  • @pmgodfrey
    @pmgodfrey 3 ปีที่แล้ว +85

    Before even starting this video, I'd like to say this. I subscribe to MANY different channels on TH-cam. Some in mechanical engineering, some in electrical engineering. A few other HVAC ones and others that have nothing to do with anything.
    This is, hands down, the channel where I learned the most and I'm not even in the HVAC industry professionally. I do own a bunch of units because I'm a landlord, but this helps me understand the process of what I'm paying for and helps me sometimes troubleshoot a unit. For this I am grateful. My hat is off to you guys both in the classroom and out in the field. Your work is very much appreciated.

    • @HVACS
      @HVACS  3 ปีที่แล้ว +9

      Very kind of you to say. Thanks!

    • @Flowtester1
      @Flowtester1 2 ปีที่แล้ว +2

      What are some good mechanical and electrical engineering channels to subscribe to.

    • @pmgodfrey
      @pmgodfrey 2 ปีที่แล้ว +3

      @@Flowtester1 -- This one, EEVblog, AvE, RODALCO2007, StuffMadeHere, HVACR
      You'll get a mix with those and TH-cam will recommend others based on that criteria.

    • @Flowtester1
      @Flowtester1 2 ปีที่แล้ว +3

      Ok thank you

    • @N3X15
      @N3X15 2 ปีที่แล้ว +3

      @@pmgodfrey HVACR provides a good, practical window into any professional troubleshooting process, as well.

  • @milanlipovic7349
    @milanlipovic7349 3 ปีที่แล้ว +41

    I’m glad you actually care about technicians I’m just starting in the industry and I think all companies should still teach their techs like you do thank you 🙏

    • @lerch400block
      @lerch400block 3 ปีที่แล้ว +3

      They really should hire an instructor vs a sales coach for a change. This is coming from a 19 year tech and rookie instructor.

  • @deanlhouston
    @deanlhouston 3 ปีที่แล้ว +34

    Way back in the day before I went to college and got an engineering degree, my old high school HVAC instructor explained subcooling (and superheating) in a way that a big dummy like myself could understand it. He first explained what sensible and latent heat were: Sensible heat being heat added/removed to change refrigerant temperature and latent heat being heat added/removed to change refrigerant state - and how until a state change is completed the temperature doesn't change.
    Once we understood that concept, subcooling is simply the sensible heat removed after the state change completed (condensed) and superheating is simply sensible heat added after state change completed (evaporated).
    You may have covered that prior to the video, but I found linking those two concepts really helped understand subcooling (and superheating).

    • @roseelectronics4582
      @roseelectronics4582 2 ปีที่แล้ว

      But that doesn't explain the beautiful concept behind subcooling and superheating

    • @raidone7413
      @raidone7413 2 ปีที่แล้ว

      Thanks

    • @bradjohnson2649
      @bradjohnson2649 ปีที่แล้ว

      Thank you for simplifying this concept. Sometimes we overcomplicate the process. 😀

    • @bradjohnson2649
      @bradjohnson2649 ปีที่แล้ว

      Thank you for simplifying this concept. Sometimes we overcomplicate the process.

    • @deanlhouston
      @deanlhouston ปีที่แล้ว

      @@roseelectronics4582 But that IS the concept of subcooling/superheating. Now I think the concept you're getting at is "why its measured?"
      I just found it helpful when my instructor separated what superheating/subcooling IS from why its measured in AC/Refrig. Building blocks to understanding the bigger picture.

  • @asweetdealfleamarketstore8889
    @asweetdealfleamarketstore8889 9 หลายเดือนก่อน +1

    Heres a respectable thought, this teacher has been awake loner than the whole class, and is probably the most tired, nevertheless he came punctual, provided a wealth of information. Kept the class awake, sought a challenging question. Taught himself in the process, extinguished questions and alleviated concerns, provided reassurance and implanted confidence. Thumbs up to you for going back home tired..

  • @larryproffitt4729
    @larryproffitt4729 3 ปีที่แล้ว +8

    Been in the field for many years and the way you explained subcool was simple, easy to understand and spot on. A excellent video. Wish I had you as a teacher back then.

