How to pass overstressed columns in etabs tutorial video

แชร์
ฝัง
  • เผยแพร่เมื่อ 8 ก.ค. 2024
  • How to fix overstress problem in etabs
    ETABS PROFESSIONAL COURSE
    JOIN NOW USING PROMO LINK ONLY FOR EXCLUSIVE CONTENT AND COMPLETE 20 STORY BUILDING DESIGN WORKSHOP:
    www.udemy.com/course/etabs-rc...
    ETABS Playlist:
    • Video
    SAP2000 tutorials : • Video
    Pass an overstressed beam in etabs video:
    • How to pass a Overstre...
    RCC Column Design using etabs tutorial - IMRF design using ACI code
    • RCC Column Design usin...
    RCC column design using etabs - SMRF design using ACI code:
    • RCC column design usin...
    RCC circular column design using Etabs tutorial:
    • RCC circular column de...
    Check design of existing RCC column using etabs section designer:
    • Check design of existi...
    How to check seismic drift limit due to earthquake
    • How to check seismic d...
    How to check drift limit due to wind
    • How to check drift lim...
    How to check beam column capacity ratio in etabs
    Etabs beam column capacity ratio n/a
    Beam column capacity ratio exceeds limit etabs
    Etabs output interpretation
    PMM ratio etabs
    Section overstressed sap2000
    Etabs design output
    Demand capacity ratio in etabs
    How to fix overstress problem in etabs
    How to pass overstressed columns
    How to pass a failing column in etabs
    Methods to pass column
    Rcc column failure
    RCC column fails in shear and torsion
    RCC column fails in torsion
    RCC column fail in flexure
    RCC column fail O/S#2
    RCC column failure O/s#45
    Solving problem of all members over stressed in etabs
    all members over stressed
    Members over stressed in etabs
    All members over stressed in etabs
    Reason of all members over stressed
    Etabs 2016 solving problem in etabs
    Overstressed failure in RCC columns
    Assign End releases to RCC columns
    Main steel percentage exceeds maximum allowed limit in etabs
    HOW TO CONTROL OVERSTRESSING IN RCC COLUMNS
    • If lateral shear force exceed the column’s strength hence make column supports pin that means the columns will distribute the shear forces to other columns as such that they become axial forces in space frames
    • If the main steel exceeds column’s limits so try applying the end releases to the beam, practically it will design beam with enough steel so that it is able to resist the applied moments and transfer it’s shear reactions to beam in form of axial loads to column
    • If columns are failing in irregular pattern try checking whether they are designed for sway special conditions, apply sway intermediate from overwrites if seismic zone is less than 3
    • If Column failing in steel limits i.e main steel still exceeds (O/S#2) so try increasing column’s cross section
    • If column failing in shear (O/S #45) so try increasing cross section on architectural restrictions
    • If columns doesn’t pass the drift checks make the column’s base supports as fixed or increase cross section or add more columns reducing the sway of structure
    • Make the column base supports as fixed reducing the sway of structure hence lesser moments to be transferred to columns
    • If column failing in shear (O/S #5) try checking the unbraced length and effective length factor
    Tension controlled section
    Compression controlled section
    Balanced condition in RCC columns
    Over reinforced RCC column failure
    Under reinforced RCC column failure
    How to pass an overstressed RCC column in etabs
    Shear failure of column in etabs
    Flexure failure of column in etabs
    Torsion and shear exceeds maximum allowed limit in etabs
    Overwrites in etabs for column design
    Etab column failing in shear
    Fix euler’s buckling failure in etabs
    Load on column exceeds Euler’s load
    Etab column faiing in flexure
    RCC column Property modifiers in Etabs
    How to solve overstress problem in etabs
    Slender column failure
    Slenderness ratio calculation
    RCC Slender column design
    Calculate column sizes
    Catchment area method structural design
    #Etabs #Engineering #Design

ความคิดเห็น • 109

  • @zubairbagan8066
    @zubairbagan8066 5 ปีที่แล้ว +1

    Thanks man , the video was very helpful . God bless you

  • @khalidsikandar6772
    @khalidsikandar6772 5 ปีที่แล้ว +1

    once again very useful tutorial u share thanks, previously i request you that plz design and analysis slab culverts, and also after this make one tutorial for detailing and drawings and dont forget the safe tutorials with best regards

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  5 ปีที่แล้ว

      Yes, actually it requires time also i am involved in few projects. But yes will do it

  • @cengizyaman9620
    @cengizyaman9620 2 ปีที่แล้ว

    HOW did you bring the detail button to the toolbar? can you help me please?

