How To Add A Light Switch Off An Outlet - EASY Tutorial STEP BY STEP

แชร์
ฝัง
  • เผยแพร่เมื่อ 9 ก.พ. 2025

ความคิดเห็น • 273

  • @TheExcellentLaborer
    @TheExcellentLaborer  3 ปีที่แล้ว +22

    Hey Team! I like wearing black shirts but boy does it show the saw dust 😂. I placed timestamps below 👇to help you navigate this video. Good luck with your projects!
    New construction vs old construction 02:20
    Safety first 03:33
    How to replace an outlet box 04:09
    How to run wire from outlet to switch 07:25
    How to wire an outlet 09:32
    How to set a switch box 13:44
    How to wire a switch box 16:27
    Final walk through 19:56

    • @johnnydez5481
      @johnnydez5481 2 ปีที่แล้ว

      Tt6

    • @richardwhite6702
      @richardwhite6702 2 ปีที่แล้ว

      I'm stealing power from a receptacle to feed 2 LED lights... I went from the receptacle up to the first light, then to the 2nd light, then to the switch... I'm not sure if the switch is faulty because I have constant power to the light now and the motion sensor/dimmer switch won't turn the light off and the lights are constantly on now... Should I have went from the receptacle, to the the switch, and then to the the 2 lights instead? Does it matter what order?

    • @davidicousgregorian
      @davidicousgregorian 2 ปีที่แล้ว

      @@richardwhite6702 yes receptacle to switch to joint lights and dimmers will work then
      but now its wrong by your decription
      unless you sent a 14/3 wire to both lights and dimmer switch from receptacle and in that case use the white nuetral from receptacle to lights and switch , and send power from black wire in receptacle and pigtail the black to power pigtail black to bypass lights straight to switch and leave red wirenutted away from receptacle (dont attach red to receptacle ) and tie red to lights and use red as switchleg silver screw from dimmer to lights then tie black onto switch for power and tie neutral white wire to switch if it is a lighted dimmer or if dimmer requires neutral and tie grounds to receptacle and switch and lights (if lights have ground screw)

    • @juanjuarez6703
      @juanjuarez6703 ปีที่แล้ว

      😊😊

  • @alanyoder7629
    @alanyoder7629 2 ปีที่แล้ว +37

    I literally just did this. I’ve wanted a light in the coat closet for 40 years. The electrician who rewired the house refused to do it. Claimed no access. I finally realized the light could be a sconce above the left side of the door and not a ceiling light. I found an outlet in the basement just below the closet to pull the power. Drilled a hole inside the wall from below, ran the wire, and now we have another outlet in the dining room as well as a switched light in the closet. Only took me 44 years to get it, but no point in hurrying. 😊

    • @UrMomsSuperRichEx
      @UrMomsSuperRichEx ปีที่แล้ว +3

      God bless you “young man”, better late than never!

    • @hexZ06
      @hexZ06 ปีที่แล้ว

      Old fart

  • @easttennessee988
    @easttennessee988 ปีที่แล้ว +1

    Thanks!

    • @TheExcellentLaborer
      @TheExcellentLaborer  ปีที่แล้ว

      You’re welcome! Thank you so much for your support. It means a lot. Good luck with your project!

  • @fjohnson8811
    @fjohnson8811 3 ปีที่แล้ว +12

    Very well taught my friend. I was always shaky on wiring for a new light but with your video I was able to install three recessed lights from an outlet. So glad I didn't have to pay an electrician for an easy job.
    Thanks again

    • @tonydurante2821
      @tonydurante2821 2 ปีที่แล้ว

      I have a switch that turns a light off and on. Only 2 wires are on the switch. Can I get power from one of those wires (black) to power a outlet?

  • @easttennessee988
    @easttennessee988 ปีที่แล้ว +4

    Amazing perfect video for me today I am wiring a small office in my basement and need a switch to a light off an outlet this looks totally doable 🤛

  • @mohammedmakba7267
    @mohammedmakba7267 3 ปีที่แล้ว +7

    Thanks for teaching, you are my favorite teacher who explains everything in such a beautiful way that a dumb like me have no problem understanding it, God bless you

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว +1

      I appreciate that Mohammed! I try to explain everything in a simple fashion that everyone can understand. God bless you too!