  • @SovereignTroll
    @SovereignTroll 3 ปีที่แล้ว +14

    Finally a perfect statement. Stacking refrigerant. In engineering we would be "storing" the excess refrigerant.

  • @Stuart68505
    @Stuart68505 2 ปีที่แล้ว +5

    Low amount of subcooling can result from a lack of cooling by the condensing unit for many different reasons. (poor air flow, bad fan bearings, dirty condenser, unit surrounded by walls that are too close or vegetation, undersized condenser, low line voltage due to utility stress, damaged fan blades not moving enough air & other factors). So having insufficient sub cooling does not necessarily mean that more refrigerant needs to be added to the system. As I got near the end of this video, I realized that you did mention inspecting the equipment for cleanliness before analyzing sub-cooling. this video was very helpful with it’s in-depth discussion of sub-cooling. Thank you for helping me to get clearer on this topic.

  • @NestorHVAC
    @NestorHVAC 3 ปีที่แล้ว +11

    Man I would love to be in that classroom!!!
    Keep the videos coming!!!

  • @P9rkour90
    @P9rkour90 ปีที่แล้ว +2

    I’m so glad I’m going to this hands on HVAC school. In my opinion, for me, I learn best hands on rather than reading through a book. Granted, the Schematics on the ac units help with wiring, nothings better than hands on learning. With that said, great video and you seem to be a great instructor!

  • @ronnies779
    @ronnies779 3 ปีที่แล้ว +2

    Your "approach" and logical explanations are by far the best I have ever come across.
    There is no reason your technicians should not all be experts in there field and because I don't hear many questions in your presentations, I would assume they all are.
    You leave little room for discovery by removing the mystery. This is what makes your presentations so valuable and is a rarity.
    I will definitely continue to watch your videos.
    Thank you!
    " Advancements are made by answering questions. Discoveries are made by questioning answers."

  • @jeffreyrex8232
    @jeffreyrex8232 3 ปีที่แล้ว +3

    Just sent this to the apprentice. Told him to subscribe to this channel for much learning 👍🏻
    Clear and concise. Doff my cap to you sir.

  • @hvacservicementor
    @hvacservicementor 3 ปีที่แล้ว +9

    This is super cool (see what I did there?) I have always thought of sub cooled liquid filling the condenser tube rows and stacking on top of one another. Never heard anyone else describe it like this. Bravo!

    • @peterstencell804
      @peterstencell804 3 ปีที่แล้ว

      You are still fight . As lone as you under stand who cares .

  • @bawlout9367
    @bawlout9367 ปีที่แล้ว

    this video was a god send along with the superheat video you guys put out. WHAT REALLY HELPED was the 3d models of the entire system running

  • @manuelyberegaytan2068
    @manuelyberegaytan2068 ปีที่แล้ว

    I've been working in refrigeration for about 7 yrs. This video is awesome because I never went to tech school. I work Low-Temp and Racks... Also any Hot-side equipment that comes my way... Keep up the good work guys

  • @jameswasher3938
    @jameswasher3938 ปีที่แล้ว

    All of these sessions are SO VERY GOOD!

  • @maxclark11
    @maxclark11 2 ปีที่แล้ว

    An amazingly simple concept made amazingly complex in this video.

  • @miltonbradley4249
    @miltonbradley4249 ปีที่แล้ว

    All your teachings are are great we'll done and to the point. As an engineer I love your style it flows with thousands of hours of experience and wisdom in your teachings

  • @mikelain13
    @mikelain13 3 ปีที่แล้ว +5

    Wish my previous employer took the time to train me like this. Thank you for the lesson.

    • @bikerbobcat
      @bikerbobcat 3 ปีที่แล้ว

      Same. The techs and I ask for it all the time (especially for installers to save us embarrassing install warranty callbacks) and it just doesn't happen. The "cost" of education clearly rolls downhill, too.

    • @f1reguy587
      @f1reguy587 3 ปีที่แล้ว +2

      I’m finding the employers education bad here too, it’s like it’s protected information...that or he doesn’t wanna be superseded... however the refrigeration side is less complicated over the huge amount of electronic knowledge needed...