  • @rahulsomde5094
    @rahulsomde5094 3 ปีที่แล้ว

    How do i join two align beams in Etabs as a one member, if one beam is inclined from say plane A to plane B and other is in plane B?

  • @alishapradhan9602
    @alishapradhan9602 2 ปีที่แล้ว +1

    Hello, what are the solutions for o/s 35 in columns?

  • @chiluvuritrilokraju6050
    @chiluvuritrilokraju6050 5 ปีที่แล้ว +1

    Sir you are doing good job sir please make a video for check for stiffness & drift & displeasement& modes in 12 & other (as per India codes) this very useful please make a video

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  5 ปีที่แล้ว

      The check for seismic and wind drift video is already available on this channel's etabs' playlist

  • @manz36115
    @manz36115 4 ปีที่แล้ว

    Sir Jow to solve Eulers load exceed
    OS# 5, please tell me I am badly struck somewhere

  • @skillhnter1303
    @skillhnter1303 ปีที่แล้ว

    JAZAKALLAH

  • @madesnoel
    @madesnoel 4 ปีที่แล้ว +1

    Can we use these steps on steel column?

  • @kannikagowda2905
    @kannikagowda2905 3 ปีที่แล้ว

    Sir can we use non-sway frame type for residential building which is designed only for gravity loads??

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  3 ปีที่แล้ว

      Yes, but it will not even include P-Delta effected due to gravitational effects. Which i don't recommend

  • @civilacademia3831
    @civilacademia3831 3 ปีที่แล้ว

    Does it make sense to increase the sections? As it will increase the self weight and lumped mass of building.

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  3 ปีที่แล้ว

      What do you mean

    • @civilacademia3831
      @civilacademia3831 3 ปีที่แล้ว

      @@EngineeringLearningPlatform I mean if the section is increased. The whole weight of building will increase, i have confusion in that regard.

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  3 ปีที่แล้ว

      @@civilacademia3831 Yes but Structural stability is important . If section is failing then last option is to increase size . Weight increase is very nominal if you do some manual calculations, you'll understand

    • @civilacademia3831
      @civilacademia3831 3 ปีที่แล้ว

      @@EngineeringLearningPlatform Okay.

  • @anasgh5343
    @anasgh5343 ปีที่แล้ว

    what does O/S #35 mean ? I have a non-prismatic column and the maximum reinforcement ratio is 1.1 % !

  • @ankitshrivas740
    @ankitshrivas740 3 ปีที่แล้ว

    Is it safe to release moments and use the design data for reinforcement

  • @kannikagowda2905
    @kannikagowda2905 3 ปีที่แล้ว

    Hello sir , if we use smaller beam dimensions does it cause increase in column reinforcement??

  • @junyanchen6434
    @junyanchen6434 4 ปีที่แล้ว

    Can you teach us how to solve “joint shear”failure in SMRF? Thank you.

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  4 ปีที่แล้ว

      You mean strong column weak beam check pass? Its simple inc. Column dinensions parallel to beam length as it will inc. Its flexural capacity compared to beams'.

  • @shahbazuddin1229
    @shahbazuddin1229 6 หลายเดือนก่อน +1

    Can you please refer any video on capacity Ratio

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  6 หลายเดือนก่อน

      Check column design video or the video with check of existing structure.

  • @hariasssss
    @hariasssss 5 ปีที่แล้ว

    if u release all the moments in all beams then column will pass in gravity loading but about the lateral loading, definitely it will increase the column sizes.and is it advisable to release the moment in all beams ?. If we release then we do have to do very careful simply supported detailing in all the places.