  • @aussie-travelandtreasurehu7620
    @aussie-travelandtreasurehu7620 3 ปีที่แล้ว +11

    Found your channel by mistake, you have everything I need to know for my basement Reno plus more, glad Canadian code and equipment are very similar. You are freaking awesome, thank you

  • @richardphysician5640
    @richardphysician5640 ปีที่แล้ว +2

    Josh, my man. If I could say I love you long time without it being weird I would like to.
    I just could not get it until I watched your video. Ty.

    • @TheExcellentLaborer
      @TheExcellentLaborer  ปีที่แล้ว +1

      Hey Richard! I am glad to know my video was helpful for you. Be sure to subscribe for more videos to come. Thank you and take care!

  • @hugogarcia7574
    @hugogarcia7574 2 ปีที่แล้ว +5

    This is the third video I watch. I like the detailed way you explain what you do. Thank you!🙂

    • @TheExcellentLaborer
      @TheExcellentLaborer  2 ปีที่แล้ว +1

      Thank you Hugo! I try to add much detail as I can. I appreciate you watching!

  • @carlosportilla7634
    @carlosportilla7634 2 ปีที่แล้ว +2

    Josh! Like the way you makes splanation on your videos 👌👋👋

  • @Raptor-700R
    @Raptor-700R 3 ปีที่แล้ว +3

    Your video came up in my feed. I gave you and shot and boy do i love the way that you explain everything so clear. So yup uou got a new subscriber 😁👍👍

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว

      Excellent! I hope you enjoy the rest of my channel. Thanks a lot for watching and subscribing!

  • @toolsiesampat2737
    @toolsiesampat2737 ปีที่แล้ว +1

    You are doing a great job from your videos I have learned a lot thank you josh

  • @thomasfoster5200
    @thomasfoster5200 2 ปีที่แล้ว +1

    thank you so much my friend you saved me a lot of money with your videos

  • @larrybowers8323
    @larrybowers8323 3 ปีที่แล้ว +3

    The Excellent Laborer (Josh) looks like you got yourself some new work gear! (You need to get sponsored. Companies like Carhartt would be great!) Thanks for keeping the channel going and all your do to teach us to build our own houses and save a ton a money. Respect!

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว +1

      It would be nice to get a sponsor! Thanks a lot Larry. I appreciate it!

  • @yepetoesca
    @yepetoesca 2 ปีที่แล้ว +1

    Finally someone shows the right way!!! Grate job. Thanks

  • @KevinCopenheaver-sh7mv
    @KevinCopenheaver-sh7mv ปีที่แล้ว +1

    Super easy to follow. Thanks for your help.

  • @johnmurphyable
    @johnmurphyable 2 ปีที่แล้ว +1

    These are some of the best construction videos ive seen on you tube!

  • @dewarfamily4862
    @dewarfamily4862 3 ปีที่แล้ว +3

    Your videos have helped me wire my brand new 14x40 shed. Thank you for your help!

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว

      That is awesome! Thanks a lot for watching my channel. Stay tuned!

  • @juancuellar8662
    @juancuellar8662 ปีที่แล้ว +1

    Good explanation, thanks for sharing your experience.

  • @alvinsaulsberry398
    @alvinsaulsberry398 9 หลายเดือนก่อน +1

    Very helpful im learning not to be afraid of doing the work now thanks😊

  • @manuelluna370
    @manuelluna370 2 ปีที่แล้ว +2

    Your video is very informative thank you

    • @TheExcellentLaborer
      @TheExcellentLaborer  2 ปีที่แล้ว

      You are welcome. Thanks for watching. Good luck with your project!

  • @albertramos3808
    @albertramos3808 ปีที่แล้ว +1

    Hey Josh, thank you so much that was a very good video, that is exactly the info I needed to add a light to a room that I built again thank you so much and have a fantastic day..

  • @CivilianDan
    @CivilianDan 3 ปีที่แล้ว +3

    Learned a couple more things I did not know before. Thank you sir.

