The knee point voltage defined as the voltage at which a 10% increase in applied voltage increases the magnetizing current by 50% for voltages greater than the knee point, the magnetizing current considerably even for small increments in voltage across the secondary terminals
Thank you sir.unga video explanation super sir🎉
Super explanation
Clearly explained 🎉
Lucidly explained. Thanks
Hi boss,
The fault current If mentioned in CT is 3kA.do we have to consider fault current of bus?
very useful to us. tq.
Thank you brother
Keep support
Jii very usefull thank you
Sir suppose we found knee point voltage less than Ct name plate details mentioned voltage what action need to take? CT should replace.
Superb
Thank you
Super sir thank you very much sir, 50,50n and 51,51n enna nu konjam nalla explain panni oru video podukal sir
what is the difference between VK and VK/2?
Formula mentioned in the video is it right....? kindly check.....
You have considered fault current as 4000A which is minimum ..... Even if you calculate fault current with trnsformer impednace minimum fault current would be 10kA or 15kA.... if you apply the same in the formulae then knee point voltage is very higher...
can you check and confirm....
Thanks. Super
Thank you too!
Bro cable Voltage drop calculation poduga
Entha cable voltage drop bro?
@@Engineering-in-tamil power cable bro
During this test, should the CT make noise?
Could you please explain the usage of knee point with details in practical
BRO, Neenga manual calculation panadhu 300CTR ku dan so, 165.3A varudhu as same as mentioned in name plate 165A. Correct dhana
Current thaan bro
Kit name ?
Hi
Hindi me bolo guru ji kya south logo hi btana hai