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  5 ปีที่แล้ว

      Thats why i dont advise to release moments in "All beams" of single storey

    • @gyansingh7700
      @gyansingh7700 4 ปีที่แล้ว

      But practically as per site any release not possible, all members joints to be act as a fixed behavior during the earthquake!!!!

  • @Osama-Anwar
    @Osama-Anwar 4 ปีที่แล้ว +1

    Can we release moments in beams in SMRF constructed on Seismic zone 3? Because in reality beam and column joint is fixed and moments from beams will be transferred to columns irrespective of how we design beams. Fixity is determined by the relative stiffness of the members rather than the design of the beam. Designing beam as simply supported is not right I think. Would you mind to elaborate on the concept behind releasing moments, please? I am unable to find any evidence about that on the internet.

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  4 ปีที่แล้ว

      Yes when you apply end releases the negative gravitational moment is converted into positive moment for beams which enhances percentage of steel in beam and it is important if you use end releases to pass columns then u use the same model for beam design as well with applied end releases

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  4 ปีที่แล้ว

      It's a design office based practice, not everything you can find on internet .

    • @Osama-Anwar
      @Osama-Anwar 4 ปีที่แล้ว

      @@EngineeringLearningPlatform When we apply beam releases our beam acts as simply supported. Is it not better to say that it is merely the behavior of simply supported beam due to which there is no negative moment in the beam. In other words, we have designed our beam in such a way that it will not be able to bear negative moments (which in reality will be acting on the beam as it has fixed ends with columns) and it will fail if any negative moment will act upon it. It is the way I see it what is your thought?

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  4 ปีที่แล้ว

      @@Osama-Anwar No it won't fail unless u detail it properly, read ACI chapter 21, it puts a certain proportion of positive steel in negative reinforcemnt necessarily . So in other words, we are increasing positive steel, which increases negative steel in detailing .

  • @vaibhavkothari5175
    @vaibhavkothari5175 5 ปีที่แล้ว

    Is changing or applying end realese effects the strength of structure
    Any special precautions while applying end realese please share

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  5 ปีที่แล้ว

      Yes when you apply end releases the negative gravitational moment is converted into positive moment for beams which enhances percentage of steel in beam and it is important if you use end releases to pass columns then u use the same model for beam design as well with applied end releases

  • @rcbsht9644
    @rcbsht9644 ปีที่แล้ว

    Can i import files into csi detail v19 directly from etabs v20

  • @engrshafiq1
    @engrshafiq1 4 ปีที่แล้ว +2

    Moment release in beams are possible when you allow cracking by providing less reinf. or development lengths. How lateral load resistance will be ensured if all beams have moment releases? Otherwise, Shear wall should be put into action by designing it as the only lateral load resisting system with a premium of increased thickness , heavily reinforcement including link beams plus properly detailed collector elements.

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  4 ปีที่แล้ว

      Releasing moments in beam means it will not really taking lateral moment hence the columns will be designed strong enough, which we call as predefined hinges and the hinges in beams are much desired as compared to in columns as hinge formation in column results in whole structural failure however hinge formation in beams being ductile member will not fail the structure but will increase the positive gravitational moment in beams as beam will not be taking moment at supports i.e negative moment . This will cause increase in positive moment steel i.e bottom reinforcement will be designed sufficient enough to resist this condition. Now about the reinforcement of supports which we apparently made zero by applying releases will not happen as if u see my beam design video we will place minimum steel and in case of seismic design we set minimum steel of 1/4th or 1/5th (based on seismic zone) of the positive moment bottom reinforcement hence becomes practical design, and will be taking negative moment as well but once the support joint yeilds then this ductile member will have enough capacity left to carry on the gravitational positive moment before repairs are made.

    • @engrshafiq1
      @engrshafiq1 4 ปีที่แล้ว

      What is the definition and concept of a Moment Resisting Frame? What is the. difference between moment frame system and truss system? (at least in trusses we have diagonals to to resist lateral forces). in Releasing M33 on all beams will introduce structural instability mechanism provided bases to rotate. If someone is trying to design isolated spread footing with this approach, then there will be a big risk. Software will also intimate you with excessive loss of accuracy or Ill conditioned stability. (by selecting SAP2000 or ETABS Standard Solver option, we can see such warnings in Run Log File)
      Kindly refer UBC97 sec 1627 definition of Moment Resisting Frame.....Code requires that beam-column joints should resist flexural efforts. Otherwise you cannot put your frame in any category of OMRF, IMRF or SMRF as set-forth in ACI or UBC/ASCE/IBC.
      1/4th or 1/5h of positive moment capacity at beam-column location is not recommended by any code for lateral load resisting system.