  • @wx2833
    @wx2833 2 ปีที่แล้ว

    Excellent content; I am wiring up a HVAC Blower Motor that I am using to build a heat collector for my workshop; I had it wired at 120v so it was running at half speed; which I thought would be enough since it ran an entire two story home in my previous HVAC package; but no joy. I have a lot of sensitive compute electronics that generate a lot of heat; So, my A/C guy suggested building a heat collector since 22 BTU's of A/C could not compete and was overpowered by the heat. I never wired up a 220v switch before; mainly just installed outlets, and some four prong, five wire three phase 240v locking outlets. I picked up a Leviton 3032-21 30a - 120/277 two pole switch; and since the draw is so low for the Blower Motor; I plan to piggyback it off a Metered 30a - 240v outlet; so this video was helpful. The reason I wrote this all out; is incase there is something I am overlooking; or something else I need to consider; since the outlet will be metered, ( and also tracks usage ); I can make sure I stay below 80% load to be safe. As a 90% disabled veteran after 25 years of service; I now work from home; to try and help my wife retire, and building personal data processing systems is something I can do; without have to burden anyone else to get the job done. I have to work with what I have left; since I cannot really use my body to create value these days. Thanks again for the straight forward; no nonsense instruction.

  • @designlife4living547
    @designlife4living547 2 ปีที่แล้ว +3

    Excellent work, well explained! Thank you.

    • @TheExcellentLaborer
      @TheExcellentLaborer  2 ปีที่แล้ว +1

      You are welcome. Thanks for the comment!

    • @froylanmunoz8009
      @froylanmunoz8009 2 ปีที่แล้ว

      @@TheExcellentLaborer thank you for excellent job I learned too much with you videos thank you thank you

  • @Tiksunny
    @Tiksunny 2 ปีที่แล้ว

    I found your channel by accident. You are awesome to help me some of the questions on doing the wires in the basement :) thank you so much for your channel

  • @icaptured0862
    @icaptured0862 2 ปีที่แล้ว +2

    Thanks for sharing your talent👍👍

  • @Rick_1337
    @Rick_1337 11 หลายเดือนก่อน

    Perfect video. Gave me the exact info I was looking for.

  • @silvergrizzly316
    @silvergrizzly316 3 ปีที่แล้ว +1

    HEY👋Josh!! This video couldn't have come at a better time, lol. I'm going to add a light socket over a work bench so I can screw in one of those 10,000 lumen paddle lights. I guess just jumping from the last outlet that the rest of the hanging led lights would be the same. Btw, I turn on my shop lights from two switches on the wall. I love your channel my friend and your detailed explanations!!!👍👍
    ☆Jay☆ 😁

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว +1

      Hey Silver Grizzly! It sounds like it will be very easy for you to add a light with that setup. I have not used paddle light before so I will have to do some research on those. Sounds like you have a three-way switch set up in your shop. I’m going to be doing a video in the future on how I do those. I’m glad you are finding value in my channel. Thanks a lot for watching Jay!

  • @keithp115
    @keithp115 2 ปีที่แล้ว +1

    This was the absolute best tutorial for what I have been looking for without exception! New subscriber sir!

    • @TheExcellentLaborer
      @TheExcellentLaborer  2 ปีที่แล้ว +1

      I am glad to hear that. Thanks a lot Keith! Stay tuned for more to come.

    • @26-CJ
      @26-CJ ปีที่แล้ว

      @@TheExcellentLaborerCan I jump out of a 20 amp rated outlet box with 12 wire to another created 2 gang box that will have a 20amp outlet that is controlled by a switch. Both the new switch and outlet are also rated at 20 amps and wire is rated right with 12 gauge.

  • @bobgherardi4392
    @bobgherardi4392 2 ปีที่แล้ว

    This looks to be spelled out simply and understandably. Was about to hire someone. Gonna do it try it myself! Thanks!

  • @michaelclark4704
    @michaelclark4704 2 ปีที่แล้ว

    This is a GREAT video. I've rewired the vast majority of my house, and I read a lot of manuals to ensure that I know what I'm doing: Stanley, Home Depot, Black and Decker, and many others. So I have a good point of comparison. This fellow is GREAT. He clarifies everything very well, and makes safety the first issue. Clear and instructions.
    Well done! One question: Does using 12 with 14 on the same line on a 15 amp service make any difference?

