Level Measurement using DP Transmitter Part 2 - Position Zero Adjustment

แชร์
ฝัง
  • เผยแพร่เมื่อ 2 ต.ค. 2024

ความคิดเห็น • 20

  • @hudzaifahhazazi2969
    @hudzaifahhazazi2969 22 วันที่ผ่านมา

    what about we placed transmitter at NV2, so the pipe get lower first after tapping then get high again. whats the calculation?

  • @abderazakbensmail7164
    @abderazakbensmail7164 5 หลายเดือนก่อน

    actual dp in this case ( dry leg) is not zero without opening the equalizer valve !!! sg1*h2 can't be equal to sg2*h3, isn't it? other thing i think that BV2 should be open too so that the LP measure cell will be communicating with the empty part of the tank that may be little bit pressurized above the atmosphiric pressure.

  • @sikanfuncreation4613
    @sikanfuncreation4613 2 ปีที่แล้ว +3

    Well done 👍

  • @SKSivalogam
    @SKSivalogam 2 ปีที่แล้ว +1

    Super... Clear explanation...

  • @jamesinocencio8005
    @jamesinocencio8005 2 ปีที่แล้ว +1

    Nice, but you dont have to open equalizer to make the water flow to the DPT, after the opening the block valve the water directly flows to DPT, the equalizer valve position om the middle of the passage through the block valve 1and 2, but not blocking the passage through the DPT diaphragm.
    BV1 BV2
    | |
    |__________EQ__________|
    | |
    | |
    DPT
    and also if you are zeroing a DPT you have to eliminate every pressure to the DPT, or open the equalizer to balance the pressure exerted on the diaphragm.

    • @jamesinocencio8005
      @jamesinocencio8005 2 ปีที่แล้ว

      BV1 BV2
      | |
      |__________EQ__________|
      | |
      | |
      DPT

    • @KickStartInstrumentation
      @KickStartInstrumentation  2 ปีที่แล้ว

      Noted your point. It will be included clearly for better understanding asap.

    • @riturajrobmorang5982
      @riturajrobmorang5982 2 ปีที่แล้ว

      Good point out @james .. 1st part as well as the later zeroing part.. but in the later part he was adjusting the zero level (as per process c-c distance + tubings to the DPT) and not the transmitter zero. This i would tell you has to be followed even with your dry/ wet calculations of the lrv. Good video keep it up. and also a very constructive comment from james

  • @vikrantpandey5279
    @vikrantpandey5279 2 ปีที่แล้ว +1

    Such an extraordinary presentation

  • @ajibolafolaniran6999
    @ajibolafolaniran6999 ปีที่แล้ว

    Good job

  • @gauthamg6982
    @gauthamg6982 2 ปีที่แล้ว +1

    Well explanation👍

  • @gowthamkt1006
    @gowthamkt1006 2 ปีที่แล้ว +1

    Superb annaaa👏🏻

  • @dineshbabunagarajan1635
    @dineshbabunagarajan1635 2 ปีที่แล้ว +1