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  4 ปีที่แล้ว +1

      @@engrshafiq11/4 and 1/5 It is recommended by ACI 08 see chapter 21 see SMRF beam design, ofcourse you cannot ignore thay force from frame but u primarily won't design beam for that moment but columns must be. U must have known that in building frame system we take modifiers of column as 0.01 in wall design model, didn't you question there that why taking as 0.01 as name suggests frame etc ? In these type of systems is it okay to rely on single model? No . You must consider the maximum positive moment as well when joints are yeilded . This video elaborates that post yeilded state, and design columns strong enough . Also another example when designing beam column why u take slab as membrane? although slab has its stiffness but why neglect? Answer is that you want to design frame strong enough to take all moments independent of slab's stiffness. Third example is why you take torsion constant to be 0.01 in internal beam for slab design purpose? answer is you want to design slab strong enough to take up its moments it self and transfer minimal residual to the beam which then becomes torsion for beam .
      Consclusively i would say making hinges in beam is not all times condition but practically you can detail column beam as pin making beam and column stronger in terms of reinforcement .

    • @engrshafiq1
      @engrshafiq1 4 ปีที่แล้ว

      @@EngineeringLearningPlatform First of all we have to understand, definition of Moment Resisting Frame? Post yield analysis of all joint failure is a useless effort especially for design intent. In Pakistan 8th Oct 2005 earthquake, many structures failed due to failure of joints.
      Regarding SMRF, ACI code says, minimum 1/4th from max moment capacity at either face of joints should be maintained every where in the section of the beam...Code is not saying that at face provide 1/4th of positive moment capacity. It is the basic requirement of moment frame that Joint should be robust enough to resist moments. In fact in SMRF ACI played with extra safety that splice location has been shifted in the middle of beam span to avoid any rebar slippages.
      All other theories related to membrane, torsional release, shear wall reduced stiffness factors are irrelevant here. If we are not understanding basic principle of Structural engineering i.e Moment Resisting Frame then discussing other issues have no value.

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  4 ปีที่แล้ว

      @@engrshafiq1 It was just to make you understand that we make multiple models for conservative design of structural member level

  • @lovelenyfernandez7028
    @lovelenyfernandez7028 ปีที่แล้ว

    What about Warning #52 Delata exceeds 1.4

  • @manz36115
    @manz36115 4 ปีที่แล้ว +1

    Sir How to solve Eulers load exceed
    OS# 5, please tell me I am badly struck somewhere

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  4 ปีที่แล้ว +1

      Yes for that unlock model, select that failed member, and go to design -> overwrites and you see effective length factor, fix that value . Like for example in class you must have computed this effective length factor "k" use that value here .

    • @manz36115
      @manz36115 4 ปีที่แล้ว

      Engineering Learning Platform Thanks for reply sir you solved my problem. Look what actually happening is, I have Foundations 1.5 m below the plinth and my storey height is 3.2 meter. In some area I can’t provide the grade beams as they are passing Over underground water tank. So if I connect that grade beam the column is passing and when I remove that beam it is failing. However on site we can’t put that grade beam . So my column height will be 1.5+3=4 m In that area and “K” value will be “0.5” as both ends are fixed . Am I right ? Sir . Kindly reply.

  • @pakistanupdates-babardhedh2969
    @pakistanupdates-babardhedh2969 3 ปีที่แล้ว

    if we make column support Pin,we need to detail this in foundation accordingly

  • @civilideas1925
    @civilideas1925 2 ปีที่แล้ว

    👍🏻

  • @rizki2211
    @rizki2211 3 ปีที่แล้ว

    Can u teach us how to solve N/A?