    • @davidroddini1512
      @davidroddini1512 2 ปีที่แล้ว +2

      For 15 amps it is safe to use both.
      The problem is someone else down the road making changes might see the heavier wire and decide to upgrade the breaker to 20 amps without realizing that part of the wiring is not rated for 20 amps.

    • @deadmanswife3625
      @deadmanswife3625 ปีที่แล้ว

      @@davidroddini1512 exactly that is what would be the problem with it : people in the future
      if you believe in such a thing as life after yours😁

  • @jimholloway1785
    @jimholloway1785 2 ปีที่แล้ว +1

    I am enjoying your videos because they are real life situations that people are facing, so it is very informative and enjoyable to me. I have seen an increase of people using Wago style connectors lately but I don't see you using them. I was curious on your thoughts on Wago style connectors over the twist wire connectors and if there is a time to use one over the other? Keep up the great work. Jim

  • @mharris15088
    @mharris15088 2 ปีที่แล้ว +1

    Thanks for that information, and thanks for your honesty.. and making this look easy.. 👀

  • @Gymjb5
    @Gymjb5 9 หลายเดือนก่อน +1

    Thank you , I’m wondering if I can do the same to install a exhaust fan .

    • @TheExcellentLaborer
      @TheExcellentLaborer  9 หลายเดือนก่อน +1

      That should not be a problem for a standard exhaust fan. I hope that helps!

    • @Gymjb5
      @Gymjb5 9 หลายเดือนก่อน

      @@TheExcellentLaborer thank you ,yeah is just a 6” inch wall exhaust fan for my shower ,now is possible for me to use 14-2 just to run the wire to the fan ? Because im running the wire from a old existing outlet,and im sorry about all these questions 🤦🏻‍♂️

  • @CharlesHogan6
    @CharlesHogan6 2 ปีที่แล้ว +1

    Thank you sir! Well done.

  • @weekendhomeprojects
    @weekendhomeprojects 3 ปีที่แล้ว +2

    Great video! I'll be putting lights in a few closets soon so this is very helpful!

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว

      Awesome! This should give you a few pointers for sure. I know this is a new construction job but is definitely relatable for a remodel too. Thanks!

    • @davidicousgregorian
      @davidicousgregorian 2 ปีที่แล้ว

      dont forget closets lights and basement and garages now require fully enclosed bulbed fixtures no closer than 12 inches from clothes and never above shelving ( pullchains and keyless fixtures are now illegal by code even if replacing broken fixtures)

    • @weekendhomeprojects
      @weekendhomeprojects 2 ปีที่แล้ว

      @@davidicousgregorian what about cables recessed puck lights?

    • @davidicousgregorian
      @davidicousgregorian 2 ปีที่แล้ว

      @@weekendhomeprojects i will check do you mean plug in or direct wire from attic or walls to power source

    • @davidicousgregorian
      @davidicousgregorian 2 ปีที่แล้ว

      @@weekendhomeprojects Incandescent luminaires with open or partially open lamps and pendant-type luminaires must not be installed in a clothes closet [410.16(B)].

  • @cubmixit
    @cubmixit 2 หลายเดือนก่อน +1

    Your work is outstanding and Ive followed you for awhile now. Why not become a licensed electrician?

    • @TheExcellentLaborer
      @TheExcellentLaborer  2 หลายเดือนก่อน +1

      @@cubmixit Thank you so much! I also appreciate you watching consistently. That really helps. I might someday I just never had a real reason to. I will always be a builder. Thanks for watching!

  • @jaywildhorsepatterson4432
    @jaywildhorsepatterson4432 ปีที่แล้ว +2

    Thank you

  • @Bobbyboy145
    @Bobbyboy145 2 ปีที่แล้ว +2

    Bravo well explained

  • @Juan_gonzalez_2000
    @Juan_gonzalez_2000 3 ปีที่แล้ว +1

    Nice explanation
    Now I’m going to do some wiring

  • @jeffmykytiuk5642
    @jeffmykytiuk5642 ปีที่แล้ว +3

    I appreciate all the hard work and explanations you put into making your videos. You are one of the best and most thorough teachers whose videos I've watched.

