Google Nest Thermostat E74 Error Troubleshoot

แชร์
ฝัง
  • เผยแพร่เมื่อ 8 พ.ย. 2024

ความคิดเห็น • 93

  • @KDiZ88
    @KDiZ88 2 ปีที่แล้ว +27

    This video isn't getting enough attention. For me, it ended up being the fuse. Thanks for the clear and CONCISE troubleshooting. We need more videos like this!

    • @randomhomegadgets
      @randomhomegadgets  2 ปีที่แล้ว +1

      Thanks for your comment. Same here, I got a blown fuse too :)

    • @zacharyf5631
      @zacharyf5631 ปีที่แล้ว

      @@randomhomegadgets Hello, I live in an apartment.. where would the HVAC fuse be? Is that typically in the garage or on the roof?

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว

      For an apartment building, it's usually on the roof. But most likely you won't be allow to access it unless you are the building maintenance person.

    • @01crs1
      @01crs1 9 หลายเดือนก่อน +2

      Same here, fuse was the issue. I know this is a 1 year old comment but adding to the thread so this video gets more visibility.

  • @lhammerick
    @lhammerick 9 หลายเดือนก่อน +4

    So helpful! I was leaving the panel off to show my kids and wasn't sure why I couldn't get it to work after I replaced the fuse. This video very helpfully noted that the panel being off deactivates the power!!! That one little critical part might have led me to calling in an electrician. Fortunately, this video mentioned it when others left that part off . . .

    • @randomhomegadgets
      @randomhomegadgets  9 หลายเดือนก่อน

      Glad that you find it helpful. Sometimes we think way ahead of ourselves and forgets the basic steps :)

    • @ChrisSullins
      @ChrisSullins 6 หลายเดือนก่อน

      Is this the unit inside or the one outside?

  • @ericbaltas8663
    @ericbaltas8663 ปีที่แล้ว +5

    Really appreciate your video, resolved my issue with no need to pay an expensive technician

  • @stevenstanfill8146
    @stevenstanfill8146 ปีที่แล้ว +1

    Thanks for taking the time to record this video. Added mulch outside without realizing that I clogged the outside drain. Cleared the drain and back to working perfectly.

  • @benlonz
    @benlonz 5 หลายเดือนก่อน +1

    Very comprehensive troubleshooting video. The blown fuse section was extremely helpful and the culprit. THANK YOU!

    • @randomhomegadgets
      @randomhomegadgets  5 หลายเดือนก่อน

      Thanks! I’m glad that you find it helpful:)

  • @taraki3040
    @taraki3040 10 หลายเดือนก่อน

    Very helpful. My issue was blown fuse. It costed only $7.5. Thank you!

    • @randomhomegadgets
      @randomhomegadgets  10 หลายเดือนก่อน

      You're welcome! Glad that you solved the problem without costing a fortune :)

  • @BobFromSeattle
    @BobFromSeattle 5 หลายเดือนก่อน

    OUTSTANDING video, comprehensive, to the point and easy to follow. This video should serve as a model for all TH-cam content creators. Immediate start to the sought content, timestamps for the various options, and no obtrusive sales pitches. After going through all of the diagnoses, it turned out to be a flooded drain pan outside. Thank you sir, well done. A like, a comment, ringing the bell, a sub, and I might even mow your lawn if you keep this up.

    • @randomhomegadgets
      @randomhomegadgets  5 หลายเดือนก่อน

      Thanks for your kind words! I’m glad that it helped you to solve the problem :)

  • @andrewmassey11
    @andrewmassey11 ปีที่แล้ว +3

    Great video! Mine was as simple as the drain being clogged. I vacuumed it out and it works perfect!

  • @jayrocke6067
    @jayrocke6067 ปีที่แล้ว

    I second the previousposter. I didn't know about the fuse until this video, which was my issue, too! You saved me a $150 service call...!

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว

      I’m glad that this is helpful for you :) Definitely feels good to be able to solve the problem yourself

  • @chasecorbin9339
    @chasecorbin9339 8 หลายเดือนก่อน +5

    Music beyond annoying when im failing to fix this damn thing

  • @MuellerMechanical
    @MuellerMechanical 3 หลายเดือนก่อน

    Thank you so much, it was the fuse, you saved us from sleeping in the 80deg heat, thanks!!