  • @mropie428
    @mropie428 2 ปีที่แล้ว +1

    Thank you for the videos and all the knowledge that you have given all of us

  • @sterlingarcher46
    @sterlingarcher46 3 ปีที่แล้ว +1

    Bryan this new series of videos are fantastic mate , keep up the good work 👍

  • @acrepairnearme
    @acrepairnearme 3 ปีที่แล้ว +3

    Great video lesson.

  • @EdgarMartinez-ks1yl
    @EdgarMartinez-ks1yl 3 ปีที่แล้ว +3

    Very informative, thank you

  • @michaelcostello6991
    @michaelcostello6991 3 ปีที่แล้ว

    Interesting discussion. Thank you.

  • @6057noel
    @6057noel 3 ปีที่แล้ว

    I like this channel. Very educative. Explained in detail.

  • @mdelgado6080
    @mdelgado6080 3 ปีที่แล้ว +3

    Awesome video great refresher

  • @AJISFREAKENAWESOME
    @AJISFREAKENAWESOME 2 ปีที่แล้ว +1

    Man I would love to be in this classroom. I’m in the automotive industry. Managing now, but I’m so interested in every other industry and this classroom just seems like a pool of knowledge. Maybe one day.

  • @ronie1337
    @ronie1337 18 วันที่ผ่านมา

    Bryan, Thanks for the info.

  • @hubercats
    @hubercats 2 ปีที่แล้ว

    Another excellent video. Thank you!

  • @gregscheyd4131
    @gregscheyd4131 ปีที่แล้ว

    VERY VERY COOL EXPLANATION , BRYAN !!!!! THANKS IMMENSELY !!!!! IM NOT AN HVAC TECH OR APPRENTICE , NOR WILL I EVER BE . I M 65 , I LIKE TO DRINK COFFE AND BEER , AND LEARN,ABOUT EVERYTHING TRADE AND TECHNICAL THAT MAY GO WRONG WITH MY WIFE'S AND MY HOUSE ..... the way I figure , you should not own ANYTHING you do not understand and BASICALLY KNOW HOW TO FIX !!!!!! ....to that end , you helped me alot : thanks again ......

  • @wmdayman
    @wmdayman 3 ปีที่แล้ว

    Fantastic explanation

  • @gregs9555
    @gregs9555 2 ปีที่แล้ว

    Good presentation, thanks!

  • @nickthadon9894
    @nickthadon9894 3 ปีที่แล้ว +3

    1 thing you should of added is checking delta T to make sure getting target temps thank for making these vids

  • @MECENGINEERS
    @MECENGINEERS 2 ปีที่แล้ว

    very good explanation of the topic.. kindly make a video explaining the copper piping when the indoor and out door units are at different elevations.
    Thanks

  • @nyimachoenyi4997
    @nyimachoenyi4997 2 ปีที่แล้ว

    Great video !! Thanks for sharing.

  • @joseramonherreramendoza9260
    @joseramonherreramendoza9260 3 ปีที่แล้ว +1

    Thank you so much for such a great info... keep it up...

  • @willllo
    @willllo ปีที่แล้ว

    Obviously this could just be 1 school but if this is how well this is taught in the US its insane to me. My qualification in the UK was just that, a peice of paper. I learned absolutley everything on the tools from very good technicians as an apprentice. School was Brazing, Elthrapy diagram, leak test, Charging to the specified charge weight through a rig. That's it. Wild how so simply you cover the depth of this so it's understandable to guys starting out. Took me a couple years on the tools with guys in practice to learn a lot of what you explain in your videos which should have been taught in school. I'm lucky too because most don't have decent techs teaching them at work.

  • @jeffreyrex8232
    @jeffreyrex8232 3 ปีที่แล้ว +4

    Ahhh RTFM! Always my first port of call when speaking with other tech’s 😉

  • @scott5654
    @scott5654 3 ปีที่แล้ว +2

    Excellent ‼️

  • @ATeamAdam
    @ATeamAdam ปีที่แล้ว

    Great lesson

  • @efrainfajardo8360
    @efrainfajardo8360 ปีที่แล้ว

    Good information,thank you.