  • @rahulsomde5094
    @rahulsomde5094 3 ปีที่แล้ว

    How do i join two right angle cantilever beams in one plane as a one member?

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  3 ปีที่แล้ว

      Perpendicular members cannot be joined . But transfer of forces remain same

    • @rahulsomde5094
      @rahulsomde5094 3 ปีที่แล้ว

      @@EngineeringLearningPlatform thanks Sir for valuable reply, but can we join two align beams in Etabs as a one member, if one beam is inclined from say plane A to plane B and other is in plane B?

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  3 ปีที่แล้ว

      @@rahulsomde5094 yes . Use replicate linear option . Do some tries .

    • @rahulsomde5094
      @rahulsomde5094 3 ปีที่แล้ว

      @@EngineeringLearningPlatform thanks Sir.

    • @rahulsomde5094
      @rahulsomde5094 3 ปีที่แล้ว

      @@EngineeringLearningPlatform actually i am trying to model a single beam which will run through out the length of landing and staircase slab, but dont know how to join the beam under staircase with beam under landing, all load is being transferring to staircase slab and landing beam, and the beam under staircase not taking any load as it is not join with landing beam.
      I am tring to join these beam as a single beam pl help.

  • @josh_up
    @josh_up ปีที่แล้ว

    The beams passed as per previous video failed after performing this. Kindly help!

  • @vaibhavkothari5175
    @vaibhavkothari5175 5 ปีที่แล้ว

    How to decrease reinforcement percent in column

  • @EngineeringLearningPlatform
    @EngineeringLearningPlatform  5 ปีที่แล้ว

    Watch "How to pass failing column on etabs"

  • @abdullahmayof347
    @abdullahmayof347 4 ปีที่แล้ว

    Please can you show us how to pass o/s #20 for columns. Thank you.

  • @shaikshabuddin190
    @shaikshabuddin190 ปีที่แล้ว

    Dear,
    To pass the structural elements you have released beam end moments where they are contected to columns, this practice is not done as its only applicable for secondary beams as of my knowledge. where ever end moments are released the particluare beam elements is designed as simply supported not as fixed right? so in this vedio fixed beams are deisgned as SSB by releasing moments to pass the elements, do you think its right ?

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  ปีที่แล้ว

      They will be detailed as ss.

    • @shaikshabuddin190
      @shaikshabuddin190 ปีที่แล้ว

      @@EngineeringLearningPlatform
      My question is , is this correct practice while we design a structure ?

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  ปีที่แล้ว

      @@shaikshabuddin190 Yes for small structures the detailing is done as per the modifications you do in model. But in larger or highrise buildings we should avoid.

    • @shaikshabuddin190
      @shaikshabuddin190 ปีที่แล้ว

      @@EngineeringLearningPlatform Even though for small structures if we follow as said by you it won't be economical design in terms of reinforcement becasue under SSB design the designed steel will not falls under economic aspects. correct?
      As a civil engineer we have to design balanced reinforced and economical structure, right?

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  ปีที่แล้ว

      @@shaikshabuddin190 what if architect doesn't allow increasing section size and economical is not a problem for a client? You'll say you can't do it? Or you will use the method. Not everything is able to be used in each situation.

  • @shoaibakram1703
    @shoaibakram1703 3 ปีที่แล้ว

    Can you provide pdf tutorial

  • @AnkitJain-wq5yf
    @AnkitJain-wq5yf 3 ปีที่แล้ว

    is it safe to release all the beam

  • @khalidsikandar6772
    @khalidsikandar6772 5 ปีที่แล้ว

    one more thing if you plz provide me ur personal email so that i can chat with u regarding design

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  5 ปีที่แล้ว

      You can contact on facebook page named "Engineering learning platform" I usually don't look up to emails much often

    • @khalidsikandar6772
      @khalidsikandar6772 5 ปีที่แล้ว

      @@EngineeringLearningPlatform okie i will

  • @anilkushwaha1985
    @anilkushwaha1985 4 ปีที่แล้ว

    totally wrong method use in this video

    • @EngineeringLearningPlatform
      @EngineeringLearningPlatform  4 ปีที่แล้ว

      It's just based on your understanding and expertise . I know not everyone can understand it .