    • @randomhomegadgets
      @randomhomegadgets  3 หลายเดือนก่อน

      Glad that it’s helpful for you :)

  • @Itsmikepowell
    @Itsmikepowell 4 หลายเดือนก่อน +1

    Thanks for the video!
    Any suggestion for a recurring e74 error? I noted today ac wasn’t on and went through my normal checks. No breaker, dry pan and fuse appeared to be in tacked. I go to TH-cam to search for answers and hear my ac kick on and resolved the problem itself?! Moments later it goes out again but once again resolved on itself?!
    Thanks for any advice 🙏

    • @randomhomegadgets
      @randomhomegadgets  4 หลายเดือนก่อน +1

      If it keeps coming on and off, it’s likely due to the consensation line not flowing well. You can check out this video on how to check the condensation line: th-cam.com/video/AiBFL-l0uxY/w-d-xo.htmlsi=l5dboXvqG975IsW0
      Also make sure the air filters are clean.

    • @Itsmikepowell
      @Itsmikepowell 4 หลายเดือนก่อน

      @@randomhomegadgets Last night I went back through your diagnosis’s and it was in fact the the float switch! The drain pain underneath the unit was bone dry so I didn’t think it could be that but when opening the side panel I noticed some slight puddling inside the unit underneath the coils. Checked the float switch and as soon as I pulled it out the AC kicked on!
      You are a rockstar my friend 💪

  • @beastma0
    @beastma0 ปีที่แล้ว

    Thank you... Thank You... Thank you! The best detailed troubleshooting vid on YT for this issue. Saved me $$$.

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว

      You are very welcome. I’m glad that you find it useful :)

  • @crispyflix
    @crispyflix 11 หลายเดือนก่อน

    Thanks for this video! Looks like my issue was more or less related to diagnosis 1. Either my wife or I may have inadvertently bumped into the power switch on our furnace when bringing out the holiday decorations from the basement 😂 🤦‍♂️

    • @randomhomegadgets
      @randomhomegadgets  11 หลายเดือนก่อน

      Thanks for the comment. I'm glad that's an easy fix :P

  • @jimmywan1548
    @jimmywan1548 11 หลายเดือนก่อน

    Amazing video. Need to get this video to the top recommended

    • @randomhomegadgets
      @randomhomegadgets  11 หลายเดือนก่อน

      Thanks for the kind words. I’m glad the video is helpful for you :)

  • @dominicnicoletti96
    @dominicnicoletti96 2 หลายเดือนก่อน

    ez trap for furnace cooling system was clogged with some debris and water setting off the "trap" signal resulting in the E74 error code for my nest. Thanks for the video

  • @carloslemus3916
    @carloslemus3916 2 หลายเดือนก่อน

    This was a great video that probably save us hundreds of dollars thank you

  • @artbazil
    @artbazil ปีที่แล้ว +2

    Great video, thanks for the tips! I have a pretty weird issue - I'm getting this error while the heating is on (and it is only visible through the Nest app). So, once I kick off the heating, it can blow hot air for 5-6 minutes and then stop for 1-2 minutes and after go on again. So, it goes on and off and at the moment it stops I do see E74 error on the app (but the unit display either shows a "Delayed" message or just continues showing that the heating mode is on). Any ideas about what is happening? I do have 2 more Nest Thermostats in my house, and others works without any issues (same wiring at the base and at the HVAC for all units)

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว +1

      This error means that the C wire is not giving enough power to charge the best display. You can use a voltage tester to test the voltage between C wire and the heating wire, should be 24V. If it’s less than that or fluctuate, then there’s a problem with the furnace main board. If the voltage is stable, then there’s a problem with the thermostat itself (may try to swap out the unit display to the ones that you know is working and see if the problem goes away).

    • @artbazil
      @artbazil ปีที่แล้ว

      @@randomhomegadgets thanks a lot for your reply! I've just measured all my 3 thermostats on each level and they all give me the same readings between C and Rh wires - about 28V (it's fluctuating, but slightly around 27.89-28.01V) I've also tried Google Nest 2nd gen and two units of third-gen and still getting this error...

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว

      Hmm, in that case that’s likely some problem with the heater main board. Sorry this is beyond my knowledge level. Probably should check with a HVAC technician.

    • @artbazil
      @artbazil ปีที่แล้ว

      @@randomhomegadgets no worries! Anyway thanks a lot for your helpful replies! Really appreciate it! 👍

    • @SirCharlesLikesChurros
      @SirCharlesLikesChurros ปีที่แล้ว

      ​@@artbazildid you end up figuring out what your issue was? Thank you

  • @seventwenty4569
    @seventwenty4569 ปีที่แล้ว

    Thank you. Found blown fuse.