  • @hhn2002
    @hhn2002 2 ปีที่แล้ว

    enjoyable to watch. thanks.

  • @DaGenius86
    @DaGenius86 8 หลายเดือนก่อน

    Excellent. Thanks

  • @craigspicer4296
    @craigspicer4296 2 ปีที่แล้ว

    Oh the the days at Tafe Tech collage lol. Love the delivery lol.

  • @HughesManHVAC
    @HughesManHVAC 2 ปีที่แล้ว

    Great video

  • @jbaker8871
    @jbaker8871 2 ปีที่แล้ว

    Really great class. Im interested on your approach vrs ambient rule of thumb. Could you go more in depth. Also mid and low temp would be great to hear. My weakness and what i hear is not consistent.

  • @robertmyers6859
    @robertmyers6859 2 ปีที่แล้ว

    GREAT JOB

  • @donnierobertson3088
    @donnierobertson3088 3 ปีที่แล้ว

    Nice job and video

  • @Suicaedere666
    @Suicaedere666 9 หลายเดือนก่อน

    Thank you B-Orr⚡️

  • @jamesmooney5348
    @jamesmooney5348 ปีที่แล้ว +1

    Thanks

  • @ryanduhaime9086
    @ryanduhaime9086 2 ปีที่แล้ว

    Hi Brian. On a new install (ac). My sub cooling was low (4) and had 0 superheat with a adjustable txt. Should I have added refrigerant to correct my sub cooling first, and then adjust the txt to correct superheat. I wasn’t sure to I ended up doing both a little at a time but curious what you would have done. Thanks best videos out there

  • @D2DNYAC
    @D2DNYAC 2 ปีที่แล้ว

    Good video thank you I like the + 4 degrees to outdoor ambient rule of thumb for liquid line temperatures, I will be experimenting with that 🤔.. so
    In summary what youa are saying is to gain more sub you need to finish condensing earlier and to loose sub finsh later?

  • @Garth2011
    @Garth2011 8 หลายเดือนก่อน

    This is also a good reason for manufacturers to make high quality data plates that will not fade or oxidize etc. over a 20+ year period of time. We have seen many of them that have faded or were losing all of their "font" paint or the like and the data is not legible without having it "x rayed" with methods to restore what was printed or etched on those data plates.

  • @mohammadqamar1854
    @mohammadqamar1854 ปีที่แล้ว

    Thanks sir

  • @zyxnix
    @zyxnix ปีที่แล้ว

    Good stuff. Gotta recheck my system. Hope I did'nt over charge it. 🙂

  • @thunnasalbako6095
    @thunnasalbako6095 2 ปีที่แล้ว

    Very informative. And I would like to ask could you please show me how to measure the sub cooling and super heating in practically? And please let me know if it's possible to apply on the freezer which is set for minus 18degree Celsius and how I could apply or doing that? Hope I can get positive answer
    Thank you very much for you kinds information Once again

  • @teeteewasherwhirlpool9156
    @teeteewasherwhirlpool9156 ปีที่แล้ว

    Hi Bryan,so I work in a place that has some of the condenser unit sits in a confine concrete wall area,and usually has 3 to 6 condenser and roughly 6" to 10" apart from each ither and majority of them has only a inch from concrete wall.so when it gets 106° outside temperature, the temperature around these condenser units climb up to 118°. So my question is,because of ambient temperature so high,will a subcooling on my condenser change? And if it is,what can I do or what is the best way to solve the high readings on my high side pressure? I appreciate the videos and an answer..have a bless day..

  • @shahzadyousaf110
    @shahzadyousaf110 ปีที่แล้ว

    Hi, Is there a way to find the Saturation pressure inside the evaporator with the air side information? like the indoor temperature and the CFM information?