  • @brandonjensen5292
    @brandonjensen5292 3 ปีที่แล้ว +1

    I changed old outlets today for the first time. Your content made it really easy. Thanks

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว

      Hey Brandon! You are welcome. Im glad you see value in my content. Stay tuned for more!

  • @mrkayes1
    @mrkayes1 2 ปีที่แล้ว

    This is what I needed to do my wiring. Good job keep it up.
    I have 2 questions
    1. Can I use wire 14-2 for multiple outlet
    2. Can I connect wire 14-2 and wire 12-2 together.

    • @davidicousgregorian
      @davidicousgregorian 2 ปีที่แล้ว +1

      first get a electrician for help and inspection of work before energizing ,theres alot of safety precautions and things non electricians dont know that vary per city and national electric codes
      now for questions
      1. A 14-2 will supply 1500watts minus 20% for a 15amp circuit max on total circuit and yes you can use more outlets 1 in 1 gang box 2 in 2 gang box etc if all wiring from panel is on same 15amp breaker up to 1200 watts max for continuous use loads like ovens motors etc or 1500 for temp use lighting or receptacles(not always running at same time / and always consider NEC wire fill cubic inch rules.they added rules for grounds and new wire fill rules for everything in or connected to box or lights switches etc.
      dont combine with 12-2 wire ever and a general rule is 14 plugs and or lights combined on a 14-2 circuit max and 8 if all kitchen or bath or garage and exterior gfi protected serviced outlets lights or devices
      Microwaves fridges dishwashers disposals sump pumps dryers and ranges are to be on dedicated single use locations (dont get power from these)
      2. never combine 12-2 with 14-2 unless you want problems with fire unless a qualified electrician helps you (14-2 can be tied with 12-2 if everyone knows what the reasons they can and cant tie together on this id always stick to all same wiring for safety and future repairs and wiring (easy answer is no)

  • @arthurreece9155
    @arthurreece9155 3 ปีที่แล้ว +1

    Thanks awesome love your channel very informative

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว +1

      Hey Arthur! I’m glad you are finding value in my channel. Thanks a lot for watching my videos!

  • @vincedidomenico4406
    @vincedidomenico4406 8 หลายเดือนก่อน

    Awesome! Thank you for the video. I want to do exactly this, but my question is, my cables have black, white, ground, AND a red wire. What do I do with the red??

  • @elliothudsonhudsonhomesott2694
    @elliothudsonhudsonhomesott2694 ปีที่แล้ว

    Great video, thank-you! Drywall taper here - let me know when you need those boxes filled with mud. 👍 🤣

  • @josephlaba6477
    @josephlaba6477 8 วันที่ผ่านมา

    Is the wiring the same if I want to power a ceiling fan with a light through an outlet?

  • @MaMa-qh4dy
    @MaMa-qh4dy 3 ปีที่แล้ว +1

    Excellent. Just subscribed!!!

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว

      Awesome Ma Ma! Let’s build this wonderful TH-cam community!🔨

  • @mississippiboi76
    @mississippiboi76 7 หลายเดือนก่อน

    What a good number for you I’m working on a tiny house and need some advise

  • @runforestrunchainsawcarvin3418
    @runforestrunchainsawcarvin3418 3 ปีที่แล้ว +1

    Well done! Thanks for the tips.

  • @amir990level2
    @amir990level2 ปีที่แล้ว

    excellent Work. if the switch was close to the incoming wire to the first outlet box, what do you recommended ? is it possible to add a junction box first, feed the first outlet box and switch from this new Junction box? in this case we do not need to pigtail the three wires together and feed the Switch from the outlet box.

  • @edwardogomez2919
    @edwardogomez2919 2 ปีที่แล้ว

    Absolutely excellent video sir. Just what I needed. Thanks

  • @veegee3447
    @veegee3447 3 ปีที่แล้ว +1

    Gm josh thank you for sharing. I have question. How do you fix light switch?. when i turn it on the light doesn't come on write away

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว

      Are you saying there is a delay when you turn the light switch on?