  • @NoName-sx9xs
    @NoName-sx9xs ปีที่แล้ว

    Do packaged units have drain pans/ safety switches? Also where would I find the control board on a packaged unit?

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว

      Yes, they should be all inside the packaged unit outside the house. How to get to it depends on the specific units. But usually there should be panel that you can open and look inside.

  • @KansasFarmer
    @KansasFarmer ปีที่แล้ว

    Thanks for the info. But none of those were my issue. Had the same error code. I pulled the face off and pushed the rh wire around a little and put the cover (interface or what ever it's called) back on and it works now. I think it just needed a hard restart 🤷‍♂️ I guess. Plus main power went off to the unit. Big storm rolled through.

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว +1

      Thanks for your comment. Probably the error code came up when the main power went out. The Google nest didn’t recognize that the power was back on until you took it out and put it back on again.

  • @01crs1
    @01crs1 9 หลายเดือนก่อน +1

    Very helpful, thank you for saving me $100's.

  • @brianlameira260
    @brianlameira260 หลายเดือนก่อน +1

    I checked everything and I keep getting the error code. I comes and goes for hours at a time. Works for a while then the error comes back when ever it wants.

    • @randomhomegadgets
      @randomhomegadgets  หลายเดือนก่อน

      Check if you have a in line flow switch. It could be that the drain pipe is partially clotted so the flow switch turn off the HVAC frequently when the water is backed up, then turn it back on when the water is able to get out.

  • @piotrdamu6194
    @piotrdamu6194 11 วันที่ผ่านมา

    Very good video thank u

    • @randomhomegadgets
      @randomhomegadgets  7 วันที่ผ่านมา

      No problem. Hope it help you solve the problem and save some money :)

  • @ChrisSullins
    @ChrisSullins 6 หลายเดือนก่อน

    Is the hvac inside or the units outside?

    • @randomhomegadgets
      @randomhomegadgets  6 หลายเดือนก่อน

      It’s the hvac inside the house

  • @subliminal_fire5025
    @subliminal_fire5025 ปีที่แล้ว +1

    Great Video and clear instructions!!! You rock!

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว

      Thank you for your kind words. I’m glad that it helped.

  • @79MORRIZ
    @79MORRIZ ปีที่แล้ว +2

    Thanks this help me to fix my

  • @schandran1
    @schandran1 3 หลายเดือนก่อน

    Hello - I'm getting intermittent E74 error on cooling. I checked the drain line, Fuse, wiring all seems ok. I need to restart the furnace to get the nest thermostat to work. I have outdoor AC unit and Lennox G61MPV furnace. Any help suggestions pls.

    • @randomhomegadgets
      @randomhomegadgets  3 หลายเดือนก่อน

      Check to see if you have an in-line float switch. If you have one, open it and see if there’s water backing up in there. It’s likely that the drain pipe is partially clotted and takes a longer time to clear out the water. So when water backs up to the float switch, it shuts off the AC

    • @user-yv9qo3ib9l
      @user-yv9qo3ib9l 3 หลายเดือนก่อน

      Thanks for your reply. I don’t have in float switch. I changed thermostat to old honeywell and all works fine. Not sure what to do.

  • @mikesweeney5724
    @mikesweeney5724 2 ปีที่แล้ว +1

    is the fuse on the furnace inside the house or a/c handler outside the house?

    • @randomhomegadgets
      @randomhomegadgets  2 ปีที่แล้ว

      Every house is different, but it’s usually inside the house near the fan blower.

  • @fadyishak9684
    @fadyishak9684 ปีที่แล้ว +2

    Thanks, very helpful and informative 🙏

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว

      Thanks for your comment. I’m glad that you find it helpful :)

  • @danyeldan2139
    @danyeldan2139 ปีที่แล้ว

    lately every time I turn on the Heater works but after riches for example 72 turns off but again turns back on right away and gives me code E74 I didn't have this problem before

  • @Mohammad-fn4sm
    @Mohammad-fn4sm 3 หลายเดือนก่อน

    Thank you !!!

    • @randomhomegadgets
      @randomhomegadgets  3 หลายเดือนก่อน

      You're welcome! I’m glad that it’s helpful for you :)

  • @Dora_2015
    @Dora_2015 2 ปีที่แล้ว +1

    Thanks for your movie. it is clearly and very useful.