  • @logzz6373
    @logzz6373 2 ปีที่แล้ว

    Thanks 💪🏾

  • @asweetdealfleamarketstore8889
    @asweetdealfleamarketstore8889 9 หลายเดือนก่อน

    Ok 1:54-1:55, look at his eyes drop in the empty answers. 😅 good morning 😂

  • @tmst2199
    @tmst2199 2 ปีที่แล้ว +3

    I would have loved to be in Orr's class when he asked "How do you measure subcooling?" Uh, with a thermometer?

  • @ltherealist3729
    @ltherealist3729 2 ปีที่แล้ว +1

    I had a condo in the wall box unit with all the temps and pressure looking good but the sub cooling stayed around 1 with a TXV inside a aqua therm air handler and only had about 12 degrees Detla T.
    I couldn't figure out why.🤷🏾‍♂️

  • @markspazianijr1143
    @markspazianijr1143 ปีที่แล้ว

    What should subcooling be for a Pentair Ultratemp 120 pool heat pump?

  • @jaymanuel4126
    @jaymanuel4126 2 ปีที่แล้ว

    Good day sir, im jay from the Philippines, is there a minimum and maximum range for superheat and subcool? I will use for troubleshooting.. thank you sir..

  • @thetruthserum2816
    @thetruthserum2816 ปีที่แล้ว

    If you had an IR thermal camera, would you be able to see the liquid stacking in the condenser coils?

  • @RP-mt6bp
    @RP-mt6bp ปีที่แล้ว

    How do you use the Clausius-Clapeyron equation to calculate the saturation pressure?

  • @milanlipovic7349
    @milanlipovic7349 3 ปีที่แล้ว

    When are you going to add line set to the app?

  • @kasranoor613
    @kasranoor613 2 ปีที่แล้ว

    can receiver affect on subcooling temp, do we set subcool differently with a system that has a receiver, how do we adust subcool in water-cooled condenser? would approach temp to be different with water-cooled condenser compared to air-cooled one?

  • @seek3n
    @seek3n 9 หลายเดือนก่อน

    I hvnt seen a factory installed head pressure service valve. And when I add undercharged refrigerant the liquid line pressure will always go up along with approach temperature from negative to positive. I always go with subcool superheat and ctoa. Please help!

  • @jollyscaria1922
    @jollyscaria1922 2 ปีที่แล้ว

    Vrey good explaning thankyou gues shering welcome gues guied gues

  • @marcoselgaucho1106
    @marcoselgaucho1106 2 ปีที่แล้ว

    Your voice when you said i don’t remember numbers🤣🤣🤣

  • @Garth2011
    @Garth2011 8 หลายเดือนก่อน

    This may be a reason why newer condensers are so large/big as to stack refrigerant with lots of condensing room plus slower fan speeds will do the same work as the faster speeds had.

  • @brianthomas736
    @brianthomas736 3 ปีที่แล้ว

    What app? Info please
    I’ve been in the field for 32 years, while some of this content is elementary, i still learn something every time, or at least I’m reminded of stuff i forgot. Great stuff

    • @davejohnsonnola7908
      @davejohnsonnola7908 3 ปีที่แล้ว

      HVAC School app.
      Tech tips.
      Podcasts.
      Videos.
      Calculators and more.

  • @texture6
    @texture6 2 ปีที่แล้ว

    The compressor compresses vapor gas refrigerant and an overcharged system (condenser) results in high head pressure and reduces the amount of work the system can perform.
    Because of compression, a saturation compression instead of a vapor gas compression.

  • @alklapaxida850
    @alklapaxida850 2 ปีที่แล้ว

    gona check that with a flir on the condensor coil ..

  • @kingjiren3681
    @kingjiren3681 ปีที่แล้ว

    Sir does this apply to like r290 equipment

  • @bardia8225
    @bardia8225 ปีที่แล้ว

    Please help me understand how subcooling is done? I know the purpose of subcooling and i have a decent understanding of thermodynamics but no one ever mentions how the subcooling is done practically. Is it basically by manipulating the pressure slightly to ensure that the refrigerent is sufficiently "cooled"? So that the pressure increases slightly after the liquid passes the condenser to ensure that the refrigerent is below the saturation level? or is it simply by dimensioning the system in a way that the saturation temperature of the refrigerent is lower than the ambient temperature?? I know how subcooling and superheating is done in a turbine because there we can actually mnipulate the high temperature and low temperature sink, but in refrigeration cycle, we can only play with the pressure so no one really explains how subcooling and superheating is actually done?