  • @dcbiglew
    @dcbiglew ปีที่แล้ว

    Nice and easy to follow. Did you do a follow up showing the final hook ups? Followed everything and want yo make sure that I get the switch and outlet wiring right. Thanks

  • @vaughan6719
    @vaughan6719 2 ปีที่แล้ว

    Great instructions. Very clear

  • @patrickarchuleta9594
    @patrickarchuleta9594 2 ปีที่แล้ว

    God almighty bless you. Your work is second to none simply great may God continue to. Bottom line

  • @tannerc900
    @tannerc900 ปีที่แล้ว

    Could this same application work for an exhaust fan?

  • @jeanfrancois7470
    @jeanfrancois7470 3 ปีที่แล้ว +1

    Thankyou good job

  • @Turk412.73
    @Turk412.73 ปีที่แล้ว

    Great ! Now , I'm outside replacing std outlet w GFCI . From that I want to power a switch to another outside lite , both gfci & switch in 1 metal 2 gang box - will your procedure be right ?

  • @anduanethlopez794
    @anduanethlopez794 2 ปีที่แล้ว +1

    Thanks brother

  • @connorsmith207
    @connorsmith207 2 ปีที่แล้ว

    When wired like this the outlets will have constant power on top and bottom right?

  • @jsubs
    @jsubs 2 ปีที่แล้ว

    Any videos showing how to install a new ceiling light using existing wall switch that controls a wall outlet. Thanks

  • @tweb3282
    @tweb3282 3 ปีที่แล้ว +1

    What do you think about using WAGO connectors? as An upcoming electrician it is being taught in school.

    • @michaeleverest3487
      @michaeleverest3487 3 ปีที่แล้ว

      They make connections faster but over time the conductors can come out. Remember wire is vibrating at 60hz a cycle. They can come loose enough that you lose the circuit, or that enough heat is generated from arcing that you get a small fire in the box or big fire. I've seen it enough times to just keep using wire nuts.

  • @THERE4fabrications
    @THERE4fabrications 3 ปีที่แล้ว +1

    Great video thanks!

  • @rafettelci3300
    @rafettelci3300 หลายเดือนก่อน

    Good job.

  • @AnthonySomes
    @AnthonySomes ปีที่แล้ว

    Could you run a 14-3 from the switch to the light? With the 12-2 coming from the receptacle?

  • @evelio677
    @evelio677 ปีที่แล้ว

    I like how you do that job thanks To share

  • @richardlawrence3137
    @richardlawrence3137 2 ปีที่แล้ว

    I am adding a light switch to my new shed, this video was perfect.

  • @johntherat339
    @johntherat339 3 ปีที่แล้ว

    This is clutch man! I need to power my well pump coming off an outlet and I'd like to be able to turn the pump on and off with a switch. Thanks for the great and timely video.

  • @alexesco1521
    @alexesco1521 ปีที่แล้ว

    Hi I’m an a situation two outlets power from beaker box and wire going to light everything works but when I turn lights off outlet goes off as well?

  • @anikettelang9831
    @anikettelang9831 11 หลายเดือนก่อน

    Will this work for using a light switch to add an outlet in a bathroom?

  • @trailsloth6956
    @trailsloth6956 ปีที่แล้ว

    Do you like the weygos? Or you prefer wire nuts?

  • @weekendhomeprojects
    @weekendhomeprojects 3 ปีที่แล้ว +2

    Social Blade has you at 900k views a month? Whats the RPM on building channels? About 4? So in that case you'd be pulling in about $3,600 a month in ad rev? Awesome job by the way, I ran across your channel early and was like....how does he only have a a few hundred subs, this content is gold.

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว +2

      The channel has really started getting a lot of traction here in the past couple months. I am very thankful for it! If it wasn’t for viewers like you it would not be what it is and I thank you for it! My RPM is higher than that. I have noticed different videos have different RPMs. So it’s hard to give an exact RPM for any building channel because the content RPM varies a fair amount. My channel has always been directed to give people insight on projects. I hope that helps!

