล้ว

    Sir 250 voltage details

    • @TARIQLAB
      @TARIQLAB  ปีที่แล้ว

      Same will work

  • @rizvanrizzy9534
    @rizvanrizzy9534 3 ปีที่แล้ว

    1 testing video bna layty to kya hota.?

    • @TARIQLAB
      @TARIQLAB  3 ปีที่แล้ว +1

      ok , varistor ki testing video channel pe hai, high voltage ki bhi bana don ga

  • @sotameniualiku2225
    @sotameniualiku2225 8 หลายเดือนก่อน

    Your headline is in English but you speak other language

  • @Mohamed-Alhomsi
    @Mohamed-Alhomsi 4 ปีที่แล้ว

    translate to English plz.

    • @TARIQLAB
      @TARIQLAB  4 ปีที่แล้ว +1

      connect one varistor 10D471K as u can see & protect ur appliances from over voltage, that's all

    • @Mohamed-Alhomsi
      @Mohamed-Alhomsi 4 ปีที่แล้ว

      Can I mount this thing for washing machine and refrigerator
      What is the highest volt that can pass?

    • @TARIQLAB
      @TARIQLAB  4 ปีที่แล้ว

      yes,, if ur line 220 or 240v then u can use this number if 110 or 120 v then another number I will suggest