  • @bretwalley4673
    @bretwalley4673 2 ปีที่แล้ว

    I measure subcooling and superheat with a testo 550.

  • @christophersmith4850
    @christophersmith4850 3 ปีที่แล้ว +2

    How does low outdoor ambient conditions affect subcooling? I'm imagining a situation where the load at the evap stays consistent (like a server room), but the outdoor ambient is low that day and a PSC motor is, more or less, moving the same amount of air over the condenser.

    • @hvacservicementor
      @hvacservicementor 3 ปีที่แล้ว +7

      Subcooling remains remarkably consistent throughout the fairly wide range of outdoor ambient the unit is rated to operate within. Server room units will have liquid receivers and head pressure controls which behave a little differently than a standard residential AC.

    • @peterstencell804
      @peterstencell804 3 ปีที่แล้ว +4

      That guy summed it up very well.

  • @YourActualMother
    @YourActualMother 2 ปีที่แล้ว

    I CAN'T BREATHE!!!! lmfao, the face 8:30

  • @masterhvac4734
    @masterhvac4734 2 ปีที่แล้ว

    good

  • @edyburkay
    @edyburkay 2 ปีที่แล้ว

    14:00 """Subcooling is a differential number between Tci-Tco "" .
    Subcooling is not the differential between condenser inlet and outlet, it is the differential of Tsat-Toutlet. Am I getting something wrong here or did theacher just explain it wrong?
    Thanx in advance.

  • @thermocoolofficials6499
    @thermocoolofficials6499 ปีที่แล้ว

    Hi Sir.Please advice.Why my sytem with 410a refigerant in it. The discharge pressure is 410 psi but the suction pressire is 70 psi only that if normal should be around 100 psi.

    • @davidb2438
      @davidb2438 ปีที่แล้ว

      Sounds like liquid line restriction

  • @jorgecolon6705
    @jorgecolon6705 29 วันที่ผ่านมา

    If subcool is the way to go then why does a piston rely on superheat charge method & txv rely on subcool?

  • @burnardhayes8995
    @burnardhayes8995 2 ปีที่แล้ว +2

    How can I join the class and would I get a certificate when done

    • @JP-zz5rm
      @JP-zz5rm 2 ปีที่แล้ว

      It’s a program , you would have to complete the entire program to actually receive the HVAC certificate and you would have to study and take the EPA test ( 100 questions total ). My program was 10 months long , M-F 5pm-10pm.

  • @Ivan-qq6dj
    @Ivan-qq6dj 3 ปีที่แล้ว +2

    Question, why AC BLOWER IS SPIN8NG THE OPPOSITE WAY. changing cap, won't spin the proper way,can reversing shaft will correct it,or reversing wires. Need a opinion,please kindly. Thank you for your help, have a blessed day

    • @larkhill2119
      @larkhill2119 2 ปีที่แล้ว +2

      Have you checked the fan is on the correct way? single phase motor or multi phase. Also if the motor was ever disassembled was the coil replaced the same way as before?

    • @paulmorrow8372
      @paulmorrow8372 2 ปีที่แล้ว

      The cap has two wires on it. If these are reversed the fan will run backwards

    • @larkhill2119
      @larkhill2119 2 ปีที่แล้ว +1

      @@paulmorrow8372 Not sure why you think that will work? start and run capacitors do not care which way round they are connected. However worth adding check the circuit because if its wrong the capacitor can hold full charge and it bites take care.

    • @tomoliver8498
      @tomoliver8498 2 ปีที่แล้ว +1

      I ran across motor spinning the wrong way on 2 different heatcraft motors new out of the box. I replaced them however I believe the wires in the motor were reversed specifically the wire that goes to the capacitor and the line wire that the capacitor gets power from because reversing those two wires changes direction of rotation.

  • @DWAYNE2ism
    @DWAYNE2ism 2 ปีที่แล้ว

    adding a heat exchanger to a system will add to system efficiency?