  • @khymchristensen1237
    @khymchristensen1237 ปีที่แล้ว

    Is it okay to use a junction box between outlets to wire a switch/light if it's an older house and no outlet to wire into nearby ? And how many outlet/switch/light combinations can be on a 15 amp breaker circuit safely?

  • @StreamFoxiptv
    @StreamFoxiptv 11 หลายเดือนก่อน

    May i ask why did you use the the 2 black wires and ground for the switch and not the black,white and ground?

    • @sargentnocap1414
      @sargentnocap1414 9 หลายเดือนก่อน

      White is your neutral and they always tie together for switches, one of the black wires is power the other one is power out.

    • @StreamFoxiptv
      @StreamFoxiptv 9 หลายเดือนก่อน

      ⁠@@sargentnocap1414thanks for the clarification.

  • @tangamanga94
    @tangamanga94 3 ปีที่แล้ว

    Thank you for the video. Why you didn't do pigtails for the switch like you did for the outlet? I thought that all lights switches also required the white wire to be installed.

  • @michaelbraun5943
    @michaelbraun5943 2 ปีที่แล้ว

    So if I'm wanting to wire my bathroom on one circuit I can put my outlet, lights and fan on a 20 AMP GFI breaker?

    • @harveylong5878
      @harveylong5878 2 ปีที่แล้ว +1

      bathroom outlets are supposed to be dedicated 20 amp breaker. fan and lighting go on their own circuit

  • @tourismnthub8259
    @tourismnthub8259 2 หลายเดือนก่อน

    Hi Josh how are you.?
    I am also electrician in India

  • @tourismnthub8259
    @tourismnthub8259 2 หลายเดือนก่อน

    You are very nice man

  • @8interlanders
    @8interlanders ปีที่แล้ว

    So is it possible to wire up all lights and outlets in a circuit with only 12/2? Or is 12/3 absolutely needed (assuming there are no 3 way switches)?

  • @justincooper1626
    @justincooper1626 ปีที่แล้ว

    Thanks for this

  • @ryanwilson6470
    @ryanwilson6470 ปีที่แล้ว

    Love the videos! It has helped me out tremendously on various projects 👍🏻. I need input on my application for my shop. I’m needing to add a light switch for four overhead lights. Is it safe to come off of an existing outlet that already has 6 outlets on the same circuit?

  • @ronbunker5778
    @ronbunker5778 3 ปีที่แล้ว +1

    This is great for open walls during construction but not for finished walls.

  • @heathercubas3888
    @heathercubas3888 3 ปีที่แล้ว +1

    I’m planning to do the opposite & add an outlet off a switch. Is it possible to add 2 outlets off one switch?

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว

      It is as long as you don’t overload the circuit. I hope that helps!

  • @o.ggonzalez3470
    @o.ggonzalez3470 3 ปีที่แล้ว +1

    Gracias maistro...

  • @tourismnthub8259
    @tourismnthub8259 2 หลายเดือนก่อน

    How much voltage use for single phase and thee phase

  • @daniel.j.rauscher
    @daniel.j.rauscher 3 ปีที่แล้ว

    Great video!

  • @bpwfla
    @bpwfla 2 ปีที่แล้ว

    Great stuff man, thanks!

  • @rodporter119
    @rodporter119 2 ปีที่แล้ว

    Excellent video. Im currently doing this exact project but not on a new room just a room without a light so im adding one. There was a switch on the wall already but it was controlling a outlet on another wall. In that outlet I tied all the whites and all the blacks together and ran a pigtail from both to the outlet, That outlet works on its own now. My plan was to connect the switch the same way you are showing here. I tried it but no luck. Put my meter on the wires in the switch box from the outlet. The black and white coming in from the outlet are both showing 120 volts. Checked all the connections at the outlet and all is good. Any ideas what may be happening

  • @georgeryan9139
    @georgeryan9139 ปีที่แล้ว

    You do not leave any slack at outlets. I know you want to save as much cost as possible, but if there is a problem in the future, you could use some extra wire. You should fold back a little wire. You still have 6” length to staple. That is how they do it in the north east.

  • @blokey5160
    @blokey5160 3 ปีที่แล้ว +2

    Nice video. Have you considered using the Wago lever nuts in place of the old fashioned twist-on wire nuts?

    • @TheExcellentLaborer
      @TheExcellentLaborer  3 ปีที่แล้ว +1

      Thanks a lot! I have considered those but I have not tried them yet. The tried and true wire nut has simply been my go to for years. If I had some I would definitely try some!

    • @lorenrickey5481
      @lorenrickey5481 3 ปีที่แล้ว

      @@TheExcellentLaborerOnce you used Wago 222’s you’ll never go back.

    • @MaMa-qh4dy
      @MaMa-qh4dy 3 ปีที่แล้ว

      @@lorenrickey5481 The issue with Wago-type connectors is that they contact the wire on a very small area - like a knife. Yes, they are easy and quick, but the amount of copper wire to the connector is slight.

    • @TheExcellentLaborer
      @TheExcellentLaborer  2 ปีที่แล้ว

      I recently tried WAGO connectors and like them a lot. Definitely easy to use!

  • @uptondarden4546
    @uptondarden4546 2 ปีที่แล้ว +1

    When you turn on the switch on and off does it turn the outlet on and off?

    • @TheExcellentLaborer
      @TheExcellentLaborer  2 ปีที่แล้ว +1

      It does not is wired like shown in the video. Hope that helps!

    • @SPQR7117
      @SPQR7117 4 หลายเดือนก่อน

      @@TheExcellentLaborer i'm guessing because you wired it in such a way that it simply continues the electricity along the new wire to the light- but the light switch in the middle simply stops it from traveling further only from that point- it has nothing to do with the power coming to the outlet box.

  • @JosephHerrera-e2l
    @JosephHerrera-e2l ปีที่แล้ว

    I have 2 wires coming out of one conduit and 3 wires coming out from another conduit the only wire that is hot is the red wire the black wires are not hot. Want to put a new receptacle in the box with the light switch that was installed before how do I wire the switch and the receptacle in the same box that it was installed before. Please help me out. Thank you.

  • @x7warrior735
    @x7warrior735 3 ปีที่แล้ว

    Awesome Job ⭐⭐⭐⭐⭐⭐

  • @Nationalist101
    @Nationalist101 ปีที่แล้ว

    So to confirm, that box is always hot, right? So when you’d turn off the switch, the outlet is still live?
    I’m working on UN-pigtailing a three way switch in my house to free up a switch so I can add its own lights off of just that switch. I THINK the extra three way switch is wired off of the outlet below it

  • @vero0992
    @vero0992 2 ปีที่แล้ว

    Man, I didn't know those crimp connectors (as you had on the ground) are removable! I still had enough to work with, but I'll know next time to work it free instead of cutting it off.

  • @lancer525
    @lancer525 ปีที่แล้ว

    I've got a puzzler for you. (it's puzzling me, you might think it simple) I have one 14/2 coming from the panel, going to a single pole switch, operating a single led outdoor light. I want to add another switch off the same feed, coming from the first existing box, going to another switch (this one is lighted) for an interior light. Same feed, two different switches, two different lights, each operated by one of the switches.
    How the heck to wire that one up?
    Thanks!

    • @sargentnocap1414
      @sargentnocap1414 ปีที่แล้ว

      You have to tie it with the hot, neutral and ground off the existing switch.

  • @jackwiederholt1276
    @jackwiederholt1276 2 ปีที่แล้ว

    Can I run a 20 amp breaker feed outlets then tap off it with 14 gauge to run lights in the same room

    • @davidroddini1512
      @davidroddini1512 2 ปีที่แล้ว

      No, you don’t want to use 14 gauge on a 20 amp breaker. This is because 14 gauge is rated for not more than 15 amps. If for some reason the lights draw too many amps, but not enough to trip the 20 amp breaker (say 18 amps for instance), that could cause the 14 gauge wires to catch on fire.

  • @ReneGonzales-v8b
    @ReneGonzales-v8b ปีที่แล้ว

    Can you use #14 wire to wire a bedroom