  • @Polo876.
    @Polo876. 4 หลายเดือนก่อน

    Did all you said but am still having the E74 error code new board new transformer still having same issue it work for a day are two are even couple hrs then bam it's out and E74 help

    • @randomhomegadgets
      @randomhomegadgets  4 หลายเดือนก่อน

      If it keeps coming on and off, it’s likely due to the consensation line not flowing well. You can check out this video on how to check the condensation line: th-cam.com/video/AiBFL-l0uxY/w-d-xo.htmlsi=l5dboXvqG975IsW0

  • @MrBostonian100
    @MrBostonian100 7 วันที่ผ่านมา

    Fuse keeps getting blown, suspecting power surge from somewhere.

    • @randomhomegadgets
      @randomhomegadgets  6 วันที่ผ่านมา

      Maybe try to put a surge protector between the power outlet and the HVAC and see if it helps.

  • @sakurasolos7941
    @sakurasolos7941 2 ปีที่แล้ว +1

    idek where a fuse is located and it’s freezing this all happens after i tried to use the heater

    • @randomhomegadgets
      @randomhomegadgets  2 ปีที่แล้ว

      The fuse is usually at the control board near the furnace/blower unit

    • @sakurasolos7941
      @sakurasolos7941 2 ปีที่แล้ว

      @@randomhomegadgets the thermostat isn’t coming on at all now 😭 i didn’t even do anything yet

    • @randomhomegadgets
      @randomhomegadgets  2 ปีที่แล้ว

      Yah, since there’s no power going to the thermostat, it will slowly drain out its battery. There’s a micro USB port at the bottom of it, you may use it to charge the battery.

    • @sakurasolos7941
      @sakurasolos7941 2 ปีที่แล้ว

      @@randomhomegadgets oh ok thx, it’s probably the fuse, i took it off the wall and no wires were lose, checked the panel too

    • @joewhan11
      @joewhan11 2 ปีที่แล้ว

      ​@@randomhomegadgets

  • @BirdChirpGaming
    @BirdChirpGaming 2 ปีที่แล้ว +3

    Commenting on all these videos with the fix that I found hoping it will help someone.
    I simply hit the emergency power light switch to my gas furnace. Once I flipped the power back on, everything was fine. I must have switched it off by mistake moving stuff up and down the basement steps where the switch is.

    • @randomhomegadgets
      @randomhomegadgets  2 ปีที่แล้ว

      Thanks for your comment! You are right, need to make sure the power to the furnace is actually on.

  • @timfish7356
    @timfish7356 ปีที่แล้ว

    Make sure your wife didn’t turn off the switch in the basement

    • @randomhomegadgets
      @randomhomegadgets  ปีที่แล้ว

      Oh yes that should be the first thing to rule out :P

  • @nrod9
    @nrod9 10 หลายเดือนก่อน

    I get a e74 warning every once in a while then within minutes of noticing it the warning goes away.

    • @randomhomegadgets
      @randomhomegadgets  10 หลายเดือนก่อน

      It could be that your HVAC restarting itself. Sometimes if the HVAC is too hot and not able to vent the air fast enough, it will temporarily shutdown and reset.

  • @aaronkelly4838
    @aaronkelly4838 ปีที่แล้ว +1

    Ll

  • @xlaw6272
    @xlaw6272 24 วันที่ผ่านมา

    I have 8 zones…7 of the thermostats are working…one doesn’t work…e74 code…no power to Rh wire…what do you think it is…I don’t see a drain pan outside by the HVAC system…

    • @randomhomegadgets
      @randomhomegadgets  21 วันที่ผ่านมา

      Is the E74 all the time or just comes and goes?

    • @xlaw6272
      @xlaw6272 21 วันที่ผ่านมา

      @@randomhomegadgets
      It’s all the time

    • @randomhomegadgets
      @randomhomegadgets  20 วันที่ผ่านมา

      Then it’s likely that there no power to that specific HVAC. Check if the breaker is off, the power cord, power switch, and the HVAC main panel fuse

  • @nestord.delgado7300
    @nestord.delgado7300 3 หลายเดือนก่อน

    Thanks for the video. Headed straight to the auto store got the fuse. Good to go. 🫡

    • @randomhomegadgets
      @randomhomegadgets  3 หลายเดือนก่อน +1

      Glad that it’s helpful for you :)