    • @thealeons3179
      @thealeons3179 ปีที่แล้ว

      I work on low temperature Chillers. We run a sub cooler on the liquid line after the condenser. This is typically a brace plate heat exchanger. It has a TXV on it, so it acts like an evaporator. The liquid line refrigerant runs through the sub cooler heat exchanger and is pre-cooled before it gets to the main TXV or metering device. This will allow you to run a much colder evaporator temperature. In some cases all the way down to -80 F

  • @jamesfitzsimmons381
    @jamesfitzsimmons381 ปีที่แล้ว

    Would had loved to have worked for you Bryan

  • @nunyabusiness6746
    @nunyabusiness6746 2 ปีที่แล้ว +1

    Did I hear him say digital manifold ? This guy seems like he knows his stuff but as an old timer I personally have to comment on some of the advantages of good old fashioned analog equipment, like the PT is right there on your gauges, no need to have to study an instruction manual to learn how to use the thing, and more importantly, watching that needle is good a real time indication of system operation, for example a pulsating needle can indicate a sticking valve in your compressor which no digital meter can show, same goes for your clamp amp, and most importantly I have still have money for a12 pack, the only digital I like is my Fluke 12 voltmeter which has an excellent Cap. checking function, i’m just hoping the thing lives longer than me because it’s no longer replaceable.

  • @sotistudent3759
    @sotistudent3759 3 ปีที่แล้ว

    teacher is a funny guy

  • @kingjiren3681
    @kingjiren3681 ปีที่แล้ว

    They ask for like 4ozs in some system's that I would use a lot more that that if I would use 134 or 404

  • @habibhoward7159
    @habibhoward7159 2 ปีที่แล้ว

    Lmao everyone is still sleep....hi from lehigh valley Pennsylvania! Just started my own company after 8 years working for someone
    ......man the freedom is so good

    • @Respect.The.Grind..
      @Respect.The.Grind.. ปีที่แล้ว

      I’m from the valley , been doing hvac in Washington state the past two years. I’ll come install for ya when I move back

  • @rafaeljaquez9214
    @rafaeljaquez9214 3 ปีที่แล้ว

    I think if you were my instructor when I went to school I would have had a better understanding

    • @davejohnsonnola7908
      @davejohnsonnola7908 3 ปีที่แล้ว

      If my instructor had been half as good, I might have gone into the field 25 years earlier.
      Now playing catch up.

  • @justinperry68
    @justinperry68 2 ปีที่แล้ว

    How do you check sub cooling on a ductless? When only one port? Say in Ac

  • @YouTubeChannel2000
    @YouTubeChannel2000 2 ปีที่แล้ว

    👍👍👍👍👍👍👍

  • @timbunner8855
    @timbunner8855 2 ปีที่แล้ว

    Saturation is when all the liquid in the evaporator has change state from a liquid to a vapor. Condensing is when all the gas has condensed to a liquid in the condenser coil. There is no saturation process taking place in the condenser coil is condensing.

  • @gerardorodriguez-uf9rx
    @gerardorodriguez-uf9rx 3 ปีที่แล้ว +1

    Paul Folin 😆

  • @Mitch2294
    @Mitch2294 2 ปีที่แล้ว

    Sounds like the answers to the questions were added in after the fact lol

  • @BaronVonSTFU
    @BaronVonSTFU 3 ปีที่แล้ว +2

    With it being 0 degrees out, my rack condenser is stacking A LOT of refrigerant. Like all of it....

    • @peterstencell804
      @peterstencell804 3 ปีที่แล้ว

      It must have a head master on it 😉 that's there job.

  • @TonyGioMusic
    @TonyGioMusic 3 ปีที่แล้ว +3

    I also prefer to yeet the refrigerant into a new system.

  • @nickmerc9299
    @nickmerc9299 3 ปีที่แล้ว

    I installed a brand new unit and check the sub oil and it was steady at 0 degrees of sub cooling I then added Refrig and the sub cooling started to jump around. Any suggestions

    • @scofield3021
      @scofield3021 2 ปีที่แล้ว

      Purge the air out